Onan generator won't crank.

It is showing a fault code 46 - low battery or controller/inverter faulty. I connected the starter solenoid control terminal to +12 volts and the starter cranked the engine with no problem. This tells me that the voltage is sufficient and I have a good ground connection. That leaves the controller/inverter. This is a VERY expensive part. I am wondering if I have overlooked something. I would hate to spend that much money and not fix it. Any thoughts?

Thanks.
Bill
__________________

__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-11-2016, 03:18 PM   #2
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Did you get the 12 VDC from the same place the generator gets it from?

I would put a meter to ground and the starter with the normal wiring and what was there when I tried to start it. Assume there is a common connection for the 12 VDC. That is what you want to check if different from the actual starting motor.

If you do not have the manual it should be on line under the number on the generator.
__________________

nothermark is offline   Reply With Quote
Old 11-11-2016, 05:08 PM   #3
Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2016
Posts: 65
I got the 12 volts right from the battery cable lug on the generator's starter.
Bill
__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Old 11-11-2016, 07:36 PM   #4
JMH
Senior Member
 
Newmar Owners Club
Join Date: Mar 2016
Posts: 914
FWIW my generator switch/inverter failed at 2 hours of run time. Cummins said it was a known issue. Even as old as yours is, you may want to check with them.

Mark and Louene Hetrick
Newbee the last VTDP 3725
JMH is offline   Reply With Quote
Old 11-12-2016, 06:45 AM   #5
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Without the model of the generator everything is speculation. You should really pull it down for yourself and see what the trouble shooting section says.

Assuming you used a jumper between the starter power terminal and the starter solenoid to run the starter then the next step for me would be to check the leads to the control board. If you have a loose or corroded lead especially in a connector that could supply less than 12 V to the sensing and control circuits. If all of them are good and the on board start switch does not work then a board is the next step unlless you are up to component level troubleshoot and repair.
nothermark is offline   Reply With Quote
Old 11-13-2016, 07:10 AM   #6
Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2016
Posts: 65
The generator is an HDKAJ 7500 watt.
Bill
__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Old 11-13-2016, 02:28 PM   #7
Member
 
Matador 01's Avatar
 
Join Date: Jun 2010
Location: San Antonio, TX
Posts: 40
I have the same generator as you in a 2003 Dutch Star. My problem was similar, except it started up in the middle of the night while on shore power (I don't have AGS). After that it wouldn't start, problem was the controller/inverter.
__________________
2003 DSDP NKK 18052
Matador 01 is offline   Reply With Quote
Old 11-13-2016, 06:15 PM   #8
Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2016
Posts: 65
Thanks for all of the replies. I think I will remove all of the covers and check the connections to the control board. If that doesn't bring the problem to light, I will have to buy a control board/inverter. (Ouch) l need to get this resolved.
Thanks again for your help.
Bill
__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Old 11-16-2016, 01:41 PM   #9
Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2016
Posts: 65
Well, I have determined that the signal from the control board to the starter solenoid is not high enough. The starter B+ is 12.35 volts. The starter solenoid signal is only 5.5 volts when the start switch is pressed. I removed the inverter assembly and opened it up to access the control board. There are 2 relays on the board. One is for the glow plugs and the other is for the starter signal. Since I have 12 volts going to one side of the contact and only 5.5 volts on the other side, I believe the relay is bad. I have ordered two relays from DigiKey. I will change them both while I'm in there and put it back together. Hopefully, this will get me going again. If not, then l will just have to spend the money for a new controller/inverter. The relays were less than $20 including shipping. I figure it's worth a try to fix the control board.

Bill
__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Old 11-17-2016, 07:51 AM   #10
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Good find, let us know how it works out!
nothermark is offline   Reply With Quote
Old 11-21-2016, 01:57 PM   #11
Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2016
Posts: 65
I replaced the relays and reinstalled the controller/inverter. The generator still will not crank. I guess I will have to bite the bullet and buy another controller/inverter unit. 😖 I'm very disappointed.

Bill
__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Old 11-22-2016, 08:17 AM   #12
Senior Member
 
Algoma's Avatar
 
Join Date: Nov 2007
Location: Charleston, WV
Posts: 3,221
If you intend to keep the coach for some time you may want to replace the generator. On my previous coach with a 7500 I had to replace the inverter twice. In those days you could get refurbished, but now you have to buy new and they aren't cheap. You can get the 8k and a decent warranty period.
__________________
John and Mary Knight
2015 Newmar Ventana 4311 - wheelchair accessible
2015 Cadillac SRX Luxury AWD
Algoma is offline   Reply With Quote
Old 12-01-2016, 08:51 AM   #13
Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Jun 2016
Posts: 65
Well, I finally got around to putting my generator back together. It now starts and runs as it should. $142 for a starter that didn't help, $20 for relays that didn't help and $1842 for a controller/inverter that did help. So $2004 later, and several afternoons of labor and I'm back in business. Sometimes you just have to spend the money to enjoy this pass time.

Thanks for all the suggestions and moral support throughout this challenge.

Bill
__________________
Bill and Brenda
2003 Newmar Mountain Aire 4097
Wborst is offline   Reply With Quote
Old 12-02-2016, 07:45 AM   #14
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Thanks for telling us what happened.

I'm curious. Did you but the board from Onan or someone else? Was there an option to have it repaired or return for some credit? I would think a board that expensive would be worth repairing but would take a fairly elaborate test setup to properly check the work afterward. Not something I would go into business doing on a whim but something I wonder about somebody else doing.
__________________

nothermark is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Crank Up Antenna to Crank Up Dish Bobski12 Technology: Internet, TV, Satellite, Cell Phones, etc. 2 06-19-2016 09:35 PM
Old Crank Sat Out New Automatic In - Crank Replaced With... Nomad Mike MH-General Discussions & Problems 4 11-02-2015 01:11 AM
Generator Won't Start - Engine Won't Crank Rob Howden RV Systems & Appliances 10 08-02-2015 07:35 PM
Onan Generator won't crank dcruze RV Systems & Appliances 13 08-01-2013 04:49 AM
Onan Genset won't crank - ideas? emiddleb Winnebago Industries Owner's Forum 8 02-25-2009 01:12 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:16 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
×