I agree with the other posters here, it is very unusual and possibly dangerous to have both lines of a 50A service wired to the same phase. Ampacity of a single 6AWG wire is 60A ("enclosed", which means in conduit or a part of a cable).

If you can find your breaker (both the local and sub-panel), can you determine the size and whether it is single pole or double pole? Note the current is dictated by the smallest breaker in the circuit.

If it is 30A or less dual pole, or 50A or less single pole, it is wired safely (as far as neutral current is concerned) though it still may not be NEC compliant.

If it is 50A double pole, it unsafe as it most likely will allow 100A neutral current on your shore power cord and coach wiring. If this is the case, I'd definitely bring it up to campground management.

Also, if your coach has an Energy Management System it will detect this connection as 30A and not let you run over 30A anyway. It looks at the voltage from line to line and if it sees approximately 240V it decides the feed is 50A, otherwise it decides it is 30 (or 20A if you press the button).

In any case you are not getting your money's worth if you paid extra for the 50A site.


Stewart, Brenda and kids
2008 Newmar Canyon Star 3410
Luv2go is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-02-2010, 11:22 AM   #16
Senior Member
RJay's Avatar
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
The two major problems this situation can cause is a low voltage condition throughout the park and the possibility of an electrical outage because of an overloaded distribution transformer feeding the park. This is a situation where a good surge protection device is worth its weight in gold.

2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 08-02-2010, 12:06 PM   #17
Moderator Emeritus
Gary RVRoamer's Avatar

Fleetwood Owners Club
Freightliner Owners Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 16,432
I don't see any violation of the NEC. The power available for the outlet is simply less than a standard 50A RV outlet, but it doesn't violate any code as long as the wire gauge and circuit breakers are consistent with the power provided, the ground is proper, etc.

We don't know that every outlet in the park is fed off the same phase. The OP merely stated that all outlets appeared to be wired the same way, i.e. no 240V. The park is likely using all of the phases from its power source, feeding one site from one side and the next from the other, or some such load balancing arrangement. Just as they would do with 30A service. I've worked in a lot of RV parks and seen/repaired more than a little campground wiring - power distribution balancing is a routine matter.

As to whether you have a right to expect full 50A/240V service in a campground that provides a 50A RV outlet at the site, I'll let the lawyers figure that out.
Gary Brinck
2004 American Tradition; 2014 Buick LaCRosse
Homebase in the Ocala Nat'l Forest near Ocala, FL
Gary RVRoamer is offline   Reply With Quote
Old 08-02-2010, 04:25 PM   #18
Senior Member
AFChap's Avatar
Winnebago Owners Club
Spartan Chassis
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 4,433
The shore power box at each site is the standard type with 20a, 30a, and 50a outlets. The 50a has a double throw 50a breaker.

My Winnebago OEM EMS system sees the power as 50a ...has the 50a input light lit and does not display total amps being used. My TRC SurgeGuard shows two normal power legs.

At the moment we are running the dual compressor basement AC and the Norcold 1200 refrigerator. Total amps there should be apx 24a. We also are running the Splendide dryer. I don't know how many more amps that adds but I would guess around 10. I was running the dryer on a separate cord (previously run under a cabinet and out through the water bay when we were on a 30a connection) connected to the 20a outlet in the shore power box but it triped the GFCI in the shore power box a couple of times, so I plugged the dryer back into it's normal outlet which is wired to the second leg of the 50a, as also is the second ac compressor. When I put my hand on the 50a plug at the power box, it is a little warm to the touch, but not much.

I have a digital line meter in an outlet in the galley and it has maintained very good voltage ...115v and above ...regardless of what we have run, so sagging voltage does not appear to be a problem.
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '05 Honda Odyssey toad
AFChap is offline   Reply With Quote
Old 08-02-2010, 08:26 PM   #19
Senior Member
RJay's Avatar
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589

What probably happened in this case is the electrician spliced a length of wire off the existing 30 amp conductor, probably in the bottom of the pedestal or in a nearby splice box, and run the second live conductor to the other side of the receptacle. If you question the owner further, you will probably discover they didn't upgrade the existing wiring. So the best scenario is that the load of a second air conditioner of each RV has been added to the existing 30 amp live conductor. Normal residential voltage is 120 volts +/- 5%(126 volts-114 volts). This is set by and depends on the DPU, PUC, Electric Co-op or what ever is the governing body in your state that controls the transmission and distribution of power. This may vary from state to state but only by a couple of volts each way. So your 115 volts is not too far from being considered low voltage. The type of loads most affected by and likely to be damaged by low voltage are inductive loads or motor loads, which are you air conditioners.

2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote

Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

Similar Threads
Thread Thread Starter Forum Replies Last Post
What is running on each leg of 50A service? wagonmaster2 Winnebago Industries Owner's Forum 23 03-01-2008 07:12 AM
50A Power and Amperage Workshop Excel Owner's Forum 16 01-17-2008 05:48 AM
Progressive HW50C with 50A Autoformer Robin_M Monaco Owner's Forum 4 11-20-2007 08:00 PM
50a Voltage Boosters Robin_M MH-General Discussions & Problems 2 09-11-2007 06:01 AM
True Queen Size Bed??? wakamicamper Travel Trailer Discussion 19 03-26-2005 05:28 PM

» Virginia Campgrounds

Reviews provided by

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities

Copyright 2002-2015 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:27 PM.

Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.