I have a question for those of you with a Surge Guard Power Monitor.

When we are on shore power, there are two rows of numbers showing the amps being used. This, as it was explained to me, is because the incoming power goes through two legs and each leg has its own draw. The sum of the two legs is the total amperage being used.

When I run the generator, only the top number registers any amperage... the bottom number is always zero. Is this right? Or, should the draw from the generator appear the same as the draw from the shore power and register on both legs?
__________________
Jerry & Shirley Friedman
2014 Chevy Silverado 3500HD
2015 Mobile Suites 38RSSB3
gator67 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-28-2006, 06:15 PM   #2
Senior Member
 
gator67's Avatar
 
Join Date: Feb 2005
Location: everywhere
Posts: 527
I have a question for those of you with a Surge Guard Power Monitor.

When we are on shore power, there are two rows of numbers showing the amps being used. This, as it was explained to me, is because the incoming power goes through two legs and each leg has its own draw. The sum of the two legs is the total amperage being used.

When I run the generator, only the top number registers any amperage... the bottom number is always zero. Is this right? Or, should the draw from the generator appear the same as the draw from the shore power and register on both legs?
__________________
Jerry & Shirley Friedman
2014 Chevy Silverado 3500HD
2015 Mobile Suites 38RSSB3
gator67 is offline   Reply With Quote
Old 01-29-2006, 01:34 AM   #3
Moderator Emeritus
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
If you have an Onan Quiet Diesel 7.5 or 8 kw generator these do not put out 240 volts. These are actually producing two 120 volt legs of power through a large inverter. If you were to try to measure between L1 and L2 you would read zero volts. This is because they are in the same phase of a sine wave. Your shore power coming into the coach is however 120/240 volt and so your EMS will show exactly what you are seing and it is correct. On generator power the amperage at the top of the EMS is the total being used.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator Question Rnicfingrp Newmar Owner's Forum 4 05-29-2008 11:29 AM
generator question Bob N Deb MH-General Discussions & Problems 4 04-16-2008 01:23 PM
AC Generator Question Jackm Winnebago Industries Owner's Forum 7 02-17-2008 09:54 PM
Generator Question Jack Barbic MH-General Discussions & Problems 12 03-21-2006 12:10 PM