Update:
I could not find out the model number, nor, a schematic for my AC system..
The fan capacitor was shot
The start capacitor fell apart.
The run capacitor was completely rusted, no values, no part number..
I could read the other 2 capacitors. Not wanting to just change 2 I decided to buy a cheap ($25 ) capacitance meter.
The fan cap is a 7.5 MFD 370 VAC
The start cap is 88-108 MFD 220 VAC
The run capacitor was told to me to most likely be 40 MFD. Not wanting to take a chance I bought the capacitance meter.
I measured the new fan and start caps I got and the meter was right on correct.
I got up on the roof, removed one side of the run cap and it tested at 40 MFD ( a value I was told by Coleman it most likely was ) so I just ordered that one. When it arrives I will post if everything worked