Old 01-09-2019, 01:39 PM   #15
Senior Member
 
saddlesore's Avatar


 
Foretravel Owners Club
Join Date: Apr 2016
Location: Salem,Orygun
Posts: 3,562
Hmmm... I can see the possibility of real issues when it comes time for using the A/C's.... May need to swap in some "Soft Start " capacitors...
__________________

__________________
Foretravel with tag axle.
retired truckdriver with 5m miles
Orygun Native
saddlesore is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-09-2019, 08:04 PM   #16
Senior Member
 
ThePowells's Avatar


 
Join Date: Mar 2017
Location: Zebulon, NC
Posts: 4,155
Quote:
Originally Posted by Cinders1 View Post
So our ‘virgin overnight’ was in Kanab, UT last weekend. We had played around with all the RV appliances, etc., several times, but had not slept in the coach (2018 Thor, Four Winds, 24’). Well it was a cluster. Our hot water, heater and fridge could not be on the camps electric without blowing a fuse. Went through 3 and by then the local stores were closed. Used a space heater and it was bearable. Next day, we got more fuses (hubby THOUGHT he had multiples of ALL but missed the 7.5). Anyway, found out that we can’t have heat, hot water AND fridge on 30 amp. We moved the hot water to propane and all worked. Called a Thor dealer and service said that’s the way it works - can’t have everything g on 30amps. “You have to pick and choose.” So my question is, if we’re ever in a 50 amp locale, would we still need the propane? Anybody else ever have this issue?

I'm not gonna weigh in on the whizzing contest over 120 / 420 / 360 and all that stuff..
Did you try all that stuff on generator? Did you still have a problem?
I am not sure where your problem with blowing that fuse lies. Your heat is gas heat with a 12 volt blower, and you already knows that your water goes both ways and it looks like you have the Norcold fridge. That shouldn't be an issue for the fuses. Regardless of having a 30 or 50 Amp site, that shouldn't affect this.

The problem I have is not being able to see exactly what is going on and knowing how it is set up, but if I understand correctly on yours 12 volt only controls the circuit boards for the water heater and fridge and the fan for heat, and if you are blowing fuses, it is the 12 volt side of your coach so being on 30, 50, or 100 wouldn't matter and we don't know what fuse is blowing as you mentioned the 7.5 being forgotten but not the one that is blowing.
__________________

__________________
Kelly and Jerry Powell with Halo (Lethal White Aussie), Nash the Rat Terrorist, and now Reid, the "Brindle we have no idea puppy"
2017 Thor Quantum W31, Ford E-450, Onan QG4000, Demco Kar Kaddy, Toytoada Prius.
ThePowells is offline   Reply With Quote
Old 01-09-2019, 10:05 PM   #17
Junior Member
 
Join Date: Sep 2018
Posts: 24
Wow! A lot of great info here! We do have 30AMP and we have an adapter if we get a 50 AMP site. The fuse was a 7.5 and in the ‘appliance’ slot. Not all electric was out. Outlets worked, thus the space heater that saved the day. Had no idea that 30AMP wouldn’t run it all, but your explanations make sense. Propane for the water heater the next day was the solution. Toasty warm when we finally changed the fuse and eliminated all the items on electric. Thanks to all!!!!
**No generator allowed - quiet time
Cinders1 is offline   Reply With Quote
Old 01-09-2019, 11:42 PM   #18
Senior Member
 
Join Date: Jan 2009
Posts: 1,650
Quote:
Originally Posted by Cinders1 View Post
So our ‘virgin overnight’ was in Kanab, UT last weekend. We had played around with all the RV appliances, etc., several times, but had not slept in the coach (2018 Thor, Four Winds, 24’). Well it was a cluster. Our hot water, heater and fridge could not be on the camps electric without blowing a fuse. Went through 3 and by then the local stores were closed. Used a space heater and it was bearable. Next day, we got more fuses (hubby THOUGHT he had multiples of ALL but missed the 7.5). Anyway, found out that we can’t have heat, hot water AND fridge on 30 amp. We moved the hot water to propane and all worked. Called a Thor dealer and service said that’s the way it works - can’t have everything g on 30amps. “You have to pick and choose.” So my question is, if we’re ever in a 50 amp locale, would we still need the propane? Anybody else ever have this issue?
I think the Thor dealer you called is wrong. Those are basic everyday appliances and you should be able to run em at the same time.

From what you've stated, I don't believe the 30 amp 120 volt circuit is the problem. I believe there's something going on with the 7.5 amp 12 volt circuit.
__________________
03 Itasca Sunova, Workhorse P32 chassis with the 8.1 and 4L85-E
Mudfrog is offline   Reply With Quote
Old 01-09-2019, 11:46 PM   #19
Senior Member
 
ThePowells's Avatar


 
Join Date: Mar 2017
Location: Zebulon, NC
Posts: 4,155
Mine actually draws more than yours and I don't have much of a problem except when SWMBO wants to dry her hair or use the microwave while the A/C is running. If we were going to keep it much longer, I was going to add an outlet in the bathroom and maybe one for the microwave that I could plug into a 20A socket with the 30A cord. It's harder to use the hair dryer and microwave at the same time. 30A will run everything that you had on without any problem. The fuse that you replaced was on the 12 volt side of the coach and had no bearing on the 30A AC side, as they are totally different. Easy way to remember is 12 volt has fuses (for the most part) and AC has breakers (always).


Also, that space heater that you plugged in uses way more power than anything else you had running at the time. I run a 1500 watt heater and it is the same as the A/C, but most of the time it doesn't trip out when using the microwave.
__________________
Kelly and Jerry Powell with Halo (Lethal White Aussie), Nash the Rat Terrorist, and now Reid, the "Brindle we have no idea puppy"
2017 Thor Quantum W31, Ford E-450, Onan QG4000, Demco Kar Kaddy, Toytoada Prius.
ThePowells is offline   Reply With Quote
Old 01-10-2019, 11:36 AM   #20
Member
 
Join Date: Jul 2018
Posts: 96
Quote:
Originally Posted by Old-Biscuit View Post
Yes you have a 30A power cord....just one HOT....3600W total

But you mention blowing a FUSE and needing more (went thru 3 fuses) and had to get more???

Used space heater ??

SO your issue is NOT 120V AC usage (not tripping circuit breaker) BUT is a 12V DC issue (blowing fuse)....which sounds like Furnace Fuse (has to use space heater)

Fridge DC Source would be on separate Fuse
Water Heater DC Source would be on separate Fuse
Furnace DC Source would be on separate Fuse

Depending on BRAND/MODEL ---furnace DC Fuse should be 10A

So which FUSE is blowing?
Our rig has 30 amp service and we can run on 110V, the fridge, the hot water heater, and the furnace at the same time. So I was thinking along the lines of Old_Biscuit.

But I am a bit perplexed.

Our furnace (and I think all RV furnaces) is exclusively a 12V operational system.

I always assumed the hot water heater and fridge will operate exclusively on 110V when plugged into shore power, even if no battery was present. If that is true, I am confused why you are blowing 12V fuses. I never tried running the hot water heater and fridge while plugged into shore power when all batteries are disconnected. If they don't work, then that would support Old_Biscuit's theory.
Ron Dittmer is offline   Reply With Quote
Old 01-10-2019, 02:13 PM   #21
Senior Member
 
Join Date: Nov 2015
Posts: 7,686
Quote:
Originally Posted by Ron Dittmer View Post
Our rig has 30 amp service and we can run on 110V, the fridge, the hot water heater, and the furnace at the same time. So I was thinking along the lines of Old_Biscuit.

But I am a bit perplexed.

Our furnace (and I think all RV furnaces) is exclusively a 12V operational system.

I always assumed the hot water heater and fridge will operate exclusively on 110V when plugged into shore power, even if no battery was present. If that is true, I am confused why you are blowing 12V fuses. I never tried running the hot water heater and fridge while plugged into shore power when all batteries are disconnected. If they don't work, then that would support Old_Biscuit's theory.

Furnace is 12V DC and propane
Fridge needs 12V DC for controls, display, circuit board ---can't operate electric element w/o DC
Water heater???
If Atwood...needs 12V DC for both electric & propane
If Suburban....can run electric element w/o DC


The DC can be from battery OR from converter when plugged into AC Power Source



7.5A is a FUSE....that is 12V DC
So regardless of AC source Power Amp *30/50----DC fuse blowing is NOT an AC issue.
It is a DC issue which needs to be repeated/identified and fixed. OR keep some 7.5A Fuses handy
__________________
2007 Dodge 3500 w/Tractor Motor & NUWA 5vr
FT traveling 2007 - 2014 "Still DEBT Free"
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 01-10-2019, 07:01 PM   #22
Senior Member
 
Gulf Streamers Club
Ford Super Duty Owner
Join Date: Aug 2015
Location: Memphis, TN
Posts: 575
50a vs 30/20

Quote:
Originally Posted by twinboat View Post
Basically, 50 amp service is 50 and 50 amps. Not 30 and 20 amps.

This*50-amp*service*has 4 wires with two 120-volt HOT feeds.*It is a*misconception*that this 50-amp RV service is something special.This service is a STANDARD 120/240 50-amp 3 pole with 4 prongs used for*numerousapplications.*

The 50-amp 120/240-volt 3 pole 4
(from what I read): Some RVs w/ GEN larger than 4000 (maybe 5500-6,000-watt? and with a 2nd AirCond unit) have the 30a and 20a breaker on the two legs of AC Power? The 30a feeds normal panel and the 2nd breaker @20a ONLY feeds the 2nd Air unit
__________________
99-GS Conquest 6266 Class-C
THenne1713 is offline   Reply With Quote
Old 01-10-2019, 08:36 PM   #23
Senior Member
 
Join Date: Apr 2016
Posts: 226
Quote:
Originally Posted by LJowdy View Post
I know I'll get a lot of flack over this but """BASICALLY""" 50 amp service, although in reality, is 240 volts, is in reality, 2 different circuits. One is 30 amps and the other is 20 amps.
LOL flack = correcting your published errors. Interesting.
I liked your """BASICALLY""".

Here, """COMPLETELY""" what you wrote regarding amperage was incorrect.
__________________
2005 Safari Cheetah 38 PDQ
Mark- is offline   Reply With Quote
Old 01-10-2019, 08:54 PM   #24
Senior Member
 
Join Date: Jun 2017
Posts: 1,252
Quote:
Originally Posted by Cinders1 View Post
Wow! A lot of great info here! We do have 30AMP and we have an adapter if we get a 50 AMP site. The fuse was a 7.5 and in the ‘appliance’ slot. Not all electric was out. Outlets worked, thus the space heater that saved the day. Had no idea that 30AMP wouldn’t run it all, but your explanations make sense. Propane for the water heater the next day was the solution. Toasty warm when we finally changed the fuse and eliminated all the items on electric. Thanks to all!!!!
**No generator allowed - quiet time
You don't have a 30 Amp AC problem.

You are blowing the DC appliance fuse (7.5 Amp)

Running your water heater does not reduce this DC load.
Running your Fridge on GAS does not reduce this load.
Only not running your furnace will reduce the load as the DC fan will not be running.
The furnace also supplies 12 VDC power to your thermostat. It should not be on the same fused circuit as the control power for your fridge and water heater.
Thor wired your coach incorrectly; you should have absolutely no problem running all three of those appliances together either on Shore Power or not.

Take your coach to a dealer who has someone with brain cells in their service department and they should be able to fix it in about an hour.

And ignore the discussion on 50 Amp service as it doesn't apply to you.

Post #2 was wrong and post #22 only applies to some generators in a 50 Amp coach.
tfryman is offline   Reply With Quote
Old 01-11-2019, 01:40 AM   #25
Senior Member
 
eddndee's Avatar
 
Join Date: Aug 2017
Location: Puget Sound
Posts: 272
Hmmm... I have never had any of these issues and have never given them any thought. I have tripped a breaker when running microwave and electric skillet but easily mitigated. I put the fridge on auto and everything else uses gas.
__________________
EdD
1998 Safari 2620 Class C
Costco member
eddndee is offline   Reply With Quote
Old 01-11-2019, 04:50 AM   #26
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 778
Quote:
Originally Posted by Old-Biscuit View Post
Yes you have a 30A power cord....just one HOT....3600W total


But you mention blowing a FUSE and needing more (went thru 3 fuses) and had to get more???


Used space heater ??


SO your issue is NOT 120V AC usage (not tripping circuit breaker) BUT is a 12V DC issue (blowing fuse)....which sounds like Furnace Fuse (has to use space heater)


Fridge DC Source would be on separate Fuse
Water Heater DC Source would be on separate Fuse
Furnace DC Source would be on separate Fuse


Depending on BRAND/MODEL ---furnace DC Fuse should be 10A


So which FUSE is blowing?
I guess mine must have been wired on a Sunday Night shift. My 12-volt circuit is wired Fridge, furnace and range hood all on the same 12-volt fuse. I believe the WH also but didn't check that one while I was working on the Furnace.
__________________

__________________
27' Wildcat 5th wheel. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motorhomes are RV's. All RV's are not Motorhomes.
cavie is offline   Reply With Quote
Reply

Tags
electric



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How much, how much, how much,is it enough? rvethereyet Going Green 38 11-22-2017 10:48 PM
How much rust is too much - fix or trade?? AK_smith Class A Motorhome Discussions 21 08-25-2015 07:57 PM
How Much is Too Much? dcarver Trailer Towing and Tow Vehicles Discussion 60 07-29-2015 09:18 PM
How much is too much - mileage osgoor Class A Motorhome Discussions 3 11-25-2012 09:45 PM
How much play is too much? Mbl Cndo Monaco Owner's Forum 8 11-28-2007 01:47 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:22 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.