Starting the generator
Hello everyone I have a question the other night it was really cold and unleveled where I had my unit parked . When I woke up I noticed my batteries were low so I attempted to start the generator. It would not start even after five try's . Once I drove the unit a couple of miles away to a local store. I tried it again and it started. What was the reason it didn't start. would it be because it was too cold or more likely that the unit was unleveled?
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
02-17-2015, 12:34 AM
|
#2
|
Registered User
Join Date: Jul 2011
Posts: 2,427
|
Quote:
Originally Posted by on2thenext
Hello everyone I have a question the other night it was really cold and unleveled where I had my unit parked . When I woke up I noticed my batteries were low so I attempted to start the generator. It would not start even after five try's . Once I drove the unit a couple of miles away to a local store. I tried it again and it started. What was the reason it didn't start. would it be because it was too cold or more likely that the unit was unleveled?
|
What kind of coach do you have? Most coaches use the house batteries to start the gen. If you were running the furnace blower fan a lot during the night, your coach batteries were drained. They may be a problem. Running the engine charged them enough to get the gen started. Level or not would not matter unless you were close to 1/4 full on gas. Most gens get the gas from the tank through a line mounted about 1/4 way up the tank so you can't run the coach out of gas by running the gen.
|
|
|
02-17-2015, 12:42 AM
|
#3
|
Senior Member
Fleetwood Owners Club Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
|
When it would not start was it cranking slow? If yes, low battery which gained a charge by driving the coach.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
|
|
|
02-17-2015, 03:21 AM
|
#4
|
Senior Member
Workhorse Chassis Owner
Join Date: Oct 2007
Location: South Jersey
Posts: 1,083
|
Sitting unlevel the low oil sensor may have stopped the gen from starting. Once moved the oil level probably came up to the sensor and let it start.
__________________
Kathy & George Zimm
Mickleton, NJ
2006 Coachman Epic & 2013 Chevy Equinox Toad
|
|
|
02-17-2015, 05:37 AM
|
#5
|
Senior Member
Join Date: Nov 2005
Posts: 3,968
|
Several reasons for not starting have already been mentioned. You didn't mention how low the fuel tank was, or how "out of level" you were. The fuel pickup tube for the generator usually only goes down to about 3/4 of the tanks capacity. If you were low on fuel and not level the combination might have been enough to have the pickup tube out of the fuel.
Also if you have an Onan generator the carburetor can be primed by holding the switch in the OFF position until the green light in the switch comes on. What you're actually doing is running the fuel pump to fill up the carb. If the generator hasn't been run for a while (especially when the vehicle isn't level) it's possible the fuel level in the carb had gotten low enough that the generator wouldn't start
__________________
Hikerdogs
2013 Adventurer 32H
|
|
|
02-17-2015, 05:42 AM
|
#6
|
Senior Member
Monaco Owners Club Vintage RV Owners Club
Join Date: Feb 2015
Location: East Texas
Posts: 716
|
I'd vote for Low batteries or if LP choke not working..
|
|
|
02-17-2015, 07:51 AM
|
#7
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
Two answers:
First, if the generator fails to start.. ASK IT WHY (the procedure is in the owner's manual) most modern RV generators have On Board Diagnostics (OBD) It is kind of an OBD-1 system (not as advanced as the OBD-II on your car or motor home) but this means you do not need special tools... Just the STOP button. a note book, your eyes, a pencil and a code book. (The owner's manual is the code book).
Second: The generator usually starts on the house batteries (Many exceptions though) so if the house batteries are LOW you will not get it to start normally.
Suggestion if it happens again... Try the EMERGENCY START (may be called AUX start or BOOST) this will parallel the chassis battery with the house batteries.
The Aux/Emergency/Boost start switch is a built in jump starter,, Generally works both ways. Done it more times than I care to admit.
__________________
Home is where I park it!
|
|
|
02-17-2015, 09:09 AM
|
#8
|
Senior Member
Join Date: Dec 2014
Posts: 102
|
Okay thank you all. From what you're saying I think my batteries were too low to start the generator and when I drove down the road a few miles to a local store it must have charged The batteries just enough to start the generator.
|
|
|
02-17-2015, 12:16 PM
|
#9
|
Senior Member
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,600
|
I owned a Class C that only had 1 small battery for the coach. It would run the 12 volt light, refrigerator, fantastic fan, and furnace. If we ran either the furnace or fan all night there would not be enough voltage to start the generator.
I installed a 2nd battery with a selector switch where I could use either batter or both batteries. I but the selector switch in a convenient location in the coach. At night I would only pull off of 1 battery and then in the AM switch to the 2nd battery to start the coach.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
|
|
|
02-22-2015, 08:51 PM
|
#10
|
Member
Tiffin Owners Club
Join Date: Dec 2014
Posts: 42
|
First time I started my generator in the middle of the night at 26 degrees, I had to hold the start button down for about 8 seconds while it primed the generator. It was making a clicking sound like a car with a low battery....
however once it got primed, it fired right up....
__________________
2015 Allegro Bus 45UP • 2015 Chevrolet Equinox LT • BlueOx Baseplate, Aventa LX Towbar, RVIBrake 2
|
|
|
02-25-2015, 02:11 PM
|
#11
|
Senior Member
Join Date: Feb 2015
Location: ct
Posts: 252
|
Some also have a lever to switch from summer use to winter use. Maybe you should look to see if yours has one.
|
|
|
02-26-2015, 12:50 AM
|
#12
|
Senior Member
Join Date: Dec 2014
Posts: 102
|
Quote:
Originally Posted by edsperfect
Some also have a lever to switch from summer use to winter use. Maybe you should look to see if yours has one.
|
Really I did not know that
|
|
|
02-26-2015, 01:02 PM
|
#13
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 54,780
|
Quote:
Originally Posted by wa8yxm
Two answers:
First, if the generator fails to start.. ASK IT WHY (the procedure is in the owner's manual) most modern RV generators have On Board Diagnostics (OBD) It is kind of an OBD-1 system (not as advanced as the OBD-II on your car or motor home) but this means you do not need special tools... Just the STOP button. a note book, your eyes, a pencil and a code book. (The owner's manual is the code book).
Second: The generator usually starts on the house batteries (Many exceptions though) so if the house batteries are LOW you will not get it to start normally.
Suggestion if it happens again... Try the EMERGENCY START (may be called AUX start or BOOST) this will parallel the chassis battery with the house batteries.
The Aux/Emergency/Boost start switch is a built in jump starter,, Generally works both ways. Done it more times than I care to admit.
|
X2!
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
02-26-2015, 01:34 PM
|
#14
|
Senior Member
Vintage RV Owners Club Fleetwood Owners Club
Join Date: Mar 2013
Location: c above
Posts: 5,525
|
Did they have that back in 82? Pushing the start button to prime the gennie?
I never heard of that either.
Tim
__________________
1982 Pace Arrow P30 454
KarKaddy SS, Toad: 2009 Genesis
Tim, Joe and Lilly too. Mpls Minn.
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|