Propane Flare Fittings Help

Been winter camping in Connecticut for the last couple of weeks. Problem was my propane usage was excessive compared with previous winter camping sessions. I found a sizable leak at the flared fitting where it attachs to the pilot assemby in the water heater. I accidently found this by smell. Luckily during winter camping I only use the electric element in my Atwood - Mdl GC6AA10E water heater. Turned off the propane supply at the tank, then started to look closely at the flared fitting. It wasn't tight; I removed the fitting with my fingers. Inspected the flare - looked good. I suspected the copper had cracked because the fitting may have been over torqued. Cleaned both surfaces and reconnected the flange nut to the body of the pilot assembly. Put a drop of blue locktite on the threads before tightening. I tightened the fitting once tight to two flats additional. Could not find the torque requirements for 3/8" copper tubing other than two flats. Put the system back in service and bubbled tested the fitting satisfactory.

Question: Does anyone know the torque requirements for 3/8" copper tubing flare fittings? Any help would be appreciated including source for my reference.
__________________

__________________
Ted Fulltiming in the DreamCatcher a
2008 Challenger 371PE on F53 w/ 2010 Cobalt
R'V there yet?
teddyu is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-22-2014, 06:49 PM   #2
Senior Member
 
Join Date: Sep 2012
Posts: 4,232
Have no idea on torque ratings but you did it properly
I am certified the Railroad Commission of Texas for LPG filling and RV technical repairs. No where were there torque ratings. In a nutshell, it was what you did. Technically, by the RRC of TX, you need to do a leak test too, but bubbling is fine.
I think, though, you are not supposed to add anything to the threads.

And by pilot asy., you mean the gas valve?
__________________

__________________
jesilvas is offline   Reply With Quote
Old 02-22-2014, 08:07 PM   #3
Senior Member
 
Damon Owners Club
Ford Super Duty Owner
Join Date: Apr 2008
Location: NAS Pensacola, FL
Posts: 329
jesilvas,

Thanks for the prompt reply. The pilot assembly (tech manual term) is what I would also call the gas valve. I put just a little locktite on threads to prevent the fitting from loosening. I had previously smelled the propane tracer, but the water heater is near the sewer hose connection and thought it was sewer gas. As loose as it was, it may have been that way (loosening) for years. Bought the unit new and never had to work on the water heater so not sure how long it was not tight. When the weather is better, I plan to look at all the flared joints. Thanks for your help.
__________________
Ted Fulltiming in the DreamCatcher a
2008 Challenger 371PE on F53 w/ 2010 Cobalt
R'V there yet?
teddyu is offline   Reply With Quote
Old 02-22-2014, 08:16 PM   #4
Senior Member
 
Join Date: Sep 2012
Posts: 4,232
I rarely see leaks from flare nuts that backed off. We PDI all new trailers obviously, but used trailers too. I think two or three times I've had flare nuts leaking, and strangely, those were all on the same trailer.
__________________
jesilvas is offline   Reply With Quote
Old 02-22-2014, 08:17 PM   #5
KIX
Senior Member
 
KIX's Avatar


 
Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 3,579
TeddyU........I agree with jesilvas.......it's just the way it's done. I've made maybe a gazilllion copper/brass flare connections over the years and you did it just the way I've always done it. Except for the loctite on the threads. Properly tightened you likely didn't need the loctite but it won't hurt anything either.
__________________
KIX
'02 Ultimate Advantage 40J Spartan MM - Cummins ISC
2013 Jeep Rubicon JK Unlimited
KIX is offline   Reply With Quote
Old 02-23-2014, 06:25 AM   #6
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,792
SO long as the nut itself does not split I do not think you can overtorque a brass flair fitting.. I've always made them "As tight as possible" and for me.. Well I break quarter inch grade 5 bolts when I do that. so you can figure out how tight it is.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 02-23-2014, 10:55 AM   #7
Senior Member
 
1ciderdog's Avatar


 
Join Date: Jun 2010
Posts: 4,325
I agree with wa8yxm
__________________
Bob, Sandi & Marmaduke the Big Pug
SW OREGON 2004 Journey 39K, 330 Cat
If towing: a 2006 Mini Cooper or 1995 Wrangler
1ciderdog is offline   Reply With Quote
Old 02-23-2014, 11:37 AM   #8
Senior Member
 
Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 5,217
With a proper flare it doesn't take a Herculean effort past snug to get a reliable seal with a properly made flare.

Personally I wouldn't use locktite on this type of joint. The way to check it "down the road" is the same as making it in the first place. Put a wrench to it then apply leak detector. Locktite would get in the way of a pepper check IMO.
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
EngineerMike is offline   Reply With Quote
Old 02-24-2014, 07:06 AM   #9
Senior Member
 
Damon Owners Club
Ford Super Duty Owner
Join Date: Apr 2008
Location: NAS Pensacola, FL
Posts: 329
To All,

Thanks for the help. I agree that this should not have happened but it did. When something weird happens that shouldn't have happened one must look at the history of maintenance or installation. I'm the sole owner and I've never touched the water heater. That leaves initial construction. Maybe the heater was installed on a Friday at the factory or maybe stuff just happens. Thanks again.
__________________
Ted Fulltiming in the DreamCatcher a
2008 Challenger 371PE on F53 w/ 2010 Cobalt
R'V there yet?
teddyu is offline   Reply With Quote
Old 02-24-2014, 07:13 AM   #10
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: St. Lucie West, FL
Posts: 5,113
Quote:
Originally Posted by EngineerMike View Post
With a proper flare it doesn't take a Herculean effort past snug to get a reliable seal with a properly made flare.

Personally I wouldn't use locktite on this type of joint. The way to check it "down the road" is the same as making it in the first place. Put a wrench to it then apply leak detector. Locktite would get in the way of a pepper check IMO.
Agree ... Loctite probably won't hurt except for future tightening (a check of tightness). Not likely to be needed.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 02-24-2014, 07:24 AM   #11
RVM #74
 
PushedAround's Avatar


 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
It is possible to over-torque a flare nut. It is not the nut that is the issue, but the shoulder of the flare. If you crush the copper too much it will become brittle and prone to cracking. Parker and a few other mfgs do publish torque values, but in general, just tighten it enough to feel the copper crush, and then stop.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 02-24-2014, 07:32 AM   #12
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: St. Lucie West, FL
Posts: 5,113
Quote:
Originally Posted by PushedAround View Post
It is possible to over-torque a flare nut. It is not the nut that is the issue, but the shoulder of the flare. If you crush the copper too much it will become brittle and prone to cracking. Parker and a few other mfgs do publish torque values, but in general, just tighten it enough to feel the copper crush, and then stop.

That's certainly better than the "tighten until it strips, then back off 1/4 turn" theory
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 02-24-2014, 09:03 AM   #13
Senior Member
 
Join Date: Nov 2007
Location: somewhere in the west
Posts: 1,168
The term "torque" does not really apply when talking about copper fittings. Torque is a measurement of the force against something, where with copper fittings threads are "mismatched" a little, supplying a joining of the two threaded surfaces.

Ed
__________________
Ed-Sommers is offline   Reply With Quote
Old 02-25-2014, 04:44 AM   #14
Registered User
 
Join Date: Aug 2013
Posts: 307
Flare fittings and compression fittings are actually made to be used with no thread sealers. Thread sealers will not let the surfaces mate up properly.

I've seen so much Teflon tape on some flare fittings that the nut wouldn't even pull the flared copper to the fitting.
__________________

__________________
malexander is offline   Reply With Quote
Reply

Tags
propane



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hydronic heat: Propane vs Diesel in winter temps? TinMan Trvlr RV Systems & Appliances 10 03-31-2014 03:32 PM
Propane Gas Smell jlabit Class A Motorhome Discussions 23 02-11-2014 08:59 AM
Can not get propane to MH from Tank guaranteed Class A Motorhome Discussions 28 01-18-2014 10:11 AM
What can happen to a MH in 10 below zero (long) brobox Entegra Owner's Forum 32 12-30-2013 01:26 PM
My Dometic 3Way Fridge On Propane Libero RV Systems & Appliances 3 10-04-2013 05:40 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:45 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.