mikelm48 02-23-2016 05:44 AM

Magnum ME-AGS-S Standalone AGS
 
Planning to add this AGS to my 2005 KSDP. I notice that the upper limit setting for starting the generator when the batteries are getting low is at 12.0 volts (range is 10 to 12) . Just wanted to check and make sure that setting was not too low. Thanks.

Scottybdivin 02-23-2016 07:37 AM

12.0V is not too low with a load on the batteries. 12.14V static is considered 50%, but any load on the batteries will cause the voltage to go lower. Magnum recommends setting it at 11.0V to prevent unnecessary starts. Do you have your AGS already? I have one to sell.

ronjhall 02-23-2016 08:28 AM

Originally set generator start at 11.0 volts. If inverter was running at same time generator would not start. After trying different settings. Ended at 12 volts for reliable starts.

mikelm48 02-23-2016 09:28 AM

Quote:

Originally Posted by Scottybdivin (Post 2950309)
12.0V is not too low with a load on the batteries. 12.14V static is considered 50%, but any load on the batteries will cause the voltage to go lower. Magnum recommends setting it at 11.0V to prevent unnecessary starts. Do you have your AGS already? I have one to sell.

Just ordered it yesterday.