A quick read of the user manual states: "To clear this fault, an inverter reset is required. Remove DC power to the inverter, or press and hold down the power switch on the inverter for 15 seconds (until the green Status LED comes on). If this fault does not clear, the unit will need to be serviced."
The blowing of your 400-amp fuse is a strong indication that the switching system (the "bridge" ?) that takes in the DC voltage and creates the 60-hertz, 120VAC output is not just "failing" but actually shorting out (thus the fuse blows). This is a return-it-to-the-manufacturer-for-repair situation I think.