Getting it from the solar panel into the trailer

I need help in finding a watertight from the solar panel into the teardrop trailer connection. What I have is a Perko watertight deck plug sitting on top PERKO Inc. - Lighting Fixtures - Watertight Deck Connection
The 180W panel when not attached to the teardrop sits on top of the garage attached to a grid tie inverter, (a watt generated is a watt saved).
I don't know if I am being overly concerned about voltage drop it is a high voltage panel.
__________________

__________________
Shadowcatche is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-26-2010, 11:11 AM   #2
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,339
It looks like that should work just fine. Use the heaviest gauge wire that that plug and receptacle accept.
__________________

__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 12-28-2010, 04:26 PM   #3
Senior Member
 
Join Date: Apr 2010
Location: Full Timer / Vagabond
Posts: 609
What exactly is the voltage of your panel? At 12 Volts it produces 15 amps. A #10 wire would do the job. If the voltage is higher then a smaller wire will work fine.

Go to the "Solar That Really Works" thread and use the wire sizing guide on the site listed there.
__________________
Ralph & Snickers
2006 3500 Chevy Dually - 8.1 - Allison
2006 30' New Horizon - Solar
ralper is offline   Reply With Quote
Old 12-28-2010, 05:22 PM   #4
Senior Member
 
Shadowcatche's Avatar
 
iRV2 No Limits Club
Join Date: Nov 2010
Posts: 1,219
Under load it appears to be 40+V, I guess I am getting paranoid because of the voltage drop dialogue.
__________________
Shadowcatche is offline   Reply With Quote
Old 12-29-2010, 09:27 PM   #5
Senior Member
 
Join Date: May 2009
Posts: 2,164
Quote:
Originally Posted by Shadowcatche View Post
Under load it appears to be 40+V, I guess I am getting paranoid because of the voltage drop dialogue.
What manufacturer/model is it?
__________________
2001 Mountain Aire DP 4095
2008 Jeep Wrangler Rubicon
RVSeniorMoments.com
TechWriter is offline   Reply With Quote
Old 12-30-2010, 08:39 PM   #6
Senior Member
 
Shadowcatche's Avatar
 
iRV2 No Limits Club
Join Date: Nov 2010
Posts: 1,219
It is a Suntech STP185S open circuit voltage is 45V (I have seen it higher?)
__________________
Shadowcatche is offline   Reply With Quote
Old 12-31-2010, 01:42 PM   #7
Senior Member
 
Join Date: May 2009
Posts: 2,164
Do the Math

Quote:
Originally Posted by Shadowcatche View Post
It is a Suntech STP185S open circuit voltage is 45V (I have seen it higher?)
First, get the electrical specs for your panel:
http://www.energymatters.com.au/imag...5S24adplus.pdf

Look for these values (names in parenthesis are the terms Suntech uses) in the panel's specs:

Vnominal = the "nominal" panel voltage = 24 V. This is the value people typically use when referring to a panel. However, output voltage is typically higher -- as you saw with a 45V output. That's the Vopen-circuit voltage (see below).
Vmax voltage (or "Optimum Operating Voltage") = 36.4 V
Imax current (or "Optimum Operating Current") = 5.09 A
Vopen-circuit voltage (or "Open - Circuit Voltage" = 45.0 V
Ishort-circuit current (or "Short-Circuit current") = 5.43 A
Pmax = Vmax voltage x Imax current = 36.4 x 5.09 = 185.3 W


Second, use these values to compute fuse size. This is the fuse that should be between a PV array and the controller (and the batteries).

Fuse size = 1.56 x Ishort-circuit current = 1.56 x 5.43 = 8.5A (a 10 or 15A fuse will do).

If you based wire size on just fuse size amperage (15A), you'd only need 14 gauge wire.

However, you need to figure line loss for a low voltage system like this.


Third, to figure line loss, I use this online "VDI" calculator because it lets you pick the percentage of line loss:
How to Size Wiring and Cabling for Your System - AltE

This forumula is used to compute a VDI value which is then used to select the wire size:
VDI = (AMPS x FEET) / (% VOLTAGE DROP x VOLTAGE)

For your panel, figuring a 1% voltage drop at 12 feet:

VDI = (5.43 x 12) / (1 x 24) = 2.7 = 3 (rounded up for greater wire size)

For a VDI = 3, a 12 gauge wire is recommended for a 24V PV with a 1% voltage drop over 12 feet.
__________________
2001 Mountain Aire DP 4095
2008 Jeep Wrangler Rubicon
RVSeniorMoments.com
TechWriter is offline   Reply With Quote
Old 12-31-2010, 06:41 PM   #8
Senior Member
 
Shadowcatche's Avatar
 
iRV2 No Limits Club
Join Date: Nov 2010
Posts: 1,219
Thanks
That will save me a good bit in not buying more wire gauge than I need.
__________________
Shadowcatche is offline   Reply With Quote
Old 01-02-2011, 11:52 AM   #9
Member
 
Join Date: Nov 2010
Posts: 63
Wait a minute here.... The obvious question to me is how are you hooking up to the battery? Are you using an MPPT controller that can transform that high voltage down to what the battery needs? The cheapest controller I know of that would do what you need is a the Morningstar Sunsaver MPPT. It is an ugly little black box, but is three stage, has built in temperature compensation and will accept up to 75V input. It is a great tool, but still around $300.

Why would anybody want to do all of that calculating when a simple chart can tell you all you need to know? Even though I could get technical like that, I refuse to do so because it just makes most people's eyes glaze over. I thought these forums were for helping people, not for impressing them. KISS

All of this to save $3 or $4 on wire? Consider using #12 landscape lighting wire from Home Depot or Lowes.
__________________
Bob
Full time boondocker, solar powered, no generator
HandyBobSolar.com
HandyBob is offline   Reply With Quote
Old 01-11-2011, 04:27 PM   #10
Senior Member
 
Shadowcatche's Avatar
 
iRV2 No Limits Club
Join Date: Nov 2010
Posts: 1,219
Yep I have a Morningstar MPPT and HB quite frankly you are to blame for being a bit paranoid about wire size, so see some one did listen. I have a bunch of 10 Ga so will use that.
This is a Grasshopper (more square) design teardrop 6X11 set up for boondocking with water filters and pump that can safely pull from lakes and streams, variable height suspension for mild off road, Bullfinch exterior shower point, 6 gal gas electric water heater, Eberspacher diesel heater, Satellite radio and TV etc.
__________________
Shadowcatche is offline   Reply With Quote
Old 01-11-2011, 06:10 PM   #11
Senior Member
 
johnsonjm209's Avatar
 
Monaco Owners Club
Ford Super Duty Owner
Join Date: Oct 2010
Posts: 295
When I was a kid we used to talk about sports. Then we talked about cars. After that and for many,many years we talked about girls. Now you guys are talking about volts, ohm, amps and mppts and I don't understand them. I wish I was young enough to go back to talking about girls again even though I didn't understand them either.

Joe from Ct.
__________________
johnsonjm209 is offline   Reply With Quote
Old 01-12-2011, 09:39 AM   #12
Member
 
Join Date: Nov 2010
Posts: 63
Wire size

Quote:
Originally Posted by Shadowcatche View Post
HB quite frankly you are to blame for being a bit paranoid about wire size, so see some one did listen.
So, there is good news & bad news.

The good news is that a lot of people are listening and they are becoming successful with solar power. My wife keeps telling me that I should be compiling a record of the letters and emails, but this is not what is important to me. I must tell you though, that my favorite was from a guy in Alaska with no solar panels who told me that by reading my info he was able to substantially cut the gas bill for his generator by just turning the charge voltage up. He figured this out by installing a Trimetric meter at my suggestion and that told him that his charging was not working. Again, you don't need to understand all of the physics. You just need to find a voltage drop chart or Google "voltage drop calculator". I would rather that people overreact than to listen to the wrong advise and end up running that #@%! generator.

The bad news is that most of the solar dealers will STILL tell you #8 is big enough for four panels or more. It definitely is not, unless you are using high voltage in the run down from the roof and you cannot do that unless you spend more money for the big MPPT controller. Even then, the bigger wire is a good buy because they get more volts to the controller, which can then turn them into more amps going into the battery. If you are on a tight budget, the MPPT is not a good bargain on small systems unless like Shadowcatche here, it is being used so that a high voltage panel which is basically free can be used. (Smart idea)

I am talking to yet another person now who was sold a kit with 30ft of #10 wire to go with a 130 watt panel and a crappy controller that will not work. You don't need to be an electronics genius to look that up in a chart and figure out that it won't work, even if he had been sold a good controller. You just need to listen to the right advise instead of the advise supplied by somebody whose profit motive is to sell you another panel after what he sold you doesn't work.
__________________
Bob
Full time boondocker, solar powered, no generator
HandyBobSolar.com
HandyBob is offline   Reply With Quote
Old 01-13-2011, 10:49 AM   #13
Senior Member
 
Shadowcatche's Avatar
 
iRV2 No Limits Club
Join Date: Nov 2010
Posts: 1,219
HandyBob
I'm running into a bit of the situation currently arguing with a number of people who are using the vehicle charging system to charge the trailer battery. Most of these are home built teardrop trailers or tiny travel trailers and the level of sophistication goes from absolutely drop dead gorgeous woody's to a 4 x 8 built on a Harbor Freight trailer. Ours will be the most sophisticated one out there that I am aware of.

My contention is that in all likelihood the tow vehicle charging system is not doing an adequate job of charging the trailer battery. They are in essence in parallel and the mismatch in batteries is likely to be very great. I suggested that a Balmar programmable dual voltage regulator might be a wise investment and I am getting the well this is the way they've been doing it for years argument and KISS.
__________________
Shadowcatche is offline   Reply With Quote
Old 01-14-2011, 10:21 AM   #14
Member
 
Join Date: Nov 2010
Posts: 63
Quote:
Originally Posted by Shadowcatche View Post
HandyBob
I suggested that a Balmar programmable dual voltage regulator might be a wise investment and I am getting the well this is the way they've been doing it for years argument and KISS.
I am not familiar with those things, but I "suspect" that it would be a waste of money. I doubt that it could raise the voltage to a higher level than it receives from the already regulated alternator output. If using big booster cables directly from the tow vehicle batteries to the trailer you can do a decent job of charging and can eventually get the trailer battery up to within a couple of tenths of a volt of where the vehicle voltage regulator is set. However, it does not really charge all the way to full unless you are willing to idle the engine for hours on end. So, the battery dies an early death from undercharging.

If they are using the trailer connector that also runs the tail lights, that is another matter. It does not work because of the voltage drop in the wire. You just need to measure the volts at the trailer battery & compare it to the vehicle's battery to see the problem. If you had an expensive clamp on DC ammeter, you could see how the amps drop off way before the battery in the trailer is full because there is not enough voltage (pressure) pushing them in. A hydrometer would supply the real proof.

Of course I cover this in my RV Battery Charging Puzzle, if only people would be willing to read it.
__________________

__________________
Bob
Full time boondocker, solar powered, no generator
HandyBobSolar.com
HandyBob is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar panel controller bsimonds Winnebago Industries Owner's Forum 5 12-26-2010 10:33 PM
Solar Panel installation?? studmuffin Monaco Owner's Forum 8 12-19-2010 01:55 AM
Solar panel preped bdpreece Monaco Owner's Forum 8 07-04-2010 10:41 PM
Solar Panel for Chassis Batteries OldForester Alpine Coach Owner's Forum 3 08-15-2008 10:01 PM
12v House Battery Problem ---Solar Panel??? Belgique Winnebago Industries Owner's Forum 6 11-06-2006 08:52 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:43 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.