A/C and Generator

When the temp gets to the set temp the a/c unit kicks down until it gets warm inside camper then a/c kicks in again. The trouble I am having is when the a/c kicks down it kills the genny. I have replaced the original thermostat with the same but new version thermostat,and still shuts genny off. Any ideas of why or what I can do to fix this problem. Thanks (1998 coachman Santara)
__________________

__________________
Good Sam member
abecar9 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-29-2013, 07:18 AM   #2
Senior Member
 
charliej's Avatar
 
Join Date: Feb 2013
Posts: 907
Quote:
Originally Posted by abecar9 View Post
When the temp gets to the set temp the a/c unit kicks down until it gets warm inside camper then a/c kicks in again. The trouble I am having is when the a/c kicks down it kills the genny. I have replaced the original thermostat with the same but new version thermostat,and still shuts genny off. Any ideas of why or what I can do to fix this problem. Thanks (1998 coachman Santara)
Don't know, but have you tried setting the fan setting on " on" rather than auto so when compressor kicks off fan is still running? Maybe it's some type of problem where gen needs a load to keep running. Good luck.
__________________

__________________
charliej is offline   Reply With Quote
Old 09-29-2013, 07:57 AM   #3
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,116
It sounds like an over-rev problem. When the A/C load drops off, the genny over-revs and kills the motor. Get your model number and D/L a manual for it. It should be an easy adjustment.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 09-29-2013, 08:04 AM   #4
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
Charlie, What model genset is it? One fairly common problem is the governed speed (RPM) of the genset - if too fast the Hertz output will be higher than normal (65HZ or over) and the controller assumes a problem and shuts down the unit with an overspeed error. With the load of the A/C unit(s) the generator RPM is lower thus keeping output under 65HZ until the A/C compressor(s) turn off. Onan/Cummins gensets use a polling method to check for HZ output periodically once triggered - I don't remember the exact timing they use, but it takes a few seconds or so of being "overspeed" to trigger a shutdown. Once you post the model number I can help you retrieve the error code(s) that are being set and can help you resolve it.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 09-29-2013, 05:43 PM   #5
Junior Member
 
abecar9's Avatar
 
Join Date: Dec 2011
Location: Atlanta,Ga.
Posts: 26
cummins E120339593 I believe an elan
__________________
Good Sam member
abecar9 is offline   Reply With Quote
Old 09-29-2013, 06:44 PM   #6
Junior Member
 
abecar9's Avatar
 
Join Date: Dec 2011
Location: Atlanta,Ga.
Posts: 26
Onan genny
__________________
Good Sam member
abecar9 is offline   Reply With Quote
Old 09-30-2013, 06:58 AM   #7
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,116
Quote:
Originally Posted by abecar9 View Post
Onan genny
That's the first step. Now you need to know the exact model number of the unit to get the specific documentation.

http://www.cumminsonan.com/cm/support/id/
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 09-30-2013, 05:36 PM   #8
Junior Member
 
abecar9's Avatar
 
Join Date: Dec 2011
Location: Atlanta,Ga.
Posts: 26
it is a RV QG 4000/mod # 4kyfa26100L
__________________
Good Sam member
abecar9 is offline   Reply With Quote
Old 09-30-2013, 06:15 PM   #9
Senior Member
 
clyon51's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Arizona West RV Park, Yuma, Az
Posts: 4,116
Quote:
Originally Posted by abecar9 View Post
it is a RV QG 4000/mod # 4kyfa26100L
Here's the Owners Manual.
RV QG 4000

This will explain the faults codes. The problem is there are a few regarding overspeed, so check the fault code the next time you have the opportunity to duplicate the problem. This will give us more specifics on the exact problem. What we need is the Service Manual which will explain the procedure to fix the problem. So far I cannot find one online that is free.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
clyon51 is offline   Reply With Quote
Old 09-30-2013, 07:19 PM   #10
Junior Member
 
abecar9's Avatar
 
Join Date: Dec 2011
Location: Atlanta,Ga.
Posts: 26
Thanks a ton for the help CLYON51 I will check the code deal tomorrow
__________________
Good Sam member
abecar9 is offline   Reply With Quote
Old 11-07-2013, 06:48 PM   #11
Junior Member
 
Join Date: Nov 2013
Posts: 1
Smile a/c generator problem

my question is do you have otherloads for the generator? if nothing else is loaded up on the generator it may be shutting down. the fan on the a/c unit, whitch is all that runs after the compressor shuts down is only about .2-.4 ampes. load that generator up, refrig. lights,a/c TV's and see what it does.
__________________
airmaster is offline   Reply With Quote
Old 11-08-2013, 05:23 AM   #12
Senior Member
 
94-Newmar's Avatar
 
Join Date: Nov 2009
Posts: 2,043
Quote:
Originally Posted by airmaster View Post
my question is do you have otherloads for the generator? if nothing else is loaded up on the generator it may be shutting down. the fan on the a/c unit, whitch is all that runs after the compressor shuts down is only about .2-.4 ampes. load that generator up, refrig. lights,a/c TV's and see what it does.
Absolutely not. Gensets continue running at zero load. The problem, as described is indicative of an overspeed error when returning to a zero load. It's no-load "run" rpm/speed could simply be set too high, it could have a governor controller failing, or carburetor problem causing it to die.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
94-Newmar is offline   Reply With Quote
Old 11-12-2013, 05:53 AM   #13
Senior Member
 
Davinger's Avatar
 
Ford Super Duty Owner
Join Date: Aug 2011
Location: Cocoa Beach Fl.
Posts: 257
Send a message via Yahoo to Davinger
Had the same problem and changed the oil, air and fuel filters on my generator and poof the AC wasn't a problem any more. Generally speaking you want to change the oil in your generator first time at 60 Hours (Break in fluid must be removed) then once every 100 hours or 1 year whichever comes first. Fuel and air filters to be changed every year.

Also remember in a Class C you can't run all of the accessories at the same time. Microwave and AC at the same time is enough to blow most breakers.
__________________

__________________
Davinger is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Palazzo Owners gmadams Palazzo Motorhomes 2879 01-16-2014 03:54 PM
Champion 2000 Watt Inverter Generator chboone RV Systems & Appliances 0 09-25-2013 12:03 AM
Dedicated Battery for Generator? mytime RV Systems & Appliances 15 08-02-2013 07:48 AM
Coachmen: a/c all outlets, microwave not working when generator running/ ladyrvr66 Forest River Owners Forum 5 07-14-2013 04:43 AM
2005 MADP generator model Grwalker Newmar Owner's Forum 5 05-30-2013 09:25 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:43 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.