PCS Controller Failure; GFCI Fault? Floor Heater Issue?

Problem: Recently I have been having trouble with my front floor heat, and it was suggested to check the GFCI in the half bath. It looked basically fine with no fault evident, but when i tested the unit, a big spark behind the outlet occurred and then the breaker for that line and the main 50 amp breaker in the half bath as well as the park's power pedestal 50 amp breaker blew. Obviously this wasn't good, and i figured replacement of the GCFI was in order. What I didn't appreciate was the resulting collateral damage.

Diagnosis: Once all of the breakers were restored, and the various devices onboard the coach restarted, I noticed the front and mid AC units were not working. Inspection of the PCS MONITOR up front read that we were pulling 96 (yes 96!) amps on L1 and causing essentially all PCS controlled devices to be shut down to compensate. After reading on the the forum herein, I discovered that the PCS BOARD (top section of the main power panel in the half bath) had likely been fried by the apparent short caused by the likely faulty GCFI. Piecing together other threads I learned that there is one 7.5A 12V fuse in the half bath 12v fuse panel that controls the MONITOR up front, and if one pulls that fuse, it disables the MONITOR and allows one to 'limp' home. This is a misnomer, because disabling the PCS controller basically is a blast to the past wherein one needs to monitor their own power consumption manually - fairly easy to do for a week or two.

FIX: First and foremost we replaced the GCFI. No sense in taking chances despite the apparent now normal operation of the unit since the short. Ordered a new board from PCS which only took a couple of days, and then replaced this unit. Not an easy job due to the number of wires you have to keep track of, but manageable. Don't forget to this with ALL power off, and note that the bottom segments in the main panel are independently energized by the inverter. One of the keys is unscrewing the main panel and pulling out a bit to get to the wires in back of the board - thanks to another member of IRV2. Upon replacement of the 7.5A 12V fuse, everything returned to normal - except I still don't have front floor heat. Any ideas?

This picture is of the new board before and after installation with my wiring organization tip. (Finally can justify the multicolor selection of electrical tape.)
Attached Thumbnails
Click image for larger version

Name:	IMG_3110.jpg
Views:	5
Size:	362.0 KB
ID:	302708   Click image for larger version

Name:	IMG_3106.jpg
Views:	5
Size:	222.2 KB
ID:	302709  

__________________
Phil and Laura (and Sam too!)
2017 DSDP 4369 on Spartan K2
2017 Unltd Rhino Rubi Recon Toad
DrPhil is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Reply

Tags
floor, heat, heater



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No AC to GFCI outlet string, but GFCI is good Eric1959 RV Systems & Appliances 12 03-21-2019 08:38 PM
Bounder: 2016 Bounder 33C - GFCI keeps tripping (Internal to RV, not house GFCI) nehmia Fleetwood Owner's Forum 8 10-22-2016 07:34 AM
Ground fault (GFCI 20Amp plug) alpinejimy Alpine Coach Owner's Forum 4 03-06-2015 10:10 AM
DSI Fault and GFCI circuit tripping Boblevy Class A Motorhome Discussions 9 03-04-2014 08:55 AM
No very good with pcs araucano Technology: Internet, TV, Satellite, Cell Phones, etc. 4 02-25-2009 10:19 AM


All times are GMT -6. The time now is 09:45 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.