Running Air conditioner

Never done this before so just curious. When we are leaving a campground where we have had our motorhome plugged in to AC. Is it ok to start the generator with the AC still plugged in and run the air off the generator? Or do we need to shut the air off unplug from ac start the generator and then start the air back on?
__________________

__________________
Ron: 1999 Dutch Star: 38' 2 Slideouts
Spartan Chassis 300 hp Cummins ISC Allison MD3060
2002 Trailblazer: Blue ox
Ron & Kerrie is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-21-2017, 01:19 PM   #2
Senior Member
 
Podivin's Avatar
 
Winnebago Owners Club
Join Date: Dec 2015
Location: Jacksonville, Fl
Posts: 2,696
It's generally recommended that high draw appliances (AC, washer/dryer etc) be turned off any time you switch power sources. Either from shore power to generator, or from generator to shore power.

Some will say that it doesn't make any difference.

I figure it can't HURT to shut off the AC for the length of time it takes for things to switch over. And it MAY prevent an issue somewhere down the road. I always turn off the AC before switching power sources.
__________________

__________________
2013 Winnebago Sightseer 36V
Podivin is offline   Reply With Quote
Old 06-21-2017, 01:28 PM   #3
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 5,252
Most transfer switches and A/C units have a built-in delay between start-up and full load so what you are asking to do shouldn't be an issue.....but to be safe, you can shut off the A/C before starting the genset. Biggest issue in this area is allowing the auto transfer switch to transfer power with large amp draw/load in place/on line.....
__________________
Old Scout
2003 40' MDTS
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 06-21-2017, 01:39 PM   #4
Senior Member
 
wildtoad's Avatar
 
Join Date: Jul 2010
Posts: 4,334
Start the gen let it get up to speed and run it for a few minutes. Then go unplug. Drive off.
__________________
Tom Wilds
Blythewood SC
2016 Newmar Bay Star Sport 3004
2015 Jeep Wrangler 2DR 4WD Sahara, Automatic, Hard Top
wildtoad is offline   Reply With Quote
Old 06-21-2017, 01:43 PM   #5
Senior Member
 
powercat_ras's Avatar
 
Winnebago Owners Club
Solo Rvers Club
Join Date: May 2015
Posts: 1,429
Most transfer switches have a 20 second delay before switching the power contactor from shore power connected mode to generator connected mode. This allows the generator to start and run with no load a few seconds before being hit with a load.

The motor in your AC compressor starts best with coolant pressure equalized on both sides of the compressor. This takes 1-2 minutes after compressor stops running.

Best to have the AC units off 2 minutes when switching from one power source to another.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2016 Honda HR-V
powercat_ras is online now   Reply With Quote
Old 06-21-2017, 03:34 PM   #6
Senior Member
 
fegans02's Avatar
 
Join Date: May 2015
Location: Richmond, VA
Posts: 163
Our tech said always turn off before switching power sources
__________________
Adrienne Fegans
2015 Newmar London Aire
Richmond, VA
fegans02 is offline   Reply With Quote
Old 06-21-2017, 04:28 PM   #7
Senior Member
 
GaryKD's Avatar
 
Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 13,552
Hi Ron & Kerrie,
Technically it is okay to leave the A/C on, start the generator and then go unplug. No muss and no fuss. The components are engineered to handle the switch. But I would not do this. If done, one is putting stress on the generator, the HVAC units and the transfer switch. It is a minor inconvenience to shut down the HVAC, start the generator, go disconnect from shore power and then turn on the HVAC, it would be best to do it this way. This minimizes stress on the components.
__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
GaryKD is offline   Reply With Quote
Old 06-21-2017, 07:48 PM   #8
Senior Member
 
hawgguy's Avatar
 
Join Date: Jun 2011
Location: College Station, Texas
Posts: 2,841
Quote:
Originally Posted by wildtoad View Post
Start the gen let it get up to speed and run it for a few minutes. Then go unplug. Drive off.
The transfer with will prioritize the generator in most setups. As soon as the genny is making power, the transfer switch will use it regardless of whether you are plugged in or not.

I think best practice would be as described above. Minimize the load by shutting off high draw devices, then start the genie, then restart the devices. A pain, I know. I am told that this reduces arcing and pitting of contacts on the transfer switch.
__________________
Bob in College Station, TX
2015 Entegra Cornerstone 45K
2012 Jeep Rubicon, 1994 FXLR
hawgguy is offline   Reply With Quote
Old 06-21-2017, 07:50 PM   #9
Senior Member
 
stang37's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Feb 2016
Location: Mississippi
Posts: 456
I agree with turning off AC before starting the generator. If I remember correctly the generator is the preferred source of power by the transfer switch even when shore power is available. By that as soon as the generator is started and up to speed the transfer switch will auto switch. I'm not sure if the transfer is smooth/fast enough that the AC wouldn't notice the source change and cycle.
__________________
2016 Newmar Ventana 4002
2020 Jeep Gladiator
stang37 is offline   Reply With Quote
Old 06-21-2017, 07:59 PM   #10
Community Moderator
 
Spk64's Avatar


 
Newmar Owners Club
Join Date: Apr 2014
Location: Southern Indiana
Posts: 9,707
I agree with shutting off the heavy loads anytime you are transferring power. I do the same when shutting power off at the pole and unplugging. Or switching to generator. The transfer switches can handle the load but repeatedly doing it will mean the transfer switch can fail sooner.
__________________
Steve
2002 Newmar Mountain Aire 4095
Spk64 is offline   Reply With Quote
Old 06-21-2017, 08:21 PM   #11
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 14,581
No heavy loads when transfer switch is switched, to minimize the switch contacts arcing. While it will not cause a instant failure, the cumulative arcing over time can cause failure.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 06-22-2017, 03:40 AM   #12
Senior Member
 
rewillia's Avatar
 
Newmar Owners Club
Spartan Chassis
Join Date: May 2016
Location: Lake Charles (domicile)
Posts: 1,064
we've experienced the GenSet main breaker tripping when we have the ACs on and crank up the generator (too much load) and have since been told (by Newmar) that the correct procedure is to turn the ACs off before switching to generator power then, turn them back on. Since doing it this way we've not have the generator's main breaker (on top of the genset) trip.
__________________
Finding The Roads That Await Us
Rick & Lydia Williams
2018 Newmar Essex 4553
NKK Member 21619 / FMCA Member 465836
rewillia is offline   Reply With Quote
Old 06-22-2017, 06:02 AM   #13
Senior Member
 
Ron & Kerrie's Avatar
 
Newmar Owners Club
Join Date: Oct 2013
Location: iowa
Posts: 449
Thanks for all the help and advice Everyone appreciate it
__________________
Ron: 1999 Dutch Star: 38' 2 Slideouts
Spartan Chassis 300 hp Cummins ISC Allison MD3060
2002 Trailblazer: Blue ox
Ron & Kerrie is offline   Reply With Quote
Old 06-23-2017, 03:29 PM   #14
Senior Member
 
Join Date: May 2017
Posts: 178
I always turn off the A/C before switching power sources. I always wait about 5 minutes before turning the A/C back on again because it takes a LOT of amperage to start an A/C compressor and with my motorhome, both A/C units come on at the same time. Also, it's good to let the jenny warm up a bit before putting a heavy load on it. The starting amperage of an A/C is about 300 percent of the running amps. Let's say your unit's running amperage is 10 amps, 120vac. So, starting amperage would be 30 amps which would taper down to 10 amps once the unit is running. But that's a strain on your power source. If for some reason the capacitor has not finished recycling when you turn it back on, then the starting amperage can go out of sight... like 80-90 amps. That's why the lights in your house dim way down if you try to turn on the A/C after a brief shut down... and the A/C won't restart in that situation. Newer units have a fail-safe for this situation... but... they can fail too!
__________________

__________________
Elbridge Price, 1998 Dutch Star Diesel Pusher
Cummins 6.8.3 mechanical injectors, Spartan Chassis
No Toad Yet
tommar is offline   Reply With Quote
Reply

Tags
air conditioner



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air conditioner water running off wrong side whitebear47 Entegra Owner's Forum 2 12-11-2016 01:05 PM
Air conditioner fan will not stop running RV735 Winnebago Industries Owner's Forum 18 01-11-2015 11:34 PM
Running Air Conditioner on Inverter? bokobird Class A Motorhome Discussions 15 08-02-2014 07:47 PM
Air Conditioner Not Running on Generator Power memphisflyer Class A Motorhome Discussions 8 05-11-2012 06:30 AM
Running roof air conditioner on generator millardbr Winnebago Industries Owner's Forum 5 07-29-2008 06:19 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:04 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
×