Replace older Dometic Penguin Heat Pumps with Newest Penguin II Units.

For those of you that want to personally replace your older ducted Penguin Heat Pumps (HP) here are my thoughts on my DIY on my 2007 Newmar MADP 4528.

1. The front #1 HP was operational, but never seemed to deliver the air flow of the other units, even on high fan position. #2 HP mid coach had a frozen compressor. #3 rear was intermittent, stick reversing valve. Finding out what was wrong took me a few days on the roof and lots of internet searching on the subject. I am a retired mechanical engineer with a decent electrical background. I can see where it takes a quality RV tech to diagnose the RV systems and do the correct thing.

2. Once it was determined that 2 HPs needed replacement we elected bite the bullet to do all 3 units and update the 5-button Dometic thermostat to the 12-button CCC2 thermostat. The current Dometic low profile HPs require an adaptor board to work with the older 5-button thermostats and while replacing only the #2 only was an option, I felt it made more sense to do it all.

3. After researching three of the Dometic Penguin II high capacity Heat Pump 651816.CXX1C0 were bought from PPL out of Texas. PPL had them on sale for $999 each with decent shipping rate.

4. Called Newmar and found out that the only additional Newmar part required was a bent L shape gasket ( Newmar Part Number 52715) to separate supply air from return air. It mounted within each 14" square Dometic gasket on the underside of the Penguin.

5. I got a shrink wrapped pallet from PPL within a week, excellent. Now how to get the old ones off the roof and the new ones up there. I rented a hand crank material lift with a 600 lb capacity and a 18 foot max lift. It folded up and with two person easily went into the standard bed of a ford pickup. $150 per week. Turned out to be a very good decision on the lifting up and down. See attached picture. Click image for larger version

Name:	Equipment Lift.jpg
Views:	782
Size:	79.8 KB
ID:	92939

6. Elected to replace the #2 unit first, as it was the one totally dead with frozen compressor. I made a long temporary RJ-11 Communication cable, not the usual telephone cable, different pin-out, to connect #1 and #3 HPs together. Set the dip switch on the old #3 HP control board so it thought it was zone #2. This was to maintain heating and cooling while replaced #2 HP.

7. Turned off the power distribution panel breaker for # 2 HP, tested for power, labeled wires and took pictures on cell phone. The only somewhat difficult part was the removal of the four lag bolts that Newmar uses to mount their roof top units. Required a 1/2 inch drive 6-point socket and a long flex handle. I looked at the lag bolts when all four were out and there was one with a very worn tip threads. Went to Home Depot and purchased 9 of the shorter ones and 3 of the longer style. After lifting and wiggling I got it to lift off. Set aside the old HP and thoroughly scrapped and cleaned the area. Poured water in the two condensate drip pockets, underneath the HP, installed in the roof. For the ones not draining well, I took apart and cleaned the condensate drip pockets in the roof. The drip pockets have clear vinyl tubing that goes to a PEX pipe that drains at the rear of the coach, each side. You will need to blow that tubing out and not kink the tubing when re-installing. Wish Newmar had installed plastic tubing with nylon thread reinforcement to prevent kinking. For some unknown reason all the ones on the driver's side were clogged. I used non-leveling caulk on condensate pockets and silicone caulk on the lag bolts.

8. I got the DW up on the roof to assist me in positioning the new HP on the opening. Got her lined up and slowly drew down the four lag bolts till the foam pads at the four mounting position were one-half the original height. Installed power and did all the control wiring short of the RJ 11 communication cable. At this point set the dip switches for zone 2 and HP on the new control board and installed the cover. By the way the new Penguin covers are a vast improvement. The old flimsy ones would crack if you looked at them wrong. Thanks to Dometic for improving that part!

9. Installed the new CCC2 thermostat temporarily with tape next to the old one.

10. Removed #1 HP. Noted that the aluminum duct tape had pulled loose around the plenum and was partially blocking the supply air duct. Removed all the tape in the area, carefully cleaned and re-taped with a high quality low temperature rated aluminum duct tape. Also noted that Newmar had installed the high voltage Junction box partway into the return air plenum. Move it a couple of inches and plastic wire tied the Newmar wiring, in the area of the return air plenum, to minimize disrupting air flow. Between the taping, moving the J-box and wire tying the New HP had a much improved air flow at the front of the coach.
Wiring differences at #1 HP were a dedicated 12V dc feed and the Hydro-Hot (furnace) wiring. The two wires for the Hydro-Hot /Furnace are a broken circuit wire. The HP controller board has a relay that connects the two together to make a circuit. It makes no difference on how you connect the two wires to the HP control wiring. Set the dip switch for furnace. Then I connected the thermostat wiring from to # 1 HP, finished installing the new CCC2 thermostat, reset the thermostat and tested with only #1 new HP connected to thermostat. Thermostat picked up the new HP and furnace capability. Reset the thermstat from the "Furnace" display to "Aqua." Something nice that Dometic added for owners of Hydrohot and Aquahot. 1/3 of the way done now.

11. Took off the cover of new #2 HP and connected the RJ-11 cable that runs to #1 HP. Reset the CCC2 again and it now showed two zones. Tested all functions and all was right with the world. 2/3 of the way done now.
12. #3 (rear) HP was more difficult due to flat rack mounted solar panels mounted over the HP. Turned out the New low profile Penguin II HP was about 1-1/4" taller than the older penguins. Had to lengthen the aluminum angle supports so there was about 1/8" clearance. Another problem I did not anticipate was the older wiring for the rear HP did not have a dedicated 12V dc feed. The new CCC2 thermostat requires it. Used a spare fuse position in 12V panel above mid toilet, removed fantastic fan and supply air, and using a fish tape I ran 16 gauge high temperature insulation stranded copper wire thru supply air duct to #3 HP plenum. Taped the 12v wires with aluminum tape to hold fast and seal penetrations. Labeled the spare fuse as HP#3. There was also Hydro-Hot (furnace) wiring like HP#1 in the front.
13. Through-out the installation I cut the old male RJ-11 cable ends off, installed new ends and tested each run for opens, shorts and pin-out errors. Used a Klein brand VDV Scout Pro 2 Tester Kit I got at Home Depot for about $80.
14. The new CCC2 12-button thermostat is easier to read, can automatically switch between Cool/HP/Aqua (furnace) as needed to maintain temperature. It even has a clock function that allows night set-back. Each zone's temperature sensor reading can be read out at the thermostat and you can compare that to the set temperature for fine tuning of the set-points. Dometic has a vastly improved it's thermostat.
It was quite a bit of work, but is doable for the RV owner who is comfortable with power and low voltage wiring and has a decent set of mechanical skills. Having a whole new HVAC system was worth it for years of trouble-free usage.

Questons?
shaman52 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-29-2015, 05:23 PM   #2
Senior Member
 
hawgguy's Avatar
 
Join Date: Jun 2011
Location: College Station, Texas
Posts: 2,841


Outstanding write up. Not an easy job, technically (with the new thermostat) or logistically. Looks like you planned well and had your ducks in a row. I've done that job - more than once.

How well does the new system work?
__________________
Bob in College Station, TX
2015 Entegra Cornerstone 45K
2012 Jeep Rubicon, 1994 FXLR
hawgguy is offline   Reply With Quote
Old 04-29-2015, 07:43 PM   #3
Senior Member
 
Sky_Boss's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,973
I hope you don't have the same quality problems that I have had with the Dometic Penguin 15K HPs.

I've replaced my front AC 4 times in 15 months after the initial failure. 3 of them were due to reverser valve problems and the other was a compressor failure. The last 2 replacements also were so loud in the heat pump mode and my current unit is very loud and I am looking at forcing another replacement. Meanwhile my older, bedroom unit keeps purring on as normal.

BTW...in case you didn't know this. The earlier model units defaulted to heat pump mode in case of a reverser valve or control board problem. The new units default to AC which is much safer on pets.
__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 2015 DSDP 4320 4369, FL Chassis, 2013 CR-V 2020 Jeep Overland, Blue Ox Avail, SMI AF1.
[SIGPIC][/SIGPIC]
Sky_Boss is offline   Reply With Quote
Old 04-29-2015, 09:19 PM   #4
Senior Member
 
Spartan Chassis
Join Date: Dec 2011
Location: Anywhere, USA
Posts: 451
The new system works great. It exceeded my expectations. http://www.irv2.com/forums/images/smilies/dance.gif

Amp draw is lower. The new units are quieter than the ones they replaced. Guess Dometic has improved the Penguin II noise and vibration issues since it was first introduced. I was warned not to over tighten the four lag bolts.

One added feature I like is that the fan motor has three speeds now.

Only time will tell, but they are operating smoothly now. Fingers are crossed for now.
shaman52 is offline   Reply With Quote
Old 04-30-2015, 05:25 AM   #5
Senior Member
 
Indy Glenn's Avatar
 
Newmar Owners Club
Ford Super Duty Owner
Join Date: Oct 2014
Posts: 1,724
Blog Entries: 2
Quote:
Originally Posted by shaman52 View Post
For those of you that want to personally replace your older ducted Penguin Heat Pumps (HP) here are my thoughts on my DIY on my 2007 Newmar MADP 4528.

1. The front #1 HP was operational, but never seemed to deliver the air flow of the other units, even on high fan position. #2 HP mid coach had a frozen compressor. #3 rear was intermittent, stick reversing valve. Finding out what was wrong took me a few days on the roof and lots of internet searching on the subject. I am a retired mechanical engineer with a decent electrical background. I can see where it takes a quality RV tech to diagnose the RV systems and do the correct thing.

2. Once it was determined that 2 HPs needed replacement we elected bite the bullet to do all 3 units and update the 5-button Dometic thermostat to the 12-button CCC2 thermostat. The current Dometic low profile HPs require an adaptor board to work with the older 5-button thermostats and while replacing only the #2 only was an option, I felt it made more sense to do it all.

3. After researching three of the Dometic Penguin II high capacity Heat Pump 651816.CXX1C0 were bought from PPL out of Texas. PPL had them on sale for $999 each with decent shipping rate.

4. Called Newmar and found out that the only additional Newmar part required was a bent L shape gasket ( Newmar Part Number 52715) to separate supply air from return air. It mounted within each 14" square Dometic gasket on the underside of the Penguin.

5. I got a shrink wrapped pallet from PPL within a week, excellent. Now how to get the old ones off the roof and the new ones up there. I rented a hand crank material lift with a 600 lb capacity and a 18 foot max lift. It folded up and with two person easily went into the standard bed of a ford pickup. $150 per week. Turned out to be a very good decision on the lifting up and down. See attached picture. Attachment 92939

6. Elected to replace the #2 unit first, as it was the one totally dead with frozen compressor. I made a long temporary RJ-11 Communication cable, not the usual telephone cable, different pin-out, to connect #1 and #3 HPs together. Set the dip switch on the old #3 HP control board so it thought it was zone #2. This was to maintain heating and cooling while replaced #2 HP.

7. Turned off the power distribution panel breaker for # 2 HP, tested for power, labeled wires and took pictures on cell phone. The only somewhat difficult part was the removal of the four lag bolts that Newmar uses to mount their roof top units. Required a 1/2 inch drive 6-point socket and a long flex handle. I looked at the lag bolts when all four were out and there was one with a very worn tip threads. Went to Home Depot and purchased 9 of the shorter ones and 3 of the longer style. After lifting and wiggling I got it to lift off. Set aside the old HP and thoroughly scrapped and cleaned the area. Poured water in the two condensate drip pockets, underneath the HP, installed in the roof. For the ones not draining well, I took apart and cleaned the condensate drip pockets in the roof. The drip pockets have clear vinyl tubing that goes to a PEX pipe that drains at the rear of the coach, each side. You will need to blow that tubing out and not kink the tubing when re-installing. Wish Newmar had installed plastic tubing with nylon thread reinforcement to prevent kinking. For some unknown reason all the ones on the driver's side were clogged. I used non-leveling caulk on condensate pockets and silicone caulk on the lag bolts.

8. I got the DW up on the roof to assist me in positioning the new HP on the opening. Got her lined up and slowly drew down the four lag bolts till the foam pads at the four mounting position were one-half the original height. Installed power and did all the control wiring short of the RJ 11 communication cable. At this point set the dip switches for zone 2 and HP on the new control board and installed the cover. By the way the new Penguin covers are a vast improvement. The old flimsy ones would crack if you looked at them wrong. Thanks to Dometic for improving that part!

9. Installed the new CCC2 thermostat temporarily with tape next to the old one.

10. Removed #1 HP. Noted that the aluminum duct tape had pulled loose around the plenum and was partially blocking the supply air duct. Removed all the tape in the area, carefully cleaned and re-taped with a high quality low temperature rated aluminum duct tape. Also noted that Newmar had installed the high voltage Junction box partway into the return air plenum. Move it a couple of inches and plastic wire tied the Newmar wiring, in the area of the return air plenum, to minimize disrupting air flow. Between the taping, moving the J-box and wire tying the New HP had a much improved air flow at the front of the coach.
Wiring differences at #1 HP were a dedicated 12V dc feed and the Hydro-Hot (furnace) wiring. The two wires for the Hydro-Hot /Furnace are a broken circuit wire. The HP controller board has a relay that connects the two together to make a circuit. It makes no difference on how you connect the two wires to the HP control wiring. Set the dip switch for furnace. Then I connected the thermostat wiring from to # 1 HP, finished installing the new CCC2 thermostat, reset the thermostat and tested with only #1 new HP connected to thermostat. Thermostat picked up the new HP and furnace capability. Reset the thermstat from the "Furnace" display to "Aqua." Something nice that Dometic added for owners of Hydrohot and Aquahot. 1/3 of the way done now.

11. Took off the cover of new #2 HP and connected the RJ-11 cable that runs to #1 HP. Reset the CCC2 again and it now showed two zones. Tested all functions and all was right with the world. 2/3 of the way done now.
12. #3 (rear) HP was more difficult due to flat rack mounted solar panels mounted over the HP. Turned out the New low profile Penguin II HP was about 1-1/4" taller than the older penguins. Had to lengthen the aluminum angle supports so there was about 1/8" clearance. Another problem I did not anticipate was the older wiring for the rear HP did not have a dedicated 12V dc feed. The new CCC2 thermostat requires it. Used a spare fuse position in 12V panel above mid toilet, removed fantastic fan and supply air, and using a fish tape I ran 16 gauge high temperature insulation stranded copper wire thru supply air duct to #3 HP plenum. Taped the 12v wires with aluminum tape to hold fast and seal penetrations. Labeled the spare fuse as HP#3. There was also Hydro-Hot (furnace) wiring like HP#1 in the front.
13. Through-out the installation I cut the old male RJ-11 cable ends off, installed new ends and tested each run for opens, shorts and pin-out errors. Used a Klein brand VDV Scout Pro 2 Tester Kit I got at Home Depot for about $80.
14. The new CCC2 12-button thermostat is easier to read, can automatically switch between Cool/HP/Aqua (furnace) as needed to maintain temperature. It even has a clock function that allows night set-back. Each zone's temperature sensor reading can be read out at the thermostat and you can compare that to the set temperature for fine tuning of the set-points. Dometic has a vastly improved it's thermostat.
It was quite a bit of work, but is doable for the RV owner who is comfortable with power and low voltage wiring and has a decent set of mechanical skills. Having a whole new HVAC system was worth it for years of trouble-free usage.

Questons?
Great write up...........thanks,

g
__________________
Glenn & Angie - my Guardian Angel plus "Haddington & Sophie The Airedales".
2017 Newmar Canyon Star 40', FMCA - Retired Army Sergeant Major
Indy Glenn is offline   Reply With Quote
Old 04-30-2015, 07:48 AM   #6
Senior Member
 
FlaRider's Avatar
 
Join Date: Jan 2013
Location: Not Sure, but I think I should have turned left at Albuquerque
Posts: 823
Quote:
Originally Posted by Indy Glenn View Post
Great write up...........thanks,



g

2X. Thanks for sharing your work.
__________________
Marc & Jennifer + 8 paws (Oliver & Charlie)
2018 DSDP 4327 Spartan
2023 Jeep Wrangler JLU Rubicon
FlaRider is offline   Reply With Quote
Old 04-30-2015, 10:26 PM   #7
Senior Member
 
harleyjt's Avatar


 
Newmar Owners Club
Tiffin Owners Club
Workhorse Chassis Owner
Join Date: Jan 2015
Location: Byhalia, MS
Posts: 3,368
Quote:
Originally Posted by FlaRider View Post
2X. Thanks for sharing your work.
X3 Thanks for the excellent report.

jt
__________________
2019 Tiffin Phaeton 40IH
2005 Newmar Kountry Star Gas (Sold)
2022 JL Wrangler 4xe or 2017 Harley Ultra in tow
JT, Em & the boys, Kong & Baxter (rescued grey tabbies)
harleyjt is offline   Reply With Quote
Old 05-02-2015, 02:05 PM   #8
Senior Member
 
ARTWERKE's Avatar
 
Join Date: May 2012
Location: Deep in the Heart of Texas
Posts: 476
Good write up, I'm saving it for when I get back & try it on my new Penguin,on the way from PPL.
__________________
2000 DSDP, 3883,Freightliner,330 Cat, 07 Jeep Commander 4x4toad.
ARTWERKE is offline   Reply With Quote
Old 06-04-2015, 04:56 PM   #9
Member
 
PeterBlack's Avatar
 
Join Date: Oct 2010
Location: USA
Posts: 52
Blog Entries: 1
Hi, I have a 2007 Monaco Knight 40PDQ. I went top side today and the themal coupler line had been touching the compressor for a while and rubbed a hole in the small copper line. . I suspect I will need a new ac unit because no one will recharge them..I have the HP.and was wondering if I am going to have to replace my 5 button thermostat too...? I still have the old rear unit... there are only 20,000 miles on this unit and it was parked in a shed... thanks....Pete
PeterBlack is offline   Reply With Quote
Old 06-04-2015, 06:28 PM   #10
Senior Member
 
Sky_Boss's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,973
Quote:
Originally Posted by PeterBlack View Post
...I have the HP.and was wondering if I am going to have to replace my 5 button thermostat too...? ...
You will NOT need to change your thermostat. You will need a converter board on the new AC unit. The good news is that the newer Penguin units default to AC in case of a reverser valve failure. That means your pets (if you have any) won't get cooked by that unit.
__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 2015 DSDP 4320 4369, FL Chassis, 2013 CR-V 2020 Jeep Overland, Blue Ox Avail, SMI AF1.
[SIGPIC][/SIGPIC]
Sky_Boss is offline   Reply With Quote
Old 06-04-2015, 07:51 PM   #11
Senior Member
 
Bill-MACV21's Avatar
 
Join Date: Nov 2014
Location: Sacramento, CA
Posts: 110
Just a quick heads up. They have 2 converter boards. One is used for a single unit installation. The other is used for multi AC rigs that are daisy chained with commo wire.

Be sure you order the correct board (you can easily guess why I know).

Also you may need to toggle dip #5 on the control board in order for your stat to switch over the system to furnace mod. Not sure of your set up but it was necessary with my Oasis set up.
Bill-MACV21 is offline   Reply With Quote
Old 06-05-2015, 08:45 AM   #12
Member
 
PeterBlack's Avatar
 
Join Date: Oct 2010
Location: USA
Posts: 52
Blog Entries: 1
Hi again... thanks for the heads up...! I was just thinking now about the boards or go with the new thermostat..? what is the price difference between the two of them..? if I get a new HP up front and the rear one goes out then I will have to purchase another board for the new one and be stuck with the old 5 button duo-therm thermostat.. the new thermostats are cool and eazy to read and I have seen them for around $100. how much would a board cost me..? Pete....
PeterBlack is offline   Reply With Quote
Old 06-05-2015, 10:16 AM   #13
Senior Member
 
Bill-MACV21's Avatar
 
Join Date: Nov 2014
Location: Sacramento, CA
Posts: 110
Quote:
Originally Posted by PeterBlack View Post
Hi again... thanks for the heads up...! I was just thinking now about the boards or go with the new thermostat..? what is the price difference between the two of them..? if I get a new HP up front and the rear one goes out then I will have to purchase another board for the new one and be stuck with the old 5 button duo-therm thermostat.. the new thermostats are cool and eazy to read and I have seen them for around $100. how much would a board cost me..? Pete....
I asked Nerwmar tech support the same question. In my case I would have to run new wiring for the control ckts. Given the hassle of trying to do it through the side walls or roof I elected to just stay with the 5 button system. My guess is that it will not be worth the trouble.

"Your mileage may vary" so I suggest you call the factory (the current Monaco may be able to help) to see if it is viable/cost effective option your rig.
__________________
One very understanding & patient wife
2018 London Aire
2014 Grand Cherokee
Bill-MACV21 is offline   Reply With Quote
Old 06-05-2015, 03:42 PM   #14
Senior Member
 
Join Date: Dec 2014
Posts: 1,666
This is the second reference that I have seen stating that the communication cable has a different pin-out than a standard telephone cable. I have two new Penguin 2 HPs and CCC2 thermostat being installed next week. I didn't see that in the installation manual. Is there another document that show the correct pin-out?


Mike

2000 Holiday Rambler Endeavor
Freghtliner XC, CAT 3126B
__________________
Mike
slowmachine is offline   Reply With Quote
Reply

Tags
ace, dometic, heat, heat pump, replace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC Heat Pumps dennismhamm Alpine Coach Owner's Forum 6 01-09-2015 07:32 AM
Dometic Ice Maker Water Line Update wil01 RV Systems & Appliances 15 12-03-2014 04:07 AM
08 Dynasty roof units run but no heat or cold TAEZZAR Monaco Owner's Forum 17 10-26-2014 11:53 AM
How do you force the heat pump on?? TexasTwoStep Excel Owner's Forum 2 07-10-2013 10:34 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.