Running The Generator

I was wondering if you want to run the generator just to keep the oil circulated and the battery charged up during long periods the motor home in storage do you have to have the coach unplugged from shore power?

Thank you in advance for the help.
__________________

__________________
Dave, Vanessa & Mindye
SFC E-7, US Army Retired
2003 Kit Road Ranger 5th Wheel
dvkiel is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-12-2014, 08:42 AM   #2
Senior Member
 
JayGee's Avatar
 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Apr 2001
Location: East Tennessee
Posts: 338
Yes. You need to run the generator with a load monthly at least just for the good of the generator.
Your batteries should be disconnected if there is no power source for them for an extended period of time. There are "things" that will drain them to no charge which will kill the life of your battery.
__________________

__________________
JayGee
Foothills of the Smokies
2005 Bounder 35E
JayGee is offline   Reply With Quote
Old 10-12-2014, 05:10 PM   #3
Senior Member/RVM #90
 
MSHappyCampers's Avatar


 
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 26,326
We run the genny about 30 minutes each month with both A/C's on!
__________________
Joe & Annette

2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
MSHappyCampers is online now   Reply With Quote
Old 10-12-2014, 06:47 PM   #4
Senior Member
 
Selah's Avatar
 
Join Date: Oct 2012
Location: Indiana
Posts: 2,319
I don't know your particular coach but with newer coaches I don't believe you need to unplug to run the generator under load. The transfer switch is either on shore power or on generator (the default). Once the generator comes up to speed the transfer switch will disconnect from shore and shift to the generator all by itself. No intervention required.
When the generator is shut down the transfer switch will automatically change back to shore power.
Again, I only have experience with newer coaches so you should probably check your particular system manual if possible.
__________________
Paul, Kathy, and Tux the Mini Schnauzer
2014 Tiffin Phaeton 42 LH, 2013 Honda CRV
"When the time comes to look back, make sure you'll like what you see"
Selah is offline   Reply With Quote
Old 10-12-2014, 07:16 PM   #5
Senior Member
 
WReeder's Avatar
 
Winnebago Owners Club
Join Date: Nov 2013
Posts: 228
If you don't use it you going to loose it! Run the generator every chance you can! They are made to use not sit!
__________________
WReeder is offline   Reply With Quote
Old 10-12-2014, 07:17 PM   #6
Senior Member
 
Mr_D's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 28,491
Quote:
Originally Posted by Selah View Post
I don't know your particular coach but with newer coaches I don't believe you need to unplug to run the generator under load. The transfer switch is either on shore power or on generator (the default). Once the generator comes up to speed the transfer switch will disconnect from shore and shift to the generator all by itself. No intervention required.
When the generator is shut down the transfer switch will automatically change back to shore power.
Again, I only have experience with newer coaches so you should probably check your particular system manual if possible.
It's best to unplug from shore power to lessen the load on the transfer switch.
On our rig I run the gen set an hour or so with the heat pumps on. For ½ hour I run one on heat and the other on cool, then switch that around for the last ½ hour.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is online now   Reply With Quote
Old 10-12-2014, 07:23 PM   #7
Senior Member
 
Country Coach Owners Club
Join Date: Jan 2006
Location: Redding
Posts: 3,412
Content in Error. Post removed by author.
__________________
Dean
1995 CC Magna #5280
C8.3L 300hp Cummins, 31,000lbs
deandec is online now   Reply With Quote
Old 10-12-2014, 07:34 PM   #8
Senior Member
 
Join Date: Dec 2013
Posts: 168
No need to unplug from shore power. Make sure the AC units are Off though, prior to any transfer of the ABT.

JohnnyB
__________________
2014 ShowHauler 45'
2014 Dodge Ram 1500 Laramie
brunsje is offline   Reply With Quote
Old 10-13-2014, 09:25 AM   #9
Senior Member
 
Hooligan's Avatar
 
Freightliner Owners Club
Join Date: Apr 2002
Location: Pensacola
Posts: 2,206
Onan maintenance manual:
"If use is infrequent, the genset should be exercised at least 2 hours per month at 1/2 rated power. Exercising drives off generator moisture, provides fresh fuel, lubricates the engine, and removes oxide from the electrical contacts and slip rings. A single two hour exercise is better than several shorter periods."

Good in theory but may be hard to accomplish if access to the stored MH is inconvenient. Luckily my MH stores alongside the house.
__________________
Hooligan, Pensacola, Fl -U.S. Coast Guard 1956-1985
2016 Thor Siesta Sprinter 24ST diesel
Our Pug "Lily" & "George" the Newfoundland
Hooligan is offline   Reply With Quote
Old 10-21-2014, 08:20 PM   #10
Senior Member
 
Join Date: Jan 2014
Posts: 141
Two years ago I started the generator with shore power connected…….it immediately tripped the circuit breaker on the shore power circuit and also wrecked my inverter….and a year later the transfer switch stopped working.

I'll never do that again.
__________________
bobguigley is offline   Reply With Quote
Old 10-22-2014, 06:13 AM   #11
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
Quote:
Originally Posted by bobguigley View Post
Two years ago I started the generator with shore power connected…….it immediately tripped the circuit breaker on the shore power circuit and also wrecked my inverter….and a year later the transfer switch stopped working.

I'll never do that again.
If it tripped the shore power supply side breakers then your transfer switch was already damaged long before that happened. The contactor blades were welded together so even though the solenoid disconnected, the shore and generator sides were still tied together. While running the generator your shore cord male end terminals were probably live as well. Welded contactor blades are usually indicative of high amperage switching (running Air Conditioners) from shore to genset or vice versa. There is absolutely no problem letting the transfer switch automatically from shore to genset - it's what they're designed to do - it's just best not to do it while AC's are running - otherwise it can weld the contactor blades together over time.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 10-22-2014, 12:21 PM   #12
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 3,225
I play it safe and shut down shore power before starting the generator.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 10-27-2014, 08:50 AM   #13
Senior Member
 
Join Date: Jun 2014
Posts: 118
I believe that I will agree with you and play it safe and disconnect from the shore power, just to be safe. Thank you,
__________________
Dave, Vanessa & Mindye
SFC E-7, US Army Retired
2003 Kit Road Ranger 5th Wheel
dvkiel is offline   Reply With Quote
Old 10-27-2014, 03:53 PM   #14
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,811
Though you may be citing an exception, with the RV in storage you should either unplug upon arrival, then start the generator for the required run of 1/2 hour under 1/2 load or more in both cases, then shut down and plug back in before leaving -or- (this is how I do it here in the CG were I am "Stuck") turn off the main breakers, start generator, then turn them back on (making sure air condititoners, if running, are shut down at least 3 minutes) and follow the same process when I shut down.

Shut off main breakers, kill generator, wait 3 minutes, restore power.
__________________

__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help Onan 8000 Generator issue adonh Class A Motorhome Discussions 15 07-22-2014 04:49 PM
Generator Problem RJEV MH-General Discussions & Problems 2 07-08-2014 08:00 PM
Generator won't stay running CdnCruiser RV Systems & Appliances 10 07-06-2014 12:39 PM
Can I install a small fuel tank in my generator box. Jasper7821 RV Systems & Appliances 13 01-28-2014 03:03 PM
Champion 2000 Watt Inverter Generator chboone RV Systems & Appliances 0 09-25-2013 12:03 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:14 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.