I have the below rig in my sig with the Onan 4.0kW MicroQuiet Generator. The genset wouldn't run when a load was applied. The fault code I received was an over-voltage fault, code # 12 I believe it was.

Took the rig to the dealer a month ago. They took it to Cummins and Cummins claims the genset works just fine when they power it up isolated from the motorhome. So, now it is back to the dealer. Cummins thinks it must be the converter or something else.

The converter? A converter converts AC to DC. When the rig is plugged into AC power, everything works just fine. Something sounds a bit fishy about this.

1. The rig's electrical system works fine when plugged in
2. The genset will not run when a load is applied.
3. The genset's built in self diagnostic code reveals an over-voltage code.

What else could be the problem if the genset is working properly????

__________________
2010 Fleetwood Encounter 32BH
Blue Ox Aladdin - 1998 Altima
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-09-2011, 11:53 AM   #2
GaryKD is offline
Senior Member
GaryKD's Avatar


Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 6,933
Hi jtroop,
I do not know your coach. Based on the information in the OP, consider looking at the transfer switch. Make sure it is passing power within spec. Next I'd check the voltage at the generator (both lines).

Is there a specific load the generator does not like (HWH, A/C, micro wave, etc.)? If that is the case, something in that circuit may be the cause of pulling too much power.

__________________
Gary
2005 Newmar KSDP 3910,
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
  Reply With Quote
   
Old 05-09-2011, 12:01 PM   #3
Cat320 is online now
Senior Member
Cat320's Avatar


Fleetwood Owners Club
Join Date: Mar 2011
Posts: 1,393
I'm not that familiar with your coach, but do you even have a converter...I don't.
__________________
2009 Amer Coach Allegiance 40X With Spartan Chassis
400 HP Cummins ISL
Pulling a Honda CRV
  Reply With Quote
   
Old 05-09-2011, 01:05 PM   #4
Buford B is offline
Member
Monaco Owners Club
Join Date: Nov 2009
Posts: 87
What load do you apply when it faults out? Don't forget that you are converting AC to DC to charge your coach batteries. That said try turning off the main breaker in the coach, fire up the genset and see what happens. Have you turned off the breaker at the genset, to make sure the genset itself is not the problem?
__________________
Buford B.
Aero AT4040XL, AFE, Koni FSD,
Source Eng. Trailing Arms
  Reply With Quote
   
Old 05-09-2011, 01:58 PM   #5
Hikerdogs is offline
Senior Member


Join Date: Nov 2005
Posts: 883
I think the Cummins dealer meant Inverter rather than Converter. The inverter changes DC battery current to AC current to power AC devices like the TV and microwave when dry camping. Most energy managment systems do not monitor the house battery charger or the inverter (they can be seperate units but in many cases one unit does both).

Since these units are not monitored they cold be drwaing more current than the generator is able to provide. The generator will shut down with an over voltage code rather than burn itself up trying to meet the demand.

Another thing that could be causing a massive current draw is a short in the wiring harness that connects the generator to the coach. It could be that a wire has rubbed against a frame or body component and is shorted to ground. Or it could be that a mouse, chipmunk or other furry critter has had a snack on some of the wiring. For some reason rodents seem to be attracted to wiring harnesses.
__________________
Hikerdogs
2001 Adventurer 32V
  Reply With Quote
   
Old 05-09-2011, 02:32 PM   #6
wardy is offline
Senior Member
wardy's Avatar
Tiffin Owners Club
Join Date: Dec 2009
Location: Maitland, Fl
Posts: 170
Similar to what other's have mentioned: Turn off ALL breakers including genset, then start the gen. Then turn on the gen breakers, if no shut-down then your main breaker and then one by one your single breakers. Then let us know what happens.
__________________
2007 Allegro Bus 42 QRP, 400 ISL
  Reply With Quote
   
Old 05-09-2011, 02:48 PM   #7
RJay is offline
Community Administrator
RJay's Avatar


Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
You say that cummins tested the genset isolated form the MH. Did they apply a load to it? That is where your having the problem. I'm not familiar with your coach but I'm assuming it is a gas genset. If you have an over-voltage fault I would suspect the voltage regulator.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
  Reply With Quote
   
Old 05-09-2011, 03:48 PM   #8
Hikerdogs is offline
Senior Member


Join Date: Nov 2005
Posts: 883
Quote:
Originally Posted by RJay View Post
You say that cummins tested the genset isolated form the MH. Did they apply a load to it? That is where your having the problem. I'm not familiar with your coach but I'm assuming it is a gas genset. If you have an over-voltage fault I would suspect the voltage regulator.
I don't believe anything newer than the early 1990's uses a separate voltage regulator. They now use printed circuit control module that isn't servicable. The module controls just about every function including regulating output voltage. It also generates the fault codes displayed. If you follow the diagnostic tree in the service manual (for almost every fault code) it's an orderly process of eliminating all potential reasons for the error code. The last thing in each of the diagnostic trees is the control module. When all other possible physical contributors have been eliminated the last thing left is the conrtol module.
__________________
Hikerdogs
2001 Adventurer 32V
  Reply With Quote
   
Old 05-09-2011, 10:27 PM   #9
jtroop is offline
Member
jtroop's Avatar
Fleetwood Owners Club
Join Date: Jun 2010
Location: Michigan
Posts: 93
Thanks for all the replies everyone. I've been at work all day so let me try to answer some of the questions.

My rig does not have an automatic transfer switch. The dealer picked it up from cummins and is trying to figure out what is wrong. When the genset went out, we were running the AC and the microwave. When you turn off the genset breaker, it will run. Turn the breaker on and it shuts down. It shuts down with nothing powered on in the rv. Of course the converter would be drawing some power.

I do not have an inverter. I'm thinking hikerdogs is correct, it is a short in the wiring harness. Cummins says the genset is fine when isolated from the rv. It shouldn't be the converter or I'd have a problem when plugged into shore power, right? I don't know why the dealer is having a hard time finding the problem. I hope they find the problem soon. We are suppose to go camping this weekend.
__________________
2010 Fleetwood Encounter 32BH
Blue Ox Aladdin - 1998 Altima
  Reply With Quote
   
Old 05-09-2011, 11:02 PM   #10
Buford B is offline
Member
Monaco Owners Club
Join Date: Nov 2009
Posts: 87
Believe me I speak from experience, too much to get into here. I had similar issues with my genset. Breaker on, no joy. Breaker off it would run all day. I ended up disconnecting the coach wires at the genset terminal after the breaker, no joy. Problem was in the genset. Maybe you should check this as well it might save you a lot of headaches and it is pretty simple and quick.
__________________
Buford B.
Aero AT4040XL, AFE, Koni FSD,
Source Eng. Trailing Arms
  Reply With Quote
   
Old 05-10-2011, 04:20 PM   #11
jtroop is offline
Member
jtroop's Avatar
Fleetwood Owners Club
Join Date: Jun 2010
Location: Michigan
Posts: 93
Quote:
Originally Posted by Buford B View Post
Believe me I speak from experience, too much to get into here. I had similar issues with my genset. Breaker on, no joy. Breaker off it would run all day. I ended up disconnecting the coach wires at the genset terminal after the breaker, no joy. Problem was in the genset. Maybe you should check this as well it might save you a lot of headaches and it is pretty simple and quick.
Yes, well...Cummins already ruled out the genset. The dealer is still trying to figure it out. I had to cancel our camping this weekend. They said it wouldn't be ready in time.
__________________
2010 Fleetwood Encounter 32BH
Blue Ox Aladdin - 1998 Altima
  Reply With Quote
   
Old 05-10-2011, 05:35 PM   #12
GaryKD is offline
Senior Member
GaryKD's Avatar


Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 6,933
Hi jtroop,
I vote for doing another isolation from the coach. Tell the RV tech to remove the wires (at the generator) that connect the generator to the coach. Only then do we know the proper isolation was done by Cummins. If the generator runs when truly isolated from the coach, the dealer tech should be able to find the hard failure quite quickly.

If possible, try to determine if the tech working on your coach is a Certified RV tech in the area of the failure.
__________________
Gary
2005 Newmar KSDP 3910,
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
  Reply With Quote
   
Old 05-11-2011, 03:00 AM   #13
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,263
If you do not have a transfer switch, then you have a receptacle you plug the coach into that is feed by the generator. May certain that the wiring in the receptacle box is not shorting out when the cord is connected.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Old 05-14-2011, 03:53 AM   #14
jtroop is offline
Member
jtroop's Avatar
Fleetwood Owners Club
Join Date: Jun 2010
Location: Michigan
Posts: 93
*UPDATE* Stopped by the dealer. They are sending the rig back to Cummins! They brought in a technician who isolated the genset from the rv. The genset would shutdown when a load was applied. Cummins was wrong. The service rep said on top of that, when they pulled the cover off the genset, Cummins didn't completely reassemble the genset!

Service rep talked to a foreman at Cummins and they said to bring it back monday. What the heck Cummins!!

__________________
2010 Fleetwood Encounter 32BH
Blue Ox Aladdin - 1998 Altima
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Holdem at Cut N Shoot allendp Texas Boomers 8 11-11-2010 09:03 PM
P32 Brake trouble terra26 Workhorse Custom Chassis Motorhome Forum 2 11-01-2010 04:59 PM
trouble shooting hydraulic fan capt Frank Freightliner Motorhome Chassis Forum 3 11-18-2009 08:05 PM
The Trouble Tree John Harrelson Just Conversation 3 05-04-2009 10:31 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 06:59 PM.