What is the best (easiest?) way to determine that the auto gen start function actually works?
__________________
Jerry & Shirley Friedman
2014 Chevy Silverado 3500HD
2015 Mobile Suites 38RSSB3
gator67 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-12-2006, 04:46 PM   #2
Senior Member
 
gator67's Avatar
 
Join Date: Feb 2005
Location: everywhere
Posts: 527
What is the best (easiest?) way to determine that the auto gen start function actually works?
__________________
Jerry & Shirley Friedman
2014 Chevy Silverado 3500HD
2015 Mobile Suites 38RSSB3
gator67 is offline   Reply With Quote
Old 04-12-2006, 06:06 PM   #3
Senior Member
 
Alpine Owners Club
Join Date: Apr 2006
Posts: 133
This is our first time on the site, so we're kinda new, too! We've found there are several functions for the AGS

1. If you schedule your generator for an exercise period, that's one way to use AGS.
2. Another, is ensuring the AGS works when your house batteries are low (we found this out when we used the microwave w/o shore power or the generator running). Once the batteries are low, the AGS should kick in (assuming the inverter is activated and quiet time is either not set or it isn't quiet time).
3. Another AGS function, would be under "load"...for example, no shore or generator power and you've set the thermostat for air conditioning to come on at a certain temp...when that temp is exceeded, the ags should turn the a/c on. Note: ours isn't working under load and we're heading to Coach Care to see if the air conditioner is wired correctly OR to Xantrex if the wiring is OK.

Also, remember AGS has to be set to "on" via the thermostat also AND all of your Xantrex setting must be correct. We've spent hours on the phone w/Xantrex and had a dealer work w/these settings also. It ain't easy!!

Good luck.


3.
3. Setting
__________________
2005 40' Limited FDTS

Brandywine
Jim & Ingrid McIntosh is offline   Reply With Quote
Old 04-13-2006, 07:48 AM   #4
Senior Member
 
Join Date: Feb 2005
Location: Livermore, CA
Posts: 201
I will ask an additional question in the same vain. Is the AGS supposed to happen if the batteries go low during quiet hours (if set) after the end of the quiet hours? It seems as though mine does not come on after the expiration of quiet hours, I must manually start the gen.
__________________
2006 Alpine Apex 40 FDQS
2002 Jeep Grand Cherokee toad
2000 Vette for the track
WeBrzn2 is offline   Reply With Quote
Old 04-13-2006, 08:24 AM   #5
Senior Member
 
Wayne R's Avatar
 
Join Date: May 2003
Location: Winter Haven Brownsville, TX
Posts: 1,143
Another convenient feature of the AGS system is that it will start the gen when the thermostat calls for air conditioning. This is especially nice if you have a pet and leave for the afternoon on a hot day. The AGS mode on the thermostat only activates the thermostat to send a start stop signal to the AGS system. At least that is how my 05 is wired.

Nothing overrides quite time, make sure your system clock is on the right time (time zone)
__________________
Wayne & Kathy
05 Alpine 40FDQS #75330 Towing 24' car hauler, 2012 Spyder, 2003 Harley FatBoy
Wayne R is offline   Reply With Quote
Old 04-13-2006, 12:32 PM   #6
Senior Member
 
Audrey & John's Avatar
 
Join Date: Oct 2004
Location: wandering North America
Posts: 484
The Auto Gen Start seems to really struggle sometimes when it tries to bring both air conditioners on. This doesn't always happen - only sometimes.

It seems to keep trying, rev a bit, the air conditioners don't quite get going, and then the gen start goes on delay again.

The last time I turned one of the air conditioners up so that only one needed to come on, and the generator was able to get that going.

Is there something wrong with our AGS?

I would think the system would be smart enough to stage the two air conditioners so that you wouldn't get a simultaneous surge.

Audrey
__________________
36ft 2006 Alpine Coach FDDS
Audrey & John is offline   Reply With Quote
Old 04-13-2006, 02:20 PM   #7
Senior Member
 
Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 5,385
Aud- If your rig is equiped w/heat strips & you are calling for heat, the heat strips are 1530 watts & the heat pump about 1920 (compressor + fan), for a combined 3.45 kw per unit. That's ~7kw if you call for both. That call should initiate a stagger logic, as you suggest, but I bet it doesn't and that the combined load is the trouble. If you don't have (or are not calling for) heat strips, then there is no reason for the gen to struggle if it has been allowed to cycle up to speed and the problem is elsewhere.
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
EngineerMike is offline   Reply With Quote
Old 04-13-2006, 02:44 PM   #8
Senior Member
 
Wayne R's Avatar
 
Join Date: May 2003
Location: Winter Haven Brownsville, TX
Posts: 1,143
Audrey and John have you tried a longer warm up delay?
__________________
Wayne & Kathy
05 Alpine 40FDQS #75330 Towing 24' car hauler, 2012 Spyder, 2003 Harley FatBoy
Wayne R is offline   Reply With Quote
Old 04-14-2006, 05:23 AM   #9
Senior Member
 
Audrey & John's Avatar
 
Join Date: Oct 2004
Location: wandering North America
Posts: 484
EngineerMike - no, we weren't using the heat strips, just the A/C.

The generator comes on and runs for a while before the A/Cs attempt to come on. Any ideas on where the problem might be if it's not the generator?

Wayne - hmmmmm..... didn't know we could configure a longer warm up delay? What difference might that make? Seems like the delay is pretty long already - about a minute or so?

The weird thing is that this doesn't always happen. Maybe it happens when the weather is hot enough and the A/Cs want to start with high fan.

When we stop at a rest area, we usually run the generator by using the AGS to start it from the comfort control panel. This is when we notice the occasional problem.

Audrey
__________________
36ft 2006 Alpine Coach FDDS
Audrey & John is offline   Reply With Quote
Old 04-14-2006, 11:51 AM   #10
Senior Member
 
Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 5,385
Aud- Just the AC's would be ~3.85kw & shouldn't be any sweat for a 7.5kw gen.
But, the longer warmup might be an issue. Diesel ignites from compression, not spark like in the toad, so operating temp is more related to ability to produce full HP from the combustion cycle. So a longer idle-up would raise temp of the cylinders about 60-100 degrees (depending on ambient), improving the compression ignition. Coulda sworn mine goes longer than a minute or so (like 3-5?) B4 allowing a load, but that's from memory which is almost as good as when I assume.
Not sure where (or if) to program the delay.
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
EngineerMike is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Have you ever needed auto gen start? footdoc RV'ing with Pets 9 08-12-2007 05:31 AM
Xantrex Auto Gen Start smlranger Winnebago Industries Owner's Forum 12 05-10-2007 09:22 AM
Auto Gen Start At Its Best! Lug_Nut Newmar Owner's Forum 7 03-03-2007 07:44 AM
Auto Gen Start for A/C JavaJelly Newmar Owner's Forum 10 12-21-2006 03:07 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:47 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.