Old 07-17-2021, 08:52 AM   #1
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Onan qd 8000 hdkak won't run when wet

As the title says.

A few weeks ago I was washing my coach and decided to wash the generator and compartment due to heavy dust build up.

After doing so I started the generator to dry it out and it kept shutting off.

So I let it sit for an hour then all was well.

OK I won't do that again.

This past weekend we had to travel from a campground to the race track which is Dry camping, (a not so common situation for most) but it was raining moderately.

When we got set up and started the generator and it shut off, I tried it several times, then checked for codes and found a Code 38 Overload.

Anyone who knows anything about electrical systems knows that there is no load on the generator for at least 1-2 minutes as the transfer switch delay prevents starting with a load on it.

After doing some reading, I flipped the breaker on the Onan, started it, let it run for 5 minutes then flipped the breaker and all was well.

I have come to the conclusion that the breaker or circuit board or something else is getting wet causing a short.

Once it dries out all is well.

Interestingly enough I have run this by the Onan specialist at a freightliner dealer, The Onan specialist at a Cummins dealer, and called Cummins Direct.

None of these experts have ever heard of this nor have any suggestions.

I am an Automotive expert for over 45 years and the lack of critical thinking is gone from the industry, even when I provide detailed clues that I can duplicate they are dumbfounded.

So I thought I would post this up for discussion.

Unfortunately I have a coach that the Generator has to be removed for anything other than oil changes and it has to go out the bottom which requires a Pit or a set of 4 big truck lifts by the wheels.

Since this is a pretty big forum I suspect someone else has experienced this and maybe found a solution.

Ted.
__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-17-2021, 07:35 PM   #2
Senior Member
 
Ken C's Avatar
 
Join Date: Nov 2007
Location: Fulltime, Formally SF Bay Area
Posts: 634
I had a similar situation on a prior coach with the 7.5 Onan after driving through a heavy rain storm. I was able to get it to keep running by shutting off the breaker on the generator and let it run for at least an hour to hope the heat and air movement would dry out what ever got wet which it did. Turned the breaker back on after letting it run and was fine and continued to us it for the next 4 days without a problem.
__________________
Ken C
2018 Dutch Star 4052 Spartan
2015 Jeep Cherokee Trailhawk
Ken C is offline   Reply With Quote
Old 07-18-2021, 06:41 AM   #3
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Thanks for chiming in Ken, seems you had the exact same symptoms and solution albeit temporary.

I guess the bigger question is WHAT is getting wet causing this.

My gut tells me it's the Breaker, which no longer has a weather boot over it Like my last generator had.

Seems odd that a breaker would be open to the elements.

Ted.
__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Old 07-18-2021, 02:42 PM   #4
"Formerly Diplomat Don"
 
Dutch Star Don's Avatar
 
Newmar Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 24,041
With the coach aired up, if you can, slide up under the generator and there is usually enough space to sit up behind the generator and in front of the axle. You should see a multi wire connector and wiring harness attached to the rear of the generator. Disconnect that plug, dry it out and use some dielectric grease to seal it. See if that solves the issue.

Typically, the above fix is for generators that won't start when wet, but may resolve your issue.
__________________
Don & Mary
2019 Newmar Dutch Star 4018 (Freightliner)
2019 Ford Raptor
Dutch Star Don is offline   Reply With Quote
Old 07-18-2021, 06:25 PM   #5
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Quote:
Originally Posted by Dutch Star Don View Post
With the coach aired up, if you can, slide up under the generator and there is usually enough space to sit up behind the generator and in front of the axle. You should see a multi wire connector and wiring harness attached to the rear of the generator. Disconnect that plug, dry it out and use some dielectric grease to seal it. See if that solves the issue.

Typically, the above fix is for generators that won't start when wet, but may resolve your issue.
I will take a crack at it thanks for the tip.
__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Old 09-11-2021, 09:09 AM   #6
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Solution

I have a solution for the problem, a weather boot for the circuit breaker

https://www.digikey.com/en/products/...113-40/1995319
__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Old 09-11-2021, 10:48 AM   #7
Senior Member
 
RandDescape's Avatar
 
Newmar Owners Club
Spartan Chassis
Join Date: Jul 2018
Posts: 577
Ted, I remember another member having a similar issue with either a VT or a DS sometime 12-24months ago. I did a few searches but couldn't find it.

My memory is that they put a weather boot around the breaker much like the one you are planning to install. So I think you are on the right track. I think in that same thread someone else was looking at putting in a weather strip to prevent water spray from coming in the hood and getting in there.

- Richard
__________________
Richard & Denise
2019 VTDP 4310 K2
2019 Expedition, Nighthawk & AF1
RandDescape is offline   Reply With Quote
Old 09-12-2021, 07:53 AM   #8
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Quote:
Originally Posted by RandDescape View Post
Ted, I remember another member having a similar issue with either a VT or a DS sometime 12-24months ago. I did a few searches but couldn't find it.

My memory is that they put a weather boot around the breaker much like the one you are planning to install. So I think you are on the right track. I think in that same thread someone else was looking at putting in a weather strip to prevent water spray from coming in the hood and getting in there.

- Richard
So this seal is 8.23 Retail probably cost .50 cents each to make in bulk.

Why Oanan decided it was a good Idea to have a circuit brake open to water intrusion is beyond me or any common sense thought.

I am convinced this is the solution and will report my results.

It will be easy to prove out because I can duplicate the issue by simply spraying the generator with water, I have done it several times.

I will install the weather boot on the circuit breaker then spray the generator with water to test it and report.
__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Old 09-17-2021, 07:46 PM   #9
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Just got tracking info I will have my circuit break weather boot next week.

Looking forward to testing this.

Ted.
__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Old 10-12-2021, 04:58 PM   #10
Senior Member
 
Vickie 4369's Avatar
 
Join Date: Nov 2012
Location: WATERBURY, CT.
Posts: 1,219
Mission complete

Finally had some time to tinker last weekend.

This is not an easy job with baseball mitts for hands.

I first tried to remove the entire front panel but something inside said Nope not happening!

Rather than take a chance and break something I removed the service panel to the left of the switch and removed it from the radiator fill cap and fuses and set it aside.

After getting the switch unbolted I used a step drill to open the switch Ports in both the panel and support bracket.

I worked the booth through both the support bracket and panel and struggled for 20 minutes trying to get the switch in position but no dice.

I then decided it would be better to put the boot through just the external panel and sandwich the boot between it and the support bracket.

With a pick and some persistence, I managed to get the switch in to position and get 1 screw started then proceeded to get the others all started, them made sure the boot was neutral then tightened all the screws.

Here are a few pics of the finished product.
Attached Thumbnails
Click image for larger version

Name:	IMG_6952.jpg
Views:	56
Size:	136.5 KB
ID:	345907   Click image for larger version

Name:	IMG_6951.jpg
Views:	40
Size:	120.8 KB
ID:	345908  

__________________
My name is Ted, My coach 2019 NEWMAR Ventana 4369 (Vickie) Cummins L9 451 Horsepower.
Vickie 4369 is offline   Reply With Quote
Reply

Tags
onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 8000 wont run (Fault Code 15) DebnDan Class A Motorhome Discussions 25 03-31-2021 06:38 PM
Onan 8000 HDKAK fuel filter change Bigdee Monaco Owner's Forum 8 09-17-2017 12:08 PM
8000 QD HDKAK Spec K Onan quits after 10 min. dtrvler RV Systems & Appliances 6 03-24-2013 03:21 PM
Onan 8000 HDKAK walkingplow RV Systems & Appliances 4 12-15-2011 10:35 AM
Changing Fuel Filter in Onan 8000W QD Model HDKAK al.m RV Systems & Appliances 4 01-06-2008 05:09 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:25 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.