Old 05-19-2022, 10:56 PM   #15
Senior Member
 
Join Date: Dec 2021
Posts: 123
Quote:
Originally Posted by kwftlaud View Post
I have a 2001 Itasca Sundancer 27P
I am having a electrical issue with my front AC circuit.

I know the circuit line. I have disconnected it.

If its hooked up to the circuit breaker it shorts out the AC line and sparks fly when I try to plug it in. If I measure the resistance on the line it reads open. If I read the resistance to ground and across the AC lines on the 30Amp plug I get a high resistance ( open ). When I connect the black wire from the bad leg I get a high résistance also so I'm not seeing any shorts.
Yet when I plug it in with that leg connected sparks fly, but doesn't trip the breaker.
I am really stumped because in my mind, if the resistance is in the 100's of kilohms I shoud not be seeing sparks fly.
Any idea what I'm missing here?
Thanks

Kip
Check you slide for cables that are showing bare wires - anything shorting to ground could throw sparks... BTW, where are the sparks showing? If at the slide , you have a short where you see sparks...seeing sparks that don't trip a breaker indicates a weak short...one that emits sparks, but is at a lower current than the listed value of the circuit breaker...look for worn insulation on your wires.
DaddyRV779 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-20-2022, 06:12 AM   #16
Registered User
 
Join Date: Sep 2018
Posts: 1,205
I'll try again...

With the diagram provided by cbeierl, you could now further isolate each JB and outlet connections to narrow it down. As others wondered, how bad is the sparking, fine little sparklers or molten metal, arc welding meteor type sparks? TV plugged in? VCR/DVD player?
OldWEB is offline   Reply With Quote
Old 05-20-2022, 06:23 AM   #17
Senior Member
 
Join Date: Jul 2005
Posts: 5,996
Quote:
Originally Posted by Archer2 View Post
@Bigb56 I guessed that the OP was saying that the sparks flew when plugging the shore power cord into the power pedestal. Nothing else that I could think of made any sense. Of course checking the circuit with an ohmmeter doesn’t show any problem because the Converter doesn’t start drawing a load until it sees 120VAC at its input but when the 120VAC shows up then it’s “Katy bar the door!”
Also, @TandW I think you meant to say just the opposite of your description of how to interpret a multimeter when measuring resistance.
High resistance reading on VOM = continuity. So does low resistance. An open circuit produces Zero reading. Open circuit means no complete path for electron flow.
__________________
TandW
TandW is offline   Reply With Quote
Old 05-20-2022, 07:18 AM   #18
Senior Member
 
Newmar Owners Club
Entegra Owners Club
Join Date: Dec 2015
Posts: 1,640
I think I see what you’re saying. Using a VOM with an analog display (meter with a needle like a Simpson 260) if the needle is sitting against the left-hand stop then it’s 0V, 0 Amps but the scale printed on the meter says maximum resistance (open circuit). If the needle is full-scale and pegged to the right it’s max V, Max Amps but the scale says zero Ohms resistance (short circuit). So in terms of the meter's indicator, continuity is maximum meter deflection and an open circuit is zero deflection.
A digital VOM set on the resistance scale but not connected to anything will usually read “OL” for “overload” and when you touch the leads together it will read “0.00”.
Is that how you are looking at it?
__________________
2021 Entegra Aspire 44W
Previous: 2006 Newmar Essex 4508
2013 Tiffin Allegro Open Road
Archer2 is offline   Reply With Quote
Old 05-20-2022, 07:40 AM   #19
Senior Member
 
Join Date: Jul 2005
Posts: 5,996
VOM is switched to a resistance range. Touch leads together. Meter deflects indicating continuity. This test should always be done to check meter batteries. Connect meter leads to circuit to be tested. If no deflection, open circuit is indicated.
__________________
TandW
TandW is offline   Reply With Quote
Old 05-20-2022, 10:30 AM   #20
Senior Member
 
Join Date: May 2018
Posts: 3,220
Quote:
Originally Posted by bigb56 View Post
I don't think the converter is the issue because he says the circuit in question "shares the breaker with the converter" so the converter is connected when he plugs in and gets no sparks. From what he is telling us so far there is no load that he can account for.
I would like to know more about the sparks, a load spark/arc is not exactly the same as "shooting sparks". I have seen a short that causes shooting sparks but clears itself before the breaker trips caused by a single strand shorting out and melting, but not numerous times.
I'll be standing by waiting for more info.
I don't think the converter is the problem, he said the problem circuit shares a breaker with the converter, no sparks happen when the converter is the only thing on that particular breaker, adding the second circuit makes the sparks.


With this line disconnected everything in my rig works ( all appliances and AC ) No sparks when I plug in.
When I connect it back up to the 15 AMP breaker ( that it shares with the converter ) I will get sparks when I plug in the shore power . The breaker does not blow.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
bigb56 is offline   Reply With Quote
Old 05-20-2022, 04:34 PM   #21
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,971
Quote:
Originally Posted by TandW View Post
VOM is switched to a resistance range. Touch leads together. Meter deflects indicating continuity. This test should always be done to check meter batteries. Connect meter leads to circuit to be tested. If no deflection, open circuit is indicated.

__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Old 05-20-2022, 05:35 PM   #22
Senior Member
 
Join Date: Feb 2022
Posts: 355
I still haven't figured it out. Someone supplied me with wiring diagrams so I'll investigate some more soon.

But one thing I want to highlight.
The sparking was strong enough to make black marks all over the plug and socket. This is no slight arc.... its a massive short.
I would think I should be able to find somewhere a short to ground, but I cant.

I did do some work on the bedroom slide a few months ago, so, I am going to open that up and check out the 120 volt wiring there.

Thanks for all of the input.
Kip
kwftlaud is offline   Reply With Quote
Old 05-20-2022, 05:44 PM   #23
Senior Member
 
Join Date: Jul 2005
Posts: 5,996
By now you should have caught on. Other posters have responded with the very good and safe suggestion that you keep the pedestal breaker off, plug in and then turn the pedestal breaker back on. They also explained that your converter is drawing a lot of current when energized as its capacitors charge up. The only problem you are going to have is burned up spades on your power plug and or a burned up receptacle at your pedestal.
__________________
TandW
TandW is offline   Reply With Quote
Old 05-20-2022, 06:06 PM   #24
Senior Member
 
Newmar Owners Club
Entegra Owners Club
Join Date: Dec 2015
Posts: 1,640
@kwftlaud, as others have said what you are experiencing (and stubbornly insisting something is wrong) is exactly what happens if you connect or disconnect a circuit while it’s energized. It’s also the exact reason that you shouldn’t do it. Circuit breakers and switches are designed to positively make and break a circuit safely. Anytime you try to make or break a circuit while heavy current is flowing you will get some arcing-in fact, that’s how an arc welder works. The really heavy current in your case is only present for a fraction of a second and that’s why no breakers trip.
But maybe We aren't understanding what you are saying. Other than the arcing at the main power shore connector, does everything seem to operate OK? All the outlets work, converter is charging your batteries, appliances OK, etc?
__________________
2021 Entegra Aspire 44W
Previous: 2006 Newmar Essex 4508
2013 Tiffin Allegro Open Road
Archer2 is offline   Reply With Quote
Old 05-20-2022, 06:21 PM   #25
Senior Member
 
edge68474's Avatar
 
Join Date: Oct 2017
Posts: 1,937
Another interesting electrical thread.
Thank you for sharing.


EDIT: I was just reminded and learned something, Wahoo!!
__________________
Larry & Sheree & KD the CAT
2009 Holiday Rambler Admiral 30SFS Lewis County, Wa.
USN 1964-68, USS LEXINGTON CVS-16
edge68474 is offline   Reply With Quote
Old 05-25-2022, 11:49 AM   #26
Senior Member
 
SCVJeff's Avatar
 
Join Date: Dec 2006
Location: Santa Clarita, CA.
Posts: 2,645
I agree with Archer.. I didn’t read every word on all the replies, but what keeps standing out at me is “sparks fly and the breaker doesn’t pop”. To me that’s standard inrush current from a big inductor in the RV. A fan or a compressor motor, and certainly whatever you use as a charger has a nice big inductor in it (transformer). Those in-rushes are normal.. If you’re not popping a breaker, plug it in and see what happens. Probably nothing
__________________
_______________________________

Jeff - WA6EQU
'06 Itasca Meridian 34H, CAT C7/350
SCVJeff is offline   Reply With Quote
Reply

Tags
problem



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
120 vac clayfeet Newmar Owner's Forum 2 04-07-2017 01:35 PM
208Y/120 VAC Three Phase Shore Power Question xtechgeek Entegra Owner's Forum 5 02-05-2017 09:32 PM
Missing 120 VAC Receptacle patmsp Monaco Owner's Forum 4 10-03-2011 07:24 AM
Warning!! Warning!! 120 VAC Issue johnwr Alpine Coach Owner's Forum 16 08-22-2011 11:31 PM