Communication is more likely the RJ6 cable…it daisy chains…from control board to control board and then into the thermostat. The fact your thermostat is displaying anything means the fuse is good.
So, you have one control board in each rooftop unit and one in the basement next to the ME-AGS. Check the cable connections that look like phone wiring. Unplug clean, replug. Do this with the salesman switch in store position.
When you restore power see if it is talking, if not reference the relearn procedure in the manual. It is a button press method of making the thermostat query the network to find what is in the network. It reads the board configuration as set by the dip switches. They tell the thermostat if you have furnace, heat, pump, air conditioning, #1, #2, etc… and AGS. (Only on the basement control board).