Automatic Generator Start suggested settings?

I recently purchased a 2023 Newmar New Aire and am having some issues with the generator starting on the first try either manually or via AGS. The rig came with two Lithionics batteries (640AH combined) and AGS is set to come on at 30% charge left from the factory.

Whenever I try to start my generator, either manually or via AGS, it doesn't start the first try. It'll prime the fuel, crank a couple of turns, stutter as it tries to catch, but not fully start. This causes a generator fault. If I manually tell it to try starting again, it'll catch right away that second try and run with no issues. However with AGS, are there settings to either prime longer, crank longer, and/or try again? It appears with the AGS once you get a failed start and fault it is out of the picture until you manually reset things so it can try again. As it stands today, it will not auto start and run to then recharge my batteries on its own.

Best,
-Mark
__________________
2023 Newmar New Aire 3543
2018 Tiffin Wayfarer 24BW
2013 Fiat 500 Turbo Dinghy
MarkMaxPayne is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-24-2023, 06:56 PM   #2
Senior Member
 
Join Date: Aug 2019
Posts: 164
Sounds like fuel drain back/air getting in the fuel line during idle periods. Given it is a 2023 coach, warranty claim at the closest Cummins/Onan dealer would be my suggestion. If you want to get some more facts, do a test of how long it takes for the problem to develop. One day of idle off time, then two days, etc. until problem presents.
__________________
Pete
2019 Newmar Ventana LE 37
IRV2 Member November 2019
PeteDr is offline   Reply With Quote
Old 06-09-2023, 09:00 PM   #3
Senior Member
 
MarkMaxPayne's Avatar


 
Newmar Owners Club
Tiffin Owners Club
Join Date: Mar 2018
Location: Portland, OR
Posts: 552
Turned out that the chassis batteries were just garbage after being abused at the dealership. I replaced them as it was becoming obvious they just were not taking and holding a good charge after owning the rig for just a month. Now that I have new chassis batteries the gererator leaps to life very quickly.

Best,
-Mark
MarkMaxPayne is offline   Reply With Quote
Old 06-10-2023, 05:54 AM   #4
Senior Member
 
FOLEYMECH's Avatar


 
Newmar Owners Club
Join Date: May 2008
Location: Tabernacle NJ
Posts: 130
are the new batteries lead acid, or agm?
FOLEYMECH is offline   Reply With Quote
Old 06-10-2023, 09:15 AM   #5
Senior Member
 
Join Date: Apr 2015
Location: Rogers, AR
Posts: 2,617
Just a question or suggestion, in your first post you mention letting the batteries get down to 30% charge before starting the generator. I don't let my batteries get down near that low before starting the generator, or charger in storage.

I'm no expert on batteries, just go by what I read and in a battery article of an RV magazine, the statement was made that continually discharging wet cell and AGM batteries to less than 50% charge will drastically reduce the life of the battery. They also said that keeping the charge above 50% will keep it in a condition to last twice as long.

When I'm in storage and I see the batteries down to 12.4V (considered 80% charge) the charger goes on the batteries. My AGS is also set to similar settings.

Just some food for thought you may want research further. I've asked here on the forum about AGS settings and have never had any response, so I haven't been able to find any good, qualified opinions on how the AGS should be set.
__________________
2019 Fleetwood Discovery LXE 40M w/2021 Equinox
alank is offline   Reply With Quote
Old 06-10-2023, 11:26 PM   #6
Senior Member
 
MarkMaxPayne's Avatar


 
Newmar Owners Club
Tiffin Owners Club
Join Date: Mar 2018
Location: Portland, OR
Posts: 552
The batteries I replaced were the chassis batteries. Lead acid.

The batteries I was referring to in the original post which are configured by the factory to drop to 30% before the generator auto start kicks in are the house Lithium Iron Phosphate batteries. The BMS on those can let them hit near 0 for 3000 to 5000 times without doing any damage. 10 years later after that many full cycles they'll still hold over 80% of their storage capacity.

Very different battery chemistry and dynamics than traditional lead acid or AGM.

Now that the chassis batteries have been replaced, the generator auto start for the lithium house batteries is working fine.

Best,
-Mark
MarkMaxPayne is offline   Reply With Quote
Old 06-11-2023, 07:37 AM   #7
Senior Member
 
redbaron73's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Jun 2011
Location: Texas
Posts: 6,425
Blog Entries: 4
Quote:
Originally Posted by MarkMaxPayne View Post
The batteries I replaced were the chassis batteries. Lead acid.

The batteries I was referring to in the original post which are configured by the factory to drop to 30% before the generator auto start kicks in are the house Lithium Iron Phosphate batteries. The BMS on those can let them hit near 0 for 3000 to 5000 times without doing any damage. 10 years later after that many full cycles they'll still hold over 80% of their storage capacity.

Very different battery chemistry and dynamics than traditional lead acid or AGM.

Now that the chassis batteries have been replaced, the generator auto start for the lithium house batteries is working fine.

Best,
-Mark
I would probably set it to 15% when dry camping and feel very safe, knowing it can go to 0 and still be ok
__________________
2022 London Aire 4551 * 2022 GD Imagine 2800BH * 2021 RAM 3500 DRW * 2020 Wrangler
NHSO (Newmar Hoot, Sevierville Original)
Kindness Matters
redbaron73 is offline   Reply With Quote
Old 06-11-2023, 07:45 AM   #8
Community Moderator


 
Join Date: Aug 2018
Location: Full timing
Posts: 6,300
The AGS in our big Road Warrior toy hauler is set at 20% to start. Last September we had lithium batteries with 960AH installed along with 1600-watts of panels.
__________________
2018 Road Warrior 427
2013 Can Am Spyder RT Limited
2017 Ram 3500 w/Aisin w/4:10
2 Dachshunds DJ (RIP 9-12-19) & Joey (RIP 5-14-21)
hamm2018 is online now   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator auto start settings. pogoil Country Coach Owners Forum 8 01-18-2021 03:57 PM
AGS (Automatic Generator Start) settings woodosgood Newmar Owner's Forum 10 05-01-2017 11:19 AM
Auto generator start/stop settings RV Vagabond iRV2.com General Discussion 9 09-29-2016 09:00 AM
Automatic generator start system/Generator/shoreline automatic changeover switc Rac912 RV Systems & Appliances 14 01-12-2016 11:51 AM
Thermostat and Auto Generator Start Settings PizzaGuy Monaco Owner's Forum 10 05-10-2009 07:59 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:15 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.