Old 06-19-2022, 11:32 AM   #1
Senior Member
 
Join Date: Feb 2014
Location: Eclectic, AL
Posts: 154
Generator is coming on when plugged into 50 amp service

Generator is starting when plugged in to 50 amp service. just burned 500 dollars of diesel. Any ideas where to look for the cause? 2020 London Aire
__________________
Dr Donny
2012 King Aire, 2020 London Aire
Eclectic, AL 36024
drdonny is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-19-2022, 11:36 AM   #2
Senior Member
 
dizcom's Avatar


 
Freightliner Owners Club
Holiday Rambler Owners Club
Join Date: Jun 2021
Posts: 1,423
AGS Automatic Generator Start on your control panel. You may have it set to come on if the temperature inside your coach gets to a certain point or something similar like automatic exercise. Just shut AGS off.
__________________
2021 Holiday Rambler Armada 44LE
2021 Jeep Wrangler High Altitude toad w/Ready Brute Elite II
dizcom is offline   Reply With Quote
Old 06-19-2022, 11:37 AM   #3
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 22,209
How is the DC System Voltage before plugging in to 50A?

What DC Voltage is the Gen Auto Start set for?
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 06-19-2022, 11:47 AM   #4
Senior Member
 
Join Date: Feb 2014
Location: Eclectic, AL
Posts: 154
I am not there to know what is before hand Set to start at 11.8 V top off 13V run time 60 minutes AC was running with generator running
__________________
Dr Donny
2012 King Aire, 2020 London Aire
Eclectic, AL 36024
drdonny is offline   Reply With Quote
Old 06-19-2022, 05:27 PM   #5
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 20,839
It sounds like you're saying you were not there when this happened. If you lost shore power, it would have come on.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
Dutch Star Don is offline   Reply With Quote
Old 06-19-2022, 06:38 PM   #6
Senior Member
 
Join Date: Feb 2014
Location: Eclectic, AL
Posts: 154
Quote:
Originally Posted by Dutch Star Don View Post
It sounds like you're saying you were not there when this happened. If you lost shore power, it would have come on.
I left it at NIRVC for service. When I got there last night the generator had been running for a while evidently. I only had enough fuel to drive 60miles. The surge protector at the pole showed everything was good there at that end. Battery voltage on chassis and house looked normal. If the power did go off would the generator not shut down when power was restored?
__________________
Dr Donny
2012 King Aire, 2020 London Aire
Eclectic, AL 36024
drdonny is offline   Reply With Quote
Old 06-19-2022, 09:11 PM   #7
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2017
Posts: 1,109
Check the power history on Silverleaf. It shows the date/time when you lost shore power and when the generator turned on and off. With this you should be able to determine when the generator turned on because Silverleaf determined you had lost shore power.
__________________
2018 Newmar Mountain Aire 4531
flyboy013 is offline   Reply With Quote
Old 06-19-2022, 09:32 PM   #8
Senior Member
 
saddlesore's Avatar


 
Foretravel Owners Club
Join Date: Apr 2016
Location: Home is Where WE PARK IT...
Posts: 5,365
Hmmm... Also check the battery connections and check each battery..You may have one or more that are failing..
__________________
Retired truckdriver, Full Timing in a Foretravel.
Escapees of Box Elder, South Dakota
....Whether our shack is moving or parked.. We are still home.
saddlesore is offline   Reply With Quote
Old 06-20-2022, 04:11 AM   #9
Senior Member
 
RVStitchy's Avatar
 
Newmar Owners Club
Join Date: May 2020
Location: Fort Lauderdale, Fl
Posts: 574
Quote:
Originally Posted by drdonny View Post
I left it at NIRVC for service. When I got there last night the generator had been running for a while evidently. I only had enough fuel to drive 60miles. The surge protector at the pole showed everything was good there at that end. Battery voltage on chassis and house looked normal. If the power did go off would the generator not shut down when power was restored?
Do you know how many hours the generator ran evidently? The generator should shut off when you get to a quarter tank of fuel. On a London Air that would be 25 to 35 gallons remaining which would get you a lot further than 60 miles. Also surprised someone at NIRVC didn't notice a generator running for an extended period of time.
__________________
2022 Dutch Star 4369 FL Towing 2022 GMC Sierra 1500
Chris & Lee, Finnegan & Kirby (Double Doodled)
2020 Kountry Star 3709 towing Equinox.
RVStitchy is offline   Reply With Quote
Old 06-20-2022, 05:15 AM   #10
Senior Member
 
Join Date: Feb 2014
Location: Eclectic, AL
Posts: 154
Quote:
Originally Posted by RVStitchy View Post
Do you know how many hours the generator ran evidently? The generator should shut off when you get to a quarter tank of fuel. On a London Air that would be 25 to 35 gallons remaining which would get you a lot further than 60 miles. Also surprised someone at NIRVC didn't notice a generator running for an extended period of time.
That was what I have always heard, but the fuel gauge was red and said low fuel. I put 141 gallons in a 150 gallon tank.
__________________
Dr Donny
2012 King Aire, 2020 London Aire
Eclectic, AL 36024
drdonny is offline   Reply With Quote
Old 06-20-2022, 06:13 AM   #11
Senior Member
 
RVStitchy's Avatar
 
Newmar Owners Club
Join Date: May 2020
Location: Fort Lauderdale, Fl
Posts: 574
Quote:
Originally Posted by drdonny View Post
That was what I have always heard, but the fuel gauge was red and said low fuel. I put 141 gallons in a 150 gallon tank.
My subtle point is - are you sure the generator was running since you said "evidently". Or did the diesel disappear some other way? 141 gallons of diesel at a 1/2 gallon per hour is 282 hours of generator run time or 11.75 days. How many hours do you have on the generator now?
__________________
2022 Dutch Star 4369 FL Towing 2022 GMC Sierra 1500
Chris & Lee, Finnegan & Kirby (Double Doodled)
2020 Kountry Star 3709 towing Equinox.
RVStitchy is offline   Reply With Quote
Old 06-20-2022, 12:02 PM   #12
Senior Member
 
Join Date: Feb 2014
Location: Eclectic, AL
Posts: 154
Generator was running when I arrived to pick up Saturday night after leaving for service. After looking at Silverleaf history it came on around 11 Thursday morning. I used wrong word when I said evidently and also did not say coach was on full. Apologize for not making that clear. Anyway it had been running a long time. Added the amount of diesel added indicated generator did not shut down when got below quarter of tank as you would expect
__________________
Dr Donny
2012 King Aire, 2020 London Aire
Eclectic, AL 36024
drdonny is offline   Reply With Quote
Old 06-20-2022, 12:30 PM   #13
Senior Member
 
Rev. Roy's Avatar
 
Spartan Chassis
Join Date: Mar 2017
Posts: 909
Sorry! The generator cannot run below 1/4 of the tank because manufacturers put the fuel feed for the generator at that level. They do that so it can't drain the tank. So it would be impossible for a generator to drain it that much.
Rev. Roy is offline   Reply With Quote
Old 06-20-2022, 12:57 PM   #14
Senior Member
 
Join Date: Feb 2014
Location: Eclectic, AL
Posts: 154
I have been taught that my whole life. I have owned over 5 motorhomes in 20years (Bluebirds and Newmars) I respectfully disagree. Fuel gauge on Spartan dash said low fuel and bottom quarter of gauge was bright red. Spartan estimated distance to travel is what I stated. My gallons of fuel match up with my facts. Things do not always work in real life as designed.
__________________
Dr Donny
2012 King Aire, 2020 London Aire
Eclectic, AL 36024
drdonny is offline   Reply With Quote
Reply

Tags
generator, service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No 120 power plugged into shore power or using Generator larliebler Class A Motorhome Discussions 26 11-01-2018 04:39 PM
Smart EMS shows 30 amp only when plugged into 50 amp on my Holiday Rambler Imperial I davdamon RV Systems & Appliances 7 09-14-2018 05:38 PM
20 amp microwave plugged into a dedicated 15 amp fused circuit? eddndee MH-General Discussions & Problems 20 09-12-2018 08:08 PM
50 Amp TT Plugged into 30 Amp Service Bob55 RV Systems & Appliances 8 08-02-2016 05:50 AM
Can I use an external generator plugged into my outside land line input connector ? Markrving Class A Motorhome Discussions 13 05-10-2014 05:34 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:16 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2022, vBulletin Solutions, Inc.