Old 02-05-2021, 12:12 PM   #15
Senior Member
 
paul65k's Avatar


 
Alpine Owners Club
Join Date: Nov 2015
Location: Lake Havasu City, AZ
Posts: 1,962
Quote:
Originally Posted by Freqz View Post
It my case, it would be a 240V inverter so you need the auto transformer to provide split phase 120V. (I donít necessarily need split phase but I do need a neutral)

Iím building this around a 8k Quattro to support a mini split and induction cooktopó 6kVA seems a little light for my use. Your way gets more charging current and cost a bit less. Several ways to skin this particular cat!
Thanks!

I have a MS planned as well....as a matter of fact I already have the 240V subpanel installed and circuit run to the outdoor unit proposed location..... just trying to figure out the interior distribution plan, front and rear!

I can already run both rooftop units off the grid but calculating that the mini-split will use 40 - 70% less amps, depending on how we end up!
__________________
Paul & Jean
2001 Alpine 36FDDS (74291) - 1600W Solar, 10,752 Wh (420Ah @24V) LiFePO4
2014 Jeep Wrangler Unlimited Rubicon
2006 Alpenlite 32RL - Sold
paul65k is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-05-2021, 12:46 PM   #16
Senior Member
 
Freqz's Avatar
 
Join Date: Aug 2017
Posts: 1,007
Quote:
Originally Posted by paul65k View Post
Thanks!

I have a MS planned as well....as a matter of fact I already have the 240V subpanel installed and circuit run to the outdoor unit proposed location..... just trying to figure out the interior distribution plan, front and rear!

I can already run both rooftop units off the grid but calculating that the mini-split will use 40 - 70% less amps, depending on how we end up!

Yeah, Victron shows ~2200W for my 15kBTU which is about what a 24kBTU mini split should take. Sheesh.

Iím still in the spitballing phase...this was much, much less complicated (and much cheaper!) for my 30A trailer . But itís also half the fun, I guess!
__________________
2018 ORV Timber Ridge 24rks
2017 F350 6.7 CC DRW
Freqz is offline   Reply With Quote
Old 02-10-2021, 12:11 PM   #17
Senior Member
 
v8dave's Avatar
 
Join Date: Aug 2012
Location: Northern California
Posts: 111
Get a manual/diagram for your installed generator and investigate the capabilities of the generator itself. I'll bet it already has split 240 Volt dual circuit capability but has been configured to only supply a single circuit at 120 Volts.


If it seems capable, check with a full line service center (i.e. Freight Liner service center or equivalent that has electricians on staff) to see if they know how to do this.


Best Regards,
__________________
Dave
Northern California
2000 Alpine Coach 36' FDS, Cummins ISC 330
v8dave is offline   Reply With Quote
Old 02-10-2021, 04:47 PM   #18
Senior Member
 
paul65k's Avatar


 
Alpine Owners Club
Join Date: Nov 2015
Location: Lake Havasu City, AZ
Posts: 1,962
Quote:
Originally Posted by v8dave View Post
Get a manual/diagram for your installed generator and investigate the capabilities of the generator itself. I'll bet it already has split 240 Volt dual circuit capability but has been configured to only supply a single circuit at 120 Volts.


If it seems capable, check with a full line service center (i.e. Freight Liner service center or equivalent that has electricians on staff) to see if they know how to do this.


Best Regards,
So the QD 7500 is only capable of single-phase as the windings apparently can not support split-phase output. The windings are not capable of developing split-phase hence the need for the autotransformer

In addition to this spec sheet, it was confirmed to me by Onan.
Attached Thumbnails
Click image for larger version

Name:	Generator Specs.jpg
Views:	19
Size:	171.1 KB
ID:	317723  
__________________
Paul & Jean
2001 Alpine 36FDDS (74291) - 1600W Solar, 10,752 Wh (420Ah @24V) LiFePO4
2014 Jeep Wrangler Unlimited Rubicon
2006 Alpenlite 32RL - Sold
paul65k is offline   Reply With Quote
Old 05-24-2021, 10:58 PM   #19
Senior Member
 
paul65k's Avatar


 
Alpine Owners Club
Join Date: Nov 2015
Location: Lake Havasu City, AZ
Posts: 1,962
Thought I would update this thread...........

I have the Autotransformer in my possession and plan to do the install next week. It looks pretty straightforward; I will intercept the input from the generator prior to reaching the transfer switch. The way it will be wired, the (2)v120V lines from the generator (sams phase) will feed into the Autotransformer on L1 which will then provide (2) lines out (L1, L2) which will now be 180* out of phase just like the 50A shore power input.....only difference will be that each line will only have 3600W (30A) each vs. the 6000W (50A) with a shore power connection.

Why is this important

Because right now when I run the generator L1 (1/2 the panel) is fed via pass-through and L2 (other 1/2) is fed by the 2nd inverter from the batteries while the 1st inverter is charging the batteries.......this of course is not the case with a 50A shore power connection because both L1 and L2 are 180* out of phase and each line passes straight through as well as BOTH are charging the batteries with a total output of 280A (@12V) which gets the batteries charged twice as fast

I will have to do a little power management if I need to run the generator AND run both AC units at the same time which can cause the breaker at the genny to trip, but in our system, we can set the available amps to 30 or any number actually, and the Inverter/chargers will manage the loads based on that without putting excess draw on the genny

Is that as clear as mud
__________________
Paul & Jean
2001 Alpine 36FDDS (74291) - 1600W Solar, 10,752 Wh (420Ah @24V) LiFePO4
2014 Jeep Wrangler Unlimited Rubicon
2006 Alpenlite 32RL - Sold
paul65k is offline   Reply With Quote
Reply

Tags
charging, generator, upgrade



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is an "upgrade" really an "upgrade"? Kilo66 iRV2.com General Discussion 10 09-27-2017 09:34 AM
TV Upgrade and Battery Upgrade - Itasca Sunrise FrankO Winnebago Industries Owner's Forum 15 12-28-2016 03:37 PM
ccc upgrade/axle upgrade? zacktown Monaco Owner's Forum 18 08-07-2012 06:57 AM
battery isolator upgrade / alternator upgrade boomvan Vintage RV's 10 03-15-2012 01:50 AM


All times are GMT -6. The time now is 02:13 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.