Over Heating generator

I have a Generac 40 QP Gas generator on my 2007 class c It over heats when running the ac when the temperature is in the mid 90's

I have done the following
shut down all but ac
installed a hard start cap in ac
new spark
clean carb
syn oil
new air cleaner
adjusted valve lash
checked cooling fan

any one else have problems with generators overheating in 95+ temps with ac on
faulknerice is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-19-2011, 11:06 AM   #2
Senior Member
 
bearaboo's Avatar
 
Join Date: May 2011
Posts: 325
Is it shutting off because of overheating? You might try running the gen with cover off and the compartment door open. I have same gen and it only shut off once when it was real hot in Yellowstone NP.
Let it sit for awhile and restarted. Have not had any problems since then, even though
I have run in it some very hot temps. Seems like you changed all the combustion parts except the fuel filter.
My sense is that it is an electrical issue within the generator. Reaches a certain temp and shuts down. Don't mean to a wise guy, but is there more 1/4 tank of gas?
bearaboo is offline   Reply With Quote
Old 07-19-2011, 02:03 PM   #3
Junior Member
 
Join Date: Jul 2011
Posts: 4
Quote:
Originally Posted by bearaboo View Post
Is it shutting off because of overheating? You might try running the gen with cover off and the compartment door open. I have same gen and it only shut off once when it was real hot in Yellowstone NP.
Let it sit for awhile and restarted. Have not had any problems since then, even though
I have run in it some very hot temps. Seems like you changed all the combustion parts except the fuel filter.
My sense is that it is an electrical issue within the generator. Reaches a certain temp and shuts down. Don't mean to a wise guy, but is there more 1/4 tank of gas?

Thank you for the idea
I have a new fule filter on order allready
the gass tank is full
and if the temp is below 90 it will run all day no problem
it is over heating i used a infered temp gauge on the oil sensor and it was 270 the shut down temp is 264

I think that maybe this generator are not designed to work in 95 or 100 degrees with high humidity they say ac takes 20 to 30% more juice at that temps and generators loose power 1% fo every 10 degrees after 80

3600 w gen
-3% 108 w
=3492 w
can a 13.5k ac unit working 30% harder =3500 w?
faulknerice is offline   Reply With Quote
Old 07-19-2011, 02:07 PM   #4
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by faulknerice View Post
I have a Generac 40 QP Gas generator on my 2007 class c It over heats when running the ac when the temperature is in the mid 90's

I have done the following
shut down all but ac
installed a hard start cap in ac
new spark
clean carb
syn oil
new air cleaner
adjusted valve lash
checked cooling fan

any one else have problems with generators overheating in 95+ temps with ac on
Yes, we had a 6.2 Kw propane Genajunk unit in our 2000 DSDP, Would over heat and blow the circuit breakers above about 2,500' in 90°-95° weather. It never totally shut down, just blew the breakers though.
We now have a liquid cooled diesel 8.0 Kw gen, will never own another propane unit!
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 07-19-2011, 02:26 PM   #5
Senior Member
 
mahon1993's Avatar
 
Join Date: Mar 2010
Location: Fowlerville, Mich.
Posts: 606
I have seen guys use small portable 120 volt fans to blow on the geretator.
Greg
__________________
2000 Monaco Diplomat 40PBD
2012 Grand Cherokee Limited
2008 FatBoy, three spoiled Great Danes and a cat.
mahon1993 is offline   Reply With Quote
Old 07-25-2011, 04:02 AM   #6
Member
 
lowpasslew's Avatar
 
Join Date: May 2011
Location: Pensacola Area
Posts: 84
Yes, brand new jayco class C quits when it gets over 95 degrees. Took it accross to Las Vegas and suffered. Generator people had no idea or suggestions.
lowpasslew is offline   Reply With Quote
Old 07-25-2011, 08:06 PM   #7
Junior Member
 
Join Date: Jul 2011
Posts: 4
oil cooler

I have a idea for a mod
Has any one ever put on a oil cooler on a gen set
I was thinking i could buy a car oil cooler kit
they go on the oil filter and are about $150

what do you think
faulknerice is offline   Reply With Quote
Old 08-08-2011, 12:56 PM   #8
Senior Member
 
Join Date: Jul 2011
Location: Hawkeye State
Posts: 144
lowpasslew - interesting my 2011 Jayco displayed similar performance on last week's trip to Black Hills - Gen worked great when coach standing still (95+ in Badlands) but quit within 5 minutes after we started moving... Gen ran great when stopped at the BH campground. On return to Iowa wife and grandkids watched movies on gen no problems; within 15 minutes of running A/C gen died again. Going to Onan on Wed will post their "answer"
__________________
2017 Precept 31U
2021 ‘Ford Escape Hybred. 4 down
Gma-n-Gpa is offline   Reply With Quote
Old 08-09-2011, 09:31 AM   #9
Senior Member
 
tcopeland's Avatar
 
Thor Owners Club
Freightliner Owners Club
Carolina Campers
Join Date: Feb 2011
Location: Jacksonville, NC
Posts: 1,322
Please let us know outcome with Onan visit!
__________________
Tom MGYSGT USMC (Ret)
2016 THOR Tuscany XTE 36MQ
2011 Jeep Wrangler Unlimited
tcopeland is offline   Reply With Quote
Old 08-10-2011, 02:36 AM   #10
Member
 
lowpasslew's Avatar
 
Join Date: May 2011
Location: Pensacola Area
Posts: 84
We were told by Jayco Headquarters to take our 2011 RV to the Cummings-Onan dealer when we got home in Orlando, FL. Took it in yesterday. People were very nice, said they had similar problems, several possible causes, they would evaluate it. They said not to use synthetic oil, which I had used after the generator was well broken in, so we are switching from Amsoil back to regular. If we had an oil problem, synthetic would invalidate the warranty. I wonder if they really know what they are talking about??

I also mentioned use of cooling fans or an oil cooler connected to the oil cooler. They acted like they had never heard of that, but would consider it. So we will wait and see. Having an RV that doesn't work in hot weather seems like a waste of $69,000. The overheating experience almost killed my 96 year old passenger during our trip. I'm not a lawyer, but a medical person.
lowpasslew is offline   Reply With Quote
Old 08-10-2011, 05:54 AM   #11
Senior Member
 
Davinger's Avatar
 
Ford Super Duty Owner
Join Date: Aug 2011
Location: Cocoa Beach Fl.
Posts: 257
Send a message via Yahoo to Davinger
Too much insulation

I work with computers a great deal and heat is a major issue. One of the first things to look for when overheating is insulation. Over time things build up around things and dust and road oil can start to accumulate on both the outside of your generator and the compartment it is in. Sometimes a good cleaning of both the unit’s exterior and the compartment it is in will allow more air flow. Most of the generator compartments have vents and if they become clogged it can stop the flow of air. Just like dust on the fans of your computer. I hope this helps.
Davinger is offline   Reply With Quote
Old 08-10-2011, 06:56 AM   #12
Senior Member
 
Join Date: Jul 2011
Location: Hawkeye State
Posts: 144
Davinger - Agree with you 100% - heat can kill electronics - in my case the coach has less than 5K milles so don't see accumulation of dirt as a major contributor. I will add the vents and gen compartment to my checklist. Thanks for the info.

lowpasslew - So other than blasting you for synthetic oil and "considering" a cooler, did the Onan dealer have any ideas to solve this problem? I am with you, a coach without aux A/C in the summer is pretty useless. Hope your 96 year old passenger is doing well after that experience..
__________________
2017 Precept 31U
2021 ‘Ford Escape Hybred. 4 down
Gma-n-Gpa is offline   Reply With Quote
Old 08-10-2011, 02:45 PM   #13
Senior Member
 
bearaboo's Avatar
 
Join Date: May 2011
Posts: 325
Interesting that you mention the synthetic oil. The one time my gen shut off in Yellowstone, that was my first thought. Maybe low oil pressure. Even bought a quart of regular oil to change it out if necessary. Hasn't happened again and I continue to use Mobil 1 10W-30.
bearaboo is offline   Reply With Quote
Old 08-10-2011, 08:33 PM   #14
Member
 
lowpasslew's Avatar
 
Join Date: May 2011
Location: Pensacola Area
Posts: 84
Quote:
Originally Posted by Gma-n-Gpa View Post
Davinger - Agree with you 100% - heat can kill electronics - in my case the coach has less than 5K milles so don't see accumulation of dirt as a major contributor. I will add the vents and gen compartment to my checklist. Thanks for the info.

lowpasslew - So other than blasting you for synthetic oil and "considering" a cooler, did the Onan dealer have any ideas to solve this problem? I am with you, a coach without aux A/C in the summer is pretty useless. Hope your 96 year old passenger is doing well after that experience..
I contacted Amsoil headquarters and they thought it was OK to use their product unless the Onan handbook or spec sheet said no. Onan dealer said nothing was in writing, but they had seen a couple instances where synthetics were suspected in poor ring seating. That is like me taking my person experience instead of my periodontal specialist training in dentistry. They still have my RV. I'll keep you posted on the results. It seldom gets over 95 in Orlando, so I won't really know until I venture into superheated conditions again.
lowpasslew is offline   Reply With Quote
Reply

Tags
generator, heating



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Remote generator start not working, please help ShapeShifter Monaco Owner's Forum 20 08-24-2016 11:05 AM
06 Hurricane Onan 5.5KW Generator heat mgscott4 Thor Industries Owner's Forum 1 07-26-2011 12:21 AM
Generator only putting out a few volts AC TallPaul RV Systems & Appliances 7 12-25-2007 02:57 PM
Generator Coolant Level OldForester Alpine Coach Owner's Forum 8 10-25-2007 05:56 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:41 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.