Need some advice from anyone knowledgable about electrical systems. We're currently volunteering in our motorhome at a wildlife refuge which only provides 30A power. I have a voltmeter that plugs into a wall socket and notice that many times when multiple appliances are running the voltage drops into the "red", reading as low as 102 volts. I haven't had any breakers pop but wonder if the A/C compressor or other systems can be damaged. Appreciate any advice.
__________________

__________________
Fulltiming in a 2006 Ellipse 40FD

Our blog
Keith K is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-02-2006, 07:18 PM   #2
Senior Member
 
Keith K's Avatar
 
Freightliner Owners Club
Join Date: Feb 2005
Posts: 192
Need some advice from anyone knowledgable about electrical systems. We're currently volunteering in our motorhome at a wildlife refuge which only provides 30A power. I have a voltmeter that plugs into a wall socket and notice that many times when multiple appliances are running the voltage drops into the "red", reading as low as 102 volts. I haven't had any breakers pop but wonder if the A/C compressor or other systems can be damaged. Appreciate any advice.
__________________

__________________
Fulltiming in a 2006 Ellipse 40FD

Our blog
Keith K is offline   Reply With Quote
Old 05-02-2006, 11:19 PM   #3
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
Keith, inductive loads, motor especially do not like long periods of low voltage or any periods of extreme low voltage. Make sure all of your connections are as tight and short as possible. Try self energy management methods too. If you want to heat up something in the mirowave turn off the air conditioner while doing so. You may want to concider an "AutoFormer", this is a device that can boost the voltage if it is a continuing and persistant problem. Good luck.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 05-03-2006, 07:13 AM   #4
Member
 
barth's Avatar
 
Appalachian Campers
Join Date: Jan 2003
Posts: 36
I have a diesel pusher with a diesel generator. When I try to start the GENerator or use the HWH levelers all it does is click. When I push the AUX start switch every thing works.I f ound that after generator is running and I try to use the jacks it kills the generator.If plugged into 110 AC every thing works.all batteries check out good,connections clean and tight. All lights /pump/heator /furnace/ works fine on 12 volts not being plugged into 110 AC. BARTH
__________________
barth is offline   Reply With Quote
Old 05-03-2006, 07:38 AM   #5
Community Moderator
 
"007"'s Avatar


 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 26,781
Barth, check you ground wire for GEN to frame of coach in fact check all gnd's convertor, battery's to the frame or a common gnd post location. May have a dirty or loose connection use star washers to keep from becoming loose. "007"
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans, now in good hands
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 05-03-2006, 09:14 AM   #6
Senior Member
 
alvinc's Avatar
 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Apr 2002
Location: Beaverton, OR, USA
Posts: 658
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Keith Krejci:
I have a voltmeter that plugs into a wall socket and notice that many times when multiple appliances are running the voltage drops into the "red", reading as low as 102 volts. I haven't had any breakers pop but wonder if the A/C compressor or other systems can be damaged. </div></BLOCKQUOTE>The Air Conditioning motors are most at risk, as RV Wizard describes. The AutoFormer would certainly help, but I have to wonder about the wiring of the 30 amp circuit. A properly fused and wired circuit should not have a 15 volt drop. By properly wired, I mean the correct wire gauge for the distance it covers. The general rule is that 10g is large enough (3% drop) for 30 amps, but only to 50 ft. At 50 feet you need 8g, at 100 ft 6g, 150 ft 4g, etc. I suspect the service is underwired, which also means it is heating up.

The autoformer will help but it will cause an even higher current draw in order to boost the voltage.

What would I do? Install the autoformer and then manage the loads. For example, don't try to run both AC's and the microwave at the same time. Maybe run only one AC when cooking.
__________________
Alvin/KB7VHI
2002 35R Southwind, W22 8.1L Vortec UltraPower, 19.5' wheels
Toad: Wrangler, lifted and on 35" tires
alvinc is offline   Reply With Quote
Old 05-03-2006, 11:07 AM   #7
Senior Member
 
Keith K's Avatar
 
Freightliner Owners Club
Join Date: Feb 2005
Posts: 192
Thanks guys for the information. Alvin, I suspect you're right about the wiring, we're full timers, have been on 30A often and I've never experienced such a big drop in voltage. I don't believe the autoformer's the answer if it is the wiring; I'll try and teach my wife power management........that should be fun. Any idea of the danger area of low voltage; for example is 105 volts going to hurt the compressor or is this pretty much a guess depending on the quality of the motor?
__________________
Fulltiming in a 2006 Ellipse 40FD

Our blog
Keith K is offline   Reply With Quote
Old 05-04-2006, 06:33 AM   #8
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 18,085
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Any idea of the danger area of low voltage; for example is 105 volts going to hurt the compressor or is this pretty much a guess depending on the quality of the motor? </div></BLOCKQUOTE>

The generally accepted minimum voltage for any motor is 106 (and a max of 128). That's based on the voltage specs for AC power generation, which is 117 VAC plus or minus 10%. Any alternating current electrical device is supposed to be able to function reliably within that range. A better quality motor may survive longer or with less complaining, but quality is not really the issue here. It's more a matter of the design tradeoffs used by the electrical engineer who designed the motor and the tolerances of the components used when it was built.

As the voltage drops, the current (amperes) needed to produce the necessary power goes up. More amps produces more heat, which at some point to cause internal failure. Most motors will run for short periods at low volatge & high amps, but longer periods are almost sure to cause damage and outright failure. Some motors may have low voltage or thermal cut-outs (internal circuit breakers) that protect them from failure.
__________________
Gary Brinck
Former owner of 2004 American Tradition
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
Gary RVRoamer is offline   Reply With Quote
Old 05-06-2006, 05:31 AM   #9
Member
 
barth's Avatar
 
Appalachian Campers
Join Date: Jan 2003
Posts: 36
007 you were wright on the money. The grounds all looked good at the battereys but they were corroded at the frame.Ive been in the auto busines for 42 years and run across this sort of thing many times.I guess I,am getting forgetful working on my own stuf.a little thing like a ground can drive you crazy. Thanks so much for your reply. Barth
__________________
barth is offline   Reply With Quote
Old 05-06-2006, 02:48 PM   #10
Senior Member
 
Keith K's Avatar
 
Freightliner Owners Club
Join Date: Feb 2005
Posts: 192
Alvin, you were right on the money. After reading your post I asked that a professional electrician look at the wiring; sure enough, it was too small a gauge. As a result, they're rewiring the post for 50A. Thanks!
__________________

__________________
Fulltiming in a 2006 Ellipse 40FD

Our blog
Keith K is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
High Voltage Question RonNBama MH-General Discussions & Problems 12 09-17-2008 07:56 AM
Low Voltage Alarm Question CaptainCrab Winnebago Industries Owner's Forum 5 01-10-2008 08:15 AM
Magnetek Charger/Converter Voltage Question 56Nomad RV Systems & Appliances 5 03-22-2007 05:51 AM
A question on Voltage Big Ben Winnebago Industries Owner's Forum 8 03-07-2006 06:10 PM
A question on Voltage RV Systems & Appliances 8 12-31-1969 07:00 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 01:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.