This is the same procedure we use:

But we include a surge protector when connecting to the pedestal. This runs a diagnostic test on the pedestal to make sure it’s working correctly. It’s has saved us a few times from bad pedestals.

Turn off the air conditioning unit.
Stop generator
Ensure pedistal breaker is turned off
Connect shore power cable to pedistal
Turn on pedistal breaker
Turn on air conditioning
__________________
JMCherry
2018 GD, Imagine 2950RL
2011, 43QPG Tiffin Allegro Bus
JMCherry is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-17-2020, 08:21 AM   #58
ptw
Senior Member
 
ptw's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Apr 2016
Posts: 1,412
Quote:
Originally Posted by mjq1987 View Post

This contact arcing can cause pitting, discoloration, scorching or melting on the metal surfaces on the plug and/or receptacle. This damage may be minor, but eventually it could lead to a high resistance connection which leads to excessive heat generation which can lead to additional component damage and fires.
I agree.

If your cord is shorted or you have a problem on your coach, you may get burnt when plugging into the outlet with the breaker on. Always safer to turn on the power with the breaker.

A big reason for campground outlets going bad is people plugging into them without turning them off. As mentioned, the arcing will also damage your plug over time.

Another good practice is to adjust the length of your cord before turning the power on at the pedestal. I always plugged in, turned the power on, then adjusted the length of the cord on the reel and closed the bay door, before someone showed a picture of the contacts on the cord reel. The contacts are not good quality carbon brush contacts that are normally used on cable reels. The contacts are just spring metal and will cause pitting on the cable reel if turning the reel with power turned on.
__________________
Paul, Christy and Leap
2017 Dutch Star 4018, 2021 Jeep Wrangler
ptw is offline   Reply With Quote
Old 08-17-2020, 12:37 PM   #59
Senior Member
 
roblaura's Avatar
 
Join Date: Feb 2014
Location: Tampa FL & NE Georgia
Posts: 269
Similar to other comments, we do the following when the coach is parked and ready for set-up:

1.Shut off the AC units at the thermostat
2.When the AC units cease operating, shut off the generator
3. Connect coach to post electric (breaker off, connect cable, breaker on)
4, Turn the AC units back on.

All of this only takes a few minutes.
roblaura is offline   Reply With Quote
Old 08-17-2020, 02:40 PM   #60
Member
 
Join Date: Sep 2017
Posts: 30
Oh my gosh. Someone told you to do this? Was this a someone who sells new units to replace yours?

1. Always shut the a/c units down. It won't get too hot too quickly you should have 10 or so minutes of residual cool. Let your generator run for 3 minutes with minimal load to cool cylinders before shutting it down.

You can be using this time to level and pushing slides out etc etc.

2. After 3 min Shut down generators. Then plug in power. Turn A/C back on, etc.
jpuckett001 is offline   Reply With Quote
Old 08-17-2020, 11:20 PM   #61
Member
 
LHRanch's Avatar
 
Join Date: Nov 2019
Location: Arizona
Posts: 36
Quote:
Originally Posted by mjq1987 View Post
the most likely result in our low voltage scenarios is potential physical damage to the metal surfaces that the arc forms between. This contact arcing can cause pitting, discoloration, scorching or melting on the metal surfaces on the plug and/or receptacle. This damage may be minor, but eventually it could lead to a high resistance connection which leads to excessive heat generation which can lead to additional component damage and fires.
It's worth noting that you can develop this problem at other times than plugging and unplugging, if you overextend your cord, have kids tripping over it, etc. such that it gradually extracts itself from the outlet. We had this situation a couple months ago, melted both the outlet and the end of the RV cord, both had to be replaced.
LHRanch is offline   Reply With Quote
Old 08-18-2020, 04:36 AM   #62
Senior Member
 
Piros1's Avatar
 
Join Date: Dec 2015
Location: Dittmer, MO 63023
Posts: 1,123
Quote:
Originally Posted by mjq1987 View Post
Arc flash is the conduction of electricity across a high resistance medium. The term is usually reserved for high voltage situations where huge amounts of current can be generated during the event.

In our case, for 30A or 50A power connections, what happens when a breaker shuts or opens or a power plug under load is removed or plugged in, is that a brief arcing can occur between the load contact (plug) and the supply contact (receptacle) of the circuit. Unless you have contact with the arc or are surrounded by a flammable environment when it happens, the most likely result in our low voltage scenarios is potential physical damage to the metal surfaces that the arc forms between. This contact arcing can cause pitting, discoloration, scorching or melting on the metal surfaces on the plug and/or receptacle. This damage may be minor, but eventually it could lead to a high resistance connection which leads to excessive heat generation which can lead to additional component damage and fires.

Most breakers are quick acting to minimize arcing and some breakers have arc fault detection and tripping (not on our RVs). The quick acting contact movement minimizes arcing and contact damage, but it still happens and breakers do wear out over time.

Minimizing arcing is the reason why it's always best, under any electrical scenario regardless of the voltage and current involved, to connect/disconnect circuits and loads when they are not operating. The arc you get on a breaker that is shut/open with no/minimal load applied is less than what you get when you shut/open it under load.
This is a very definitive and clear answer, I guess I should of been more definitive. I hate to see folks have problems that are preventable. As you stated odds are you are not going to be hurt by the flash but I have seen equipment plugs/receptacles ruined from being unplugged under load. F FF own the if repetitively doing this will eventually cause issues.
__________________
2005 CC Affinity 770, 2006 Jeep TJ
2015 Newmar Essex 4553 2022 Jeep Gladiator.
Piros1 is offline   Reply With Quote
Old 08-18-2020, 04:41 AM   #63
Senior Member
 
Piros1's Avatar
 
Join Date: Dec 2015
Location: Dittmer, MO 63023
Posts: 1,123
Quote:
Originally Posted by ptw View Post
I agree.

If your cord is shorted or you have a problem on your coach, you may get burnt when plugging into the outlet with the breaker on. Always safer to turn on the power with the breaker.

A big reason for campground outlets going bad is people plugging into them without turning them off. As mentioned, the arcing will also damage your plug over time.

Another good practice is to adjust the length of your cord before turning the power on at the pedestal. I always plugged in, turned the power on, then adjusted the length of the cord on the reel and closed the bay door, before someone showed a picture of the contacts on the cord reel. The contacts are not good quality carbon brush contacts that are normally used on cable reels. The contacts are just spring metal and will cause pitting on the cable reel if turning the reel with power turned on.
I had to bypass my cord reel on my new to me coach due to this exact problem. I assume the previous owner must have been doing what you are referring to. When I returned home with the coach I disassembled the reel and discovered the contacts were burned up from arcing. My replacement will be the type that does not use contacts, it spools the cord in a storage tube like I have on my Country Coach.
__________________
2005 CC Affinity 770, 2006 Jeep TJ
2015 Newmar Essex 4553 2022 Jeep Gladiator.
Piros1 is offline   Reply With Quote
Old 08-18-2020, 12:47 PM   #64
Senior Member


 
Newmar Owners Club
Join Date: Aug 2014
Location: WA
Posts: 536
Just an update to my last post. Service center found ground wire loose at transfer case and tightened all connections. Will check things out when we go on it next time.


Mahdi & Debbie
2019 Dutch Star 4018
2020 Tahoe LT
mahdi is offline   Reply With Quote
Old 08-19-2020, 09:30 AM   #65
Senior Member
 
Join Date: May 2017
Posts: 1,190
Quote:
Originally Posted by mahdi View Post
Just an update to my last post. Service center found ground wire loose at transfer case and tightened all connections. Will check things out when we go on it next time.


Mahdi & Debbie
2019 Dutch Star 4018
2020 Tahoe LT
Guess you are referring to your post #22 on page 2? So what transfer case? And exactly what problem did this solve?
__________________
Elbridge Price, 1998 Dutch Star Diesel Pusher
Cummins 6.8.3 mechanical injectors, Spartan Chassis
2016 Toyota Prius; Acme EZE Tow Dolly
tommar is offline   Reply With Quote
Old 08-19-2020, 09:49 AM   #66
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,750
Quote:
Originally Posted by Piros1 View Post
First never plug or unplug your power cord into the power pedestal without turning the supply breaker off first. You can arc flash and this is an unsafe procedure and can be very dangerous.
I've stayed at many parks where you don't get the breaker on the pedestal.

Owner has a breaker room for the park.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 08-19-2020, 11:29 PM   #67
Senior Member
 
Piros1's Avatar
 
Join Date: Dec 2015
Location: Dittmer, MO 63023
Posts: 1,123
Quote:
Originally Posted by 96 Wideglide View Post
I've stayed at many parks where you don't get the breaker on the pedestal.

Owner has a breaker room for the park.
You can turn the main off in your RV and essentially do the same as shutting power at the pedestal. This would be the option if you there is no shut off at the pedestal not the preferred method but better than plugging it in under load. As stated earlier plugging in under load will create arcing on the plug and receptacle causing bad connections and creating excessive heat that can melt the insulation on the wires and plug.
__________________
2005 CC Affinity 770, 2006 Jeep TJ
2015 Newmar Essex 4553 2022 Jeep Gladiator.
Piros1 is offline   Reply With Quote
Old 08-19-2020, 11:54 PM   #68
Senior Member
 
FL420's Avatar
 
Join Date: Jan 2018
Posts: 3,009
Quote:
Originally Posted by Piros1 View Post
You can turn the main off in your RV and essentially do the same as shutting power at the pedestal. This would be the option if you there is no shut off at the pedestal not the preferred method but better than plugging it in under load. As stated earlier plugging in under load will create arcing on the plug and receptacle causing bad connections and creating excessive heat that can melt the insulation on the wires and plug.
Now why didn't I think of that??[emoji848]
Thx for the tip!
[emoji40]
__________________
2005 Monaco Knight 40PLQ; Cummins 8.3L ISC330, Pacbrake, Allison 3000, Roadmaster RR8R, ScanGauge D, 2004 Kawasaki Vulcan VN750(Geezer Glide) on a Versahaul carrier pulling a 2013 Kia Soul+; 2.0L, 6 speed Sport shifter(great car) on an American Car Dolly(great dolly.)
FL420 is offline   Reply With Quote
Old 08-20-2020, 08:30 AM   #69
Senior Member


 
Newmar Owners Club
Join Date: Aug 2014
Location: WA
Posts: 536
Sorry Tommar. I meant to say transfer switch not transfer case. Yes I was referring to my post about no power when connecting to CG after generator was turned off.


Senior moment.



Mahdi & Debbie
2019 Dutch Star 4018
2020 Tahoe LT
mahdi is offline   Reply With Quote
Old 08-20-2020, 09:14 AM   #70
Member
 
Join Date: Sep 2018
Posts: 62
breaker

You know that a breaker is not designed to be a switch. When it is used as a switch its life is cut very short. I plug in hot, just like everything in my S&B.
__________________
Tom & Zandy
2017 DSDP 4369
2007 Country Coach sold
texskeet is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Getting 50A installed at the house, quick check.. ls1ashley Tiffin Owner's Forum 12 05-21-2018 12:23 PM
50A RV to 50A Welder dogbone Ramblin iRV2.com General Discussion 17 08-04-2013 12:05 PM
What do you do after you get there - FL/TX/AL IC2 Just Conversation 15 11-01-2011 06:29 AM
TRUE 50a vs BOGUS 50a AFChap MH-General Discussions & Problems 18 08-02-2010 08:26 PM