Old 12-31-2006, 12:55 PM   #1
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
I ran a 20amp extension to MH.

The Powerline panel showed 30amp in, Xantrex all looked normal. I kicked on the elec heat thinkng the system would take care of things.

I pushed the 30/20amp select switch on Powerline thinking that was the safe bet. Well, even though the amps reading was ~16, everything clicked off.

I figured I blew a house breaker, nope. I checked all coach breakers I could think of, all look good.

So I hit the Invert button and the panel came back to life. But now the Powerline panel shows 50amp incoming but there is no amps reading, and the Xantrex is not showing Charge anymore. I tried off/on a couple times, unplugged from shore, no change.

Is there something else I should check, or did I do some damage?

crap.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 12-31-2006, 12:55 PM   #2
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
I ran a 20amp extension to MH.

The Powerline panel showed 30amp in, Xantrex all looked normal. I kicked on the elec heat thinkng the system would take care of things.

I pushed the 30/20amp select switch on Powerline thinking that was the safe bet. Well, even though the amps reading was ~16, everything clicked off.

I figured I blew a house breaker, nope. I checked all coach breakers I could think of, all look good.

So I hit the Invert button and the panel came back to life. But now the Powerline panel shows 50amp incoming but there is no amps reading, and the Xantrex is not showing Charge anymore. I tried off/on a couple times, unplugged from shore, no change.

Is there something else I should check, or did I do some damage?

crap.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 12-31-2006, 01:20 PM   #3
Winnebago Owner
 
Easyrider's Avatar
 
Join Date: Dec 2004
Location: Baraboo, Wisconsin
Posts: 237
Did a circuit breaker at your source ( inside your house ) get triggered?
__________________
Steve & Nancy
2005 Itasca Sunrise 33', W20 Chassis, Ultrapower, Henderson Trac Bar
2012 Chevy Captiva Sport AWD, ReadyBrute Elite Tow Bar, Blue Ox Base Plate, Protect-A-Tow
Easyrider is offline   Reply With Quote
Old 12-31-2006, 01:28 PM   #4
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
No, that's the weird thing. No breakers(coach or house) blew. It's like the inverter shutdown and now has "readings" I don't like. I am running rear LP heater now and believe I am running off battery power and not recharging.

Maybe I'll go fire up the Gen and see if things "change".
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 12-31-2006, 01:55 PM   #5
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
I went and looked, panel was the same and my batt indicator was down to yellow so was definitely running off batts.

I unplugged from shore, and fired up the generator, at first the Powerline panel showed both 50amp and Gen as power in. Then after 20secs or so the 50amp light went out. The Xantrex panel also then started showing "Charge" again. So it looks like things are now working correctly on Gen. I am going to let it run awhile, then will try switching back to shore power and see what happens.

Crossing my fingers...

Man, for new batteries(according to seller, and they look new), they sure don't seem to last long.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 12-31-2006, 04:57 PM   #6
Winnebago Owner
 
Join Date: Oct 2003
Location: Fulltime- On the Road
Posts: 125
There's a 30amp "push-in" type breaker mounted on the front of the Xantrec. I'lll bet it tripped. Reset it and all will be fine.
__________________
Roadking - Homeless, full time, wandering gypsies
Winnebago Ultimate Advantage
Harley and Honda Civic
Roadking is offline   Reply With Quote
Old 12-31-2006, 06:09 PM   #7
Winnebago Owner
 
Join Date: Oct 2003
Location: Fulltime- On the Road
Posts: 125
McDuff -- The AC shore power for the 110v AC outlets comes from a 30 amp breaker in the coach main panel. This power then goes to the Xantrec 30 amp breaker then to a relay/switch in the Xantrec. From the relay/switch the power then goes to the sub panel and the various AC circuits in the coach. The relay/switch in the Xantrec switches when either the Generator is running, or when the invertor is turned on. This is why you have AC power (and the EMS panel illuminates) when the inverter is on or when the generator is on.


Reset the 30 amp "push in" breaker located on the front panel of the Xantrec invertor/charger and all will be fine.

Good luck.
__________________
Roadking - Homeless, full time, wandering gypsies
Winnebago Ultimate Advantage
Harley and Honda Civic
Roadking is offline   Reply With Quote
Old 01-01-2007, 05:30 AM   #8
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
Roadking - thanks for the info. Did not notice a breaker on front panel, I will check it when I go out later.

I was bummed last night, when I switched back to shore power, it was still screwed up. Might also try a different ext cord in a different plug, just for grins.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 01-01-2007, 08:03 AM   #9
Winnebago Owner
 
Navy Flier's Avatar
 
Join Date: Feb 2005
Posts: 221
I have tried twice to run elec heat from a 20 amp source and have tripped the house breaker both times. The problem is that on start up the elec heat can easily overwhelm the 20 amp breaker. Using elec heat on less than a 30 amp source just doesn't work. If you don't have 30 amps either use the gas heat or the generator.
__________________
Chuck & Carol
08 Horizon 40TD
04 Honda CR-V
Navy Flier is offline   Reply With Quote
Old 01-04-2007, 04:57 AM   #10
Winnebago Owner
 
Join Date: Dec 2006
Location: Tx
Posts: 130
Just to let everybody know <hanging head>

The extension cord/reel I was using(first time) also had a breaker in it. It was what was tripped.

Sheesh, you would think I'd know the KISS principle by now...

Thanks for all suggestions.
__________________
Rather be Ridin' than Rollin'
2003 UA 40E(wheelchair accessible)
McDuff is offline   Reply With Quote
Old 01-04-2007, 06:35 AM   #11
Winnie-Wise
 
SargeW's Avatar
 
Join Date: Sep 2002
Location: Fallbrook, Ca
Posts: 307
McDuff,

I had a similar situation recently when I too tried to run the heat pump off of a 20 amp circut and an extension cord. Only in my system I have installed a 50 amp Surge Guard with high and low cut out protection. After about 10 seconds my surge guard cut power to the coach. It resets itself after about 2 minutes.

I highly recommend a surge guard for just this kind of situation. It could save you from low voltage at a RV park from ruining one or more of your eletrical appliances.

Sarge
__________________
Marty and Diane, Fulltiming!

Our Travel Blog www.mytripjournal.com/rvnchickalaska
SargeW is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why did Winnebago drop Caterpillar? Catpowered Winnebago General Discussions 8 12-22-2008 01:14 PM
did I ruin my new batteries?? rick_od Electrical | Charging, Solar and Electronics 10 08-27-2007 01:46 PM
what did you replace the "RV Radio" with? LandHo Tech | Toys and Gear 13 07-21-2006 08:56 AM
Just did the roof! Too old for this!! smlranger General Maintenance and Repair 7 03-15-2006 07:13 PM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 05:14 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.