Quote:
Originally Posted by racer0624
My PD 52 won't switch over to generator. We've been on shore power for 2 months. I'm wondering if it might just be a stuck contact. Any ideas?
|
First a disclaimer. If you are not experienced or are uncomfortable working with 120/240 voltage have repairs done by someone who is. That said there are several things that are easy and safe to check.
First thing to check is the breakers on the generator. There should be two either on the right side or the front. If you started the generator under load they may have tripped. Make and model of generator would help
Transfer switches come two way. One is shore power priority, the other is generator priority. I've had both and since yours is working on shore power, I would guess that is what you have.
It would be helpful to have the make and model of the transfer switch.
Where I would start is with power and generator off. Take the cover off it. Check for burnt wires, loose grounds into the buss bar anything that looks abnormal.
Next, still with power off you should be able to see the magnetic relays on the ATS. One should be out, the other in. Push on them both and see if they move. The magnet or relay may have failed. I had one that was shore power priority, and had no generator power. I could push the relay in and the generator would energize. As soon as I let go it would stop.
Some newer ATS these are completely enclosed. Then the only thing you can do is determine which line in is for shore power and which is for generator. Start the generator, get your VOM out and test voltage between one line of the generator in and the ground. Check both sides. Now check the voltage going out. If you have generator power going in but not out your ATS has failed.
Newer ones are a little more complicated as they have some electronics in them but they come as a complete non repairable unit. You just take it out and put a new one in.
It is very rare that contacts would stick. Especially since you have been on shore power. Turn your shore power off and back on with the breaker at the pedestal and you should hear an audible click. My newest one makes several noises. I'm assuming that is the electronics determining what sort of power it has coming in.
Most of all be careful.