Old 07-25-2018, 05:25 PM   #15
Senior Member
 
manderson2228's Avatar
 
Tiffin Owners Club
Nor'easters Club
Appalachian Campers
Carolina Campers
Join Date: Sep 2016
Posts: 673
Quote:
Originally Posted by Freqz View Post
The AC compressors are rated at 95 degrees: as you go up in temp you go up in current. By 115 it’s 4 amps per compressor [emoji33]. It’s a lot and something g I’m struggling with designing a system to keep me cool in West Texas on 30 amps.

I bet at 95 you fire up both just fine.

If it does, I wonder if the starting surge is getting you or the running amps? If it’s the starting sure a couple of $300 easy starts from micro air could be your ticket...

I'm not arguing with you on the amp increases at additional heat. I am just curious where you got that information. I've not heard that before and would like to read up on it a little bit.
__________________
-Mike
2020 Tiffin Open Road 34PA
manderson2228 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-25-2018, 05:56 PM   #16
Senior Member
 
Freqz's Avatar
 
Join Date: Aug 2017
Posts: 1,020
Quote:
Originally Posted by manderson2228 View Post
I'm not arguing with you on the amp increases at additional heat. I am just curious where you got that information. I've not heard that before and would like to read up on it a little bit.


For instance:

https://www.airxcel.com/docs/default...e.pdf?sfvrsn=5

__________________
2018 ORV Timber Ridge 24rks
2017 F350 6.7 CC DRW
Freqz is offline   Reply With Quote
Old 07-25-2018, 08:58 PM   #17
Senior Member
 
Join Date: Jul 2014
Posts: 35,439
If the engine was weak, bogging down, and unable to create enough power, it would slow down until the voltage dropped below 100 volts. At that point, the " Auto Transfer Switch " would open and the engine would recover, starting the cycle again in 30 seconds when it closes again.

If your engine is bogging down and dropping dead, its a fuel or ignition problem.

If the fuel system is in good shape, I would then suspect loss of ignition, possably from an overheat.

Here is a Harbor Freight ignition tester. Hook it up, run the generator until it shuts down, and see if it keeps sparking as it dies.

https://m.harborfreight.com/90-in-li...not%20provided
twinboat is online now   Reply With Quote
Old 07-26-2018, 10:03 AM   #18
Senior Member
 
tada's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2018
Location: Tucson, AZ
Posts: 134
Unfortunately I’m out of commission for a week. Yesterday afternoon I had an appointment with a retinal specialist for a large dark area in my vision. He found my retina had partially detached and I had emergency surgery. Now under his orders, I have to lay in bed for a week and can’t do any mechanical work.

By the time it heals, the temperature will have dropped and I’ll be able to do some more troubleshooting. Thanks to everyone for all the input, Tom.
tada is offline   Reply With Quote
Old 07-26-2018, 12:42 PM   #19
Senior Member
 
Freqz's Avatar
 
Join Date: Aug 2017
Posts: 1,020
Ouch. Good luck and speedy healing!
__________________
2018 ORV Timber Ridge 24rks
2017 F350 6.7 CC DRW
Freqz is offline   Reply With Quote
Old 07-27-2018, 10:12 AM   #20
Senior Member
 
Join Date: Oct 2005
Posts: 1,224
Just realized when I run both ACs on the genny they are sharing the neutral which is true when plugged in but the difference is the genny legs are in sinc while shore power they are opposite canceling the loadWith the genny that means the neutral gets both sides of the load and is overloaded.Not sure I explained this right but the neutral got pretty hot.
bldrbob is offline   Reply With Quote
Old 07-27-2018, 10:34 AM   #21
Senior Member
 
tada's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2018
Location: Tucson, AZ
Posts: 134
It’s 92° this morning and I had my wife start the generator and both ACs about an hour and a half ago. So far so good. It really may be heat related.

In my spare time I’ve been reading threads on the Onan generators. Apparently they had two fuel filters. One pre pump that attached directly to the pump, and a secondary filter that attached to the carb. When I tuned up the carb there was only one filter - the one attached to the carb which I changed. In one of the threads I read it said that that filter should be eliminated at replaced with an Onan adapter that has no filter and that the pre pump filter should be installed. Do you think that would help with fuel starvation issues under load?
tada is offline   Reply With Quote
Old 07-27-2018, 03:34 PM   #22
Senior Member
 
tada's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2018
Location: Tucson, AZ
Posts: 134
An update

I let the generator and both ACs run for approximately five hours in 105° heat. I had to leave for a doctors appointment. The generator kept running the whole time. But I came back to find both ACs completely off with the Intellitec thermostat showing both ACs in a shed condition. I tried restarting them with the thermostat switch. Neither would come on. I finally powered everything down including the generator and contacted the shop who installed the ACs. They are hoping that a low voltage condition did not damage the circuit boards on the ACs. Not a good day for me.

Edit: I found the main 30A and AC 20A breaker in the coach had tripped. I reset them and have the 15k BTU unit running at present. So the AC units are still ok. But the Intellitec EMS is not shedding correctly. If it was, the breakers should not have tripped. Or the electrical part of the generator is acting up. Or it’s just too damn hot in the desert right now!
tada is offline   Reply With Quote
Old 07-27-2018, 05:16 PM   #23
Senior Member
 
Join Date: Jul 2014
Posts: 35,439
Quote:
Originally Posted by bldrbob View Post
Just realized when I run both ACs on the genny they are sharing the neutral which is true when plugged in but the difference is the genny legs are in sinc while shore power they are opposite canceling the loadWith the genny that means the neutral gets both sides of the load and is overloaded.Not sure I explained this right but the neutral got pretty hot.
There should be 2 white, ( neutral ) wires coming from the generator.
twinboat is online now   Reply With Quote
Old 07-27-2018, 05:16 PM   #24
Senior Member
 
tada's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2018
Location: Tucson, AZ
Posts: 134
Ok, I fired up the rear AC and saw the EMS shedding correctly. But after about 10 minutes the rear compressor came on and killed the generator. Maybe adding two easy starts would solve this problem.
tada is offline   Reply With Quote
Old 07-29-2018, 04:43 PM   #25
Senior Member
 
Join Date: Nov 2009
Posts: 1,152
I had a TT that had a no name unit on it and it took about 22 amps to run it, and almost killed a 3500 watt generator to start it. IIRC it was a Chinese unit.
I have also seen u-tube videos where they starting draw on the Coleman unit on different coaches would draw about 85 amps on start up.
I have 35' Winnie with 2 small units on it and 30 amp service. Has a type of load controller that only lets one unit start at a time. I tested my units and they draw about 25 amps to start and each draws about 8 amps in the heat in Phoenix, about 6 amps here in Michigan.
Not sure if Coleman is still making their units or importing them but this is not the first I have heard of new units not wanting to run on the system that was powering the old ones.
leadman is offline   Reply With Quote
Old 07-29-2018, 05:08 PM   #26
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvul", TN
Posts: 1,665
Quote:
Originally Posted by leadman View Post
I had a TT that had a no name unit on it and it took about 22 amps to run it, and almost killed a 3500 watt generator to start it. IIRC it was a Chinese unit.
I have also seen u-tube videos where they starting draw on the Coleman unit on different coaches would draw about 85 amps on start up.
I have 35' Winnie with 2 small units on it and 30 amp service. Has a type of load controller that only lets one unit start at a time. I tested my units and they draw about 25 amps to start and each draws about 8 amps in the heat in Phoenix, about 6 amps here in Michigan.
Not sure if Coleman is still making their units or importing them but this is not the first I have heard of new units not wanting to run on the system that was powering the old ones.
What is the BTU rating on an air conditioner that only draws 8 amps?
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2018 Grand Design Momentum 394M Toy Hauler
Excessive Payload Capacity is a Wonderful Thing!
xrated is offline   Reply With Quote
Old 07-29-2018, 07:50 PM   #27
Senior Member
 
tada's Avatar
 
Fleetwood Owners Club
Join Date: Jun 2018
Location: Tucson, AZ
Posts: 134
I’ve ordered two hard start capacitors from Amazon that will be here Tuesday. Looks like an easy install. I’ll report the results.
tada is offline   Reply With Quote
Old 07-30-2018, 05:09 AM   #28
Senior Member
 
gatorcq's Avatar
 
Freightliner Owners Club
Join Date: Apr 2004
Location: Show Low Az
Posts: 1,325
put them on LOW, then report back
__________________
Dale&Susan, 08 Alfa Gold, DaGirlsRv Blog
2015 F-150XLT_2000W Solar_800 AmpHr Lithium
Magnum_MSH 3012 & PT100
gatorcq is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Running Both A/C units on Generator tmarie416 Monaco Owner's Forum 4 08-22-2016 08:27 PM
getting both A/C units running at same time rpelrod Class A Motorhome Discussions 23 06-19-2015 01:02 PM
A/C units both work well for 15 t0 45 min then BOTH shut down baustin RV Systems & Appliances 2 09-26-2014 06:57 PM
Running both roof A/C units rlancast National RV Owner's Forum 27 07-02-2013 01:23 AM
Running both A/C units with genset Heater Fleetwood Owner's Forum 31 10-30-2011 04:44 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:47 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.