Running both the A/C and microwave while on generator

We have a Cummins Onan QG 4kw model in our 2010 Fleetwood Encounter it will run the A/C or the microwave just fine. But if we have the A/C on and then start the MW, the generator will slowly start to bog down at 15-20 seconds, then die after about 30-40 seconds.

The genny should produce 33amps, the A/C (I believe) is 15k btu, and the microwave is probably about 900-1000w. The compressor is running, not cycling on and off when this occurs.

Sometimes I have noticed that the genny will hesitate slightly when the A/C is running, then resumes normal RPMs. I exercise it at least once a month and it always starts right up, unless it's very hot and it has vapor locked, when I turn it off, then try to restart it before its cooled off.

Does anyone have any ideas or solutions? Or is this just normal, and its not made to handle both the A/C and MW at the same time. Thanks in advance for your input!


Percival6 is online now   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-05-2015, 05:59 PM   #2
Senior Member
Johndale's Avatar

Winnebago Owners Club
Join Date: Sep 2013
Location: Ft Worth texas
Posts: 823
You are pushing your limit on amps. I trained my wife what I call the Lisa Douglas theory from green acres. Always watch your amp gauge and stay below 30 amps. I have a 5.5 and it works mine real good but not like yours. Check around and see what else you have plugged in.

Sent from my iPhone using iRV2 - RV Forum

2003 Sightseer 33L
Ford F53
Johndale is offline   Reply With Quote
Old 08-05-2015, 06:02 PM   #3
Senior Member
jacwjames's Avatar
Monaco Owners Club
Join Date: Jun 2014
Posts: 3,598
You generator as a 4kw, at 120 volt output it can produce ~33amps of power less ~10% efficiency so say 30 amps of available power. The AC unit will probably pull ~15 amps, possibly more. The microwave probably 8 amps.

Are you using any lights? I assume you have a converter or inverter on you RV. What else might you be running, exhaust fans, On my coach there is about 4 amp draw . If the refrig is running on electric that could be another couple amps. Even with this additional load you are still only at ~30 amps?

There could be a possibility that the AC unit is starting to fail pulling higher amps. You might have to get a load meter and test.

My blower motor was starting to seize up causing the breaker to trip on a more regular basis. When I replace it and had it out on the workbench I could barely turn the shaft by hand.
Jim J
2002 Monaco Windsor 38 PKD
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 08-05-2015, 06:37 PM   #4
Senior Member
Join Date: Jul 2014
Posts: 5,498
You need to check the watts input on the microwave. A 900 watt microwave is the cooking wattage.

A 900 watt microwave will pull pulling 1450 watts, per Hamilton Beach.

That puts you right at the border of your generator output with a little over 12 amps for the microwave and 15 amps or more with a dirty condenser coil.

You could try changing the gas filter to see if it helps.

I would see if the 4000 watt output is surge or continuous output.
twinboat is online now   Reply With Quote
Old 08-05-2015, 06:50 PM   #5
Senior Member
Deny's Avatar
Winnebago Owners Club
Join Date: Feb 2014
Posts: 741
Just get in the habit of turning off the A/C before you run the Microwave. No good reason to cause issues with a good Generator. Issues with Generators are expensive.

PS- A/C on and Hot water heater on electric, plus a few lights, converter,etc, NOT counting the Microwave--shows a 30AMP draw on my Progressive Industries Electric Mgt system (Winnebago view 2014). If the Power Pole is not in good shape, with plenty of power,it will kick a breaker on the Pole
Deny is online now   Reply With Quote
Old 08-05-2015, 08:20 PM   #6
Senior Member
Join Date: Aug 2014
Location: S.F. Bay Area
Posts: 120
Yes, I have gotten into the habit of turning the A/C off, but then it will be about 3 to 4 minutes before it kicks back on, even if I only use the MW for 45 seconds.

I will sometimes have the vent on over oven, the one thing I didn't think about was the refrigerator being on auto and switching over to AC when the genny comes online. I'll have to check that next time.

I have about 400 watts of solar on the roof and will usually encounter this problem when on the road and stop for lunch, so the batteries are typically fully charged.

I hope the A/C unit isn't going bad! Last thing I want is an expense like that. Maybe it is just right at the limit of the generator. I'll have to check on phantom loads next time we're out.

Thanks for advice so far!
Percival6 is online now   Reply With Quote
Old 08-05-2015, 08:24 PM   #7
Senior Member
Santara's Avatar
Forest River Owners Club
Ford Super Duty Owner
Join Date: Aug 2010
Location: S florida
Posts: 253
have started puttin refig on gas when cooking
Rick & Barbara
"98" 30 'Coachmen C Santara FL (front lounge) V 10
TST tpms, ScanGauge 2 cats Tyler,Lucy
Santara is offline   Reply With Quote
Old 08-05-2015, 08:29 PM   #8
Junior Member
Join Date: Jul 2015
Location: Where ever it's parked.
Posts: 16
Borrow a good Fluke meter and check the voltage and frequency of the generator output. If low Hz or v, then your inductive loads like the AC and MW will draw higher current than at full voltage.
Spada84 is offline   Reply With Quote
Old 08-05-2015, 08:36 PM   #9
Senior Member
jondrew's Avatar
Join Date: Jan 2014
Location: Orlando
Posts: 1,687
Something doesn't sound right here. If you exceed the load capacity of the generator you should pop the breaker, not kill the generator. I think you have an issue with your generator. I think getting an AC ammeter as others suggested is a good idea. Possibly your generator breaker is not functioning correctly.
2015 Fleetwood Discovery 40G
2014 CRV w/EZ Tow
jondrew is offline   Reply With Quote
Old 08-05-2015, 09:01 PM   #10
Senior Member
Dtwallace's Avatar
Join Date: May 2014
Posts: 808
With a 4KW genset, and trying to operate all of the mentioned equipment at one time, you are overloading the genset.

A 5.5 will be at the edge with the load you are putting on your 4.0. The only thing you can do is cut back on the load by selecting only the items that can be run without overloading your genset.

If you are not planning to change units in the near future, you could consider upgrading your genset to at least a 5.5kw model. The cabinetry should be the same size but that something you'd have to verify that.

By the way, like mentioned above, you should be tripping a breaker not bogging down the genset when you do overload it. This could be a sign of a failed or bypassed breaker, not good at all.
Dan & Loretta, US Army Retired Aero Scout Pilot
2012 Fleetwood Providence 42P Class A/DP
Spartan Chassis, 8.9L Cummins 450HP
Dtwallace is offline   Reply With Quote
Old 08-06-2015, 06:52 AM   #11
Senior Member
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 21,176
AC 13-15 amps depending on make, model, how long since you cleaned the condenser, other things.
Microwave about 11 amps
Water heater 10-12
Fridge measured yesterday 2-3
15+11+11+3=40 amps
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 08-06-2015, 10:33 AM   #12
Senior Member
Join Date: Aug 2014
Location: S.F. Bay Area
Posts: 120
Thanks all! I will check on the condenser, then find out what the power output of the generator is doing. If voltage is low that will also pull more amps, right?
Percival6 is online now   Reply With Quote
Old 08-06-2015, 02:09 PM   #13
Senior Member
milasman's Avatar
Fleetwood Owners Club
Join Date: Apr 2012
Posts: 863
You have a problem with the contoll board of the generator, shuts generator off with load under 30 amps. As board progressively gets worse, it will shut generator off when A/C cycles on the pump. Vapor lock is not keeping you from restarting the generator, it is the controller board over heating. One thing you can do now is turn A/C off and leave fan running, then run microwave. With my controll board, sometimes turning off A/C would shut generator off. I amp measured every possible combination of running different things, usually it took three major things to go over 30 amps. A/C, microwave, electric hot water, fridge and a few lights measured to 28 amps. If you push over 30, the breaker should trip before genny shuts down. You could try checking trouble codes, but that usually a wild goose chase.
milasman is offline   Reply With Quote
Old 08-09-2015, 08:48 AM   #14
Senior Member
Join Date: Aug 2014
Location: S.F. Bay Area
Posts: 120
Ok, so got some readings from the generator yesterday. Ran it with no loads and it's output was 121.1vac, the frequency was around 180hz. Turned on the A/C, voltage dropped to 119.5, but was steady. Frequency varied between 60 and 62hz, and was fairly steady.

I made sure the refrigerator was off and switched off the converter at the breaker panel. MH doesn't have electric water heater. So only major sources of power consumption are the a/c and the microwave.

While the a/c was running, I turned on the microwave, generator became erratic, surging up and down, voltage began to drop 115, 112, 109, 104, 102 then the engine stalled. Frequency was all around 120hz and very erratic.

After restarting the generator, ran the MW by itself, voltage was steady around 114vac, but the frequency was wildly fluctuating between 142 and 155 hz. Checked what the MW was drawing with a WattsUp unit, peaked at 2.4kw, then held steady at 1.3kw.

Now the meter I'm using is not a Fluke, but has been reliable and is pretty good quality. Thinking something might be wrong with it, I took it inside to check what it would do with shorepower. It showed a steady 119.9 vac and 59.997 hz. No hunting, perfectly steady.

Today, while out on a day trip to the beach, we ran the generator for about 1/2 hour to heat up a few things in the MW. Longest the MW was on was 4 minutes at one time, on one of the shorter warm ups, the generator started surging. I shut off the microwave, then turned it back on, and the generator was fine.

It seems like the generator and microwave don't get along too well and when you throw in the A/C, all hell breaks loose. Yeah, it would be easy enough to only run one thing at a time, but it certainly seems something is wrong. Any ideas?

I have an extended warranty, so I will probably contact a local Cummins service facility this week, and would like an idea what to say a where to point them.

Thanks to everyone for their input!


Percival6 is online now   Reply With Quote


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
Generac Generator won't keep Microwave going. nordic tug National RV Owner's Forum 5 05-28-2015 10:38 PM
Inverter not running microwave or recep. llbwrb Class A Motorhome Discussions 11 12-27-2014 05:22 PM
Microwave not running with generator tom6908 RV Systems & Appliances 3 05-19-2014 03:30 PM
Found convection microwave running wstrace3 Thor Industries Owner's Forum 14 03-29-2014 02:35 PM
Coachmen: a/c all outlets, microwave not working when generator running/ ladyrvr66 Forest River Owners Forum 5 07-14-2013 03:43 AM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities

Copyright 2002-2015 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:12 AM.

Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.