GFI Shore Receptacle Trips

We have a 2005 Alpine Coach 36 FDDS. Whenever I plug our power chord into a 15 amp GFI shore receptacle, the receptacle trips. This happens every time, right after the 2 minute 15 second waiting period for the surge protector to kick in.

We have a 50 amp system with a permanently installed Surge Guard model 34560 made by TRC (Technology Research Corp), which is now Southwire. I have tried their website and calling their tech support and can't get a return call from them. I also tried Progressive Industries tech support (that makes a competitive surge protector), and can't get a return call from them either.

I tried turning absolutely everything in the coach off before plugging in, including shutting down all of the breakers, and it still trips.

So what could it be? Is it worth trying to find and fix? I asked a repair shop, and they didn't want to do it. They said that GFI doesn't like RVs.
__________________
2005 Alpine Coach 36 FDDS
with Cummins ISL 8.9L 400hp
3x5 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-14-2022, 07:11 PM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 27,791
My first 3 RVs wouldn't trip a GFCI , my last 5er and current coach will .

There are numerous possible causes ; first could be the surge guard cycle , others include water heater and fridge electric elements .

But if the GFCI trips with the main 50 amp breakers off , and you can't by pass the surge guard .

Other members have had success tracking the issue down , my last 5er was brand new and tripped GFCI from day one after going through the 120 volt system and replacing the converter , with no resolution in sight I learned to live with the situation .

Any way to run your extension cord to a non GFCI circuit outlet .
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 09-14-2022, 08:00 PM   #3
Senior Member
 
Join Date: Sep 2015
Location: Red Bluff, Ca
Posts: 364
Any way to run your extension cord to a non GFCI circuit outlet?

Or just replace the GFCI with a standard non-GFCI receptacle.
__________________
Gene
1998 36FDS Alpine
Red Bluff, Ca.
gmcgene is offline   Reply With Quote
Old 09-14-2022, 08:08 PM   #4
Senior Member
 
lazybyrd's Avatar
 
Alpine Owners Club
Join Date: Feb 2018
Location: Cut n Shoot, TX
Posts: 199
Had similar experiences at a storage facility. They replaced the gfci with a non gfci and that corrected the problem. I cannot explain the reason it trips but have heard of it several times.
__________________
Dawn & Steve Byrd
2003 Alpine
Cut n Shoot, TX
lazybyrd is offline   Reply With Quote
Old 09-14-2022, 08:19 PM   #5
Senior Member
 
Join Date: Jul 2014
Posts: 31,765
Instead of switching off the breaker, you could try unplugging the fridge. That takes both wires out of the circuit.

To really seek out the issue, removing the neutral wire for each corresponding circuit breaker will help find the fault.

Water heaters and inverter/chargers would be first on the list.
twinboat is online now   Reply With Quote
Old 09-16-2022, 02:04 PM   #6
3x5
Senior Member
 
Join Date: Aug 2017
Posts: 240
I have a main panel and a subpanel. I turned off the main breaker, and all of the other breakers including in the subpanel for good measure. Then I planned to turn on one circuit at a time to narrow down finding the problem. But it still tripped the gfci with all of the breakers off.

Shouldn't turning off all the breakers have isolated everything downline from tripping the gfci? Am I missing something here? Or is the ground fault be between the main panel and the Surge Guard?

Like you suggest, I may have to just live with this.

Thanks for your advice.
__________________
2005 Alpine Coach 36 FDDS
with Cummins ISL 8.9L 400hp
3x5 is offline   Reply With Quote
Old 09-16-2022, 02:28 PM   #7
3x5
Senior Member
 
Join Date: Aug 2017
Posts: 240
Quote:
Originally Posted by twinboat View Post
Instead of switching off the breaker, you could try unplugging the fridge. That takes both wires out of the circuit.

To really seek out the issue, removing the neutral wire for each corresponding circuit breaker will help find the fault.

Water heaters and inverter/chargers would be first on the list.

Twinboat. I just read your post more carefully. So switching off the breaker doesn't isolate the ground fault. The gfi is looking at the neutral, and it is not shut off by the breaker?
__________________
2005 Alpine Coach 36 FDDS
with Cummins ISL 8.9L 400hp
3x5 is offline   Reply With Quote
Old 09-16-2022, 02:59 PM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 31,765
Quote:
Originally Posted by 3x5 View Post
Twinboat. I just read your post more carefully. So switching off the breaker doesn't isolate the ground fault. The gfi is looking at the neutral, and it is not shut off by the breaker?
The GFCI monitors both hot and neutral for equal current flow.

If current is leaking from neutral to ground, that current isn't going back thru the device and the GFCI will trip.

Water heaters have a resistance wire inside a grounded core. If the wire gets to hot ( powered up with no water surrounding it ), it can burn thru the insulation and touch the core. That causes a ground fault.
I believe fridge heaters are built the same way.
twinboat is online now   Reply With Quote
Old 09-16-2022, 10:41 PM   #9
3x5
Senior Member
 
Join Date: Aug 2017
Posts: 240
Twinboat:

You did it! Wow! You are the Master! You are a Wizard!!! Thank you, thank you, thank you!

BOTTOM LINE: I pulled the white neutral wire for the electric half of the water heater off the neutral bar and now the gfci receptacle for shore power does not trip. Just a screw driver and couple of minutes to test, and all solved. It was easier than running an extension cord to another outlet.

How did you know my electric water heater didn't work? I just had the breaker off. I didn't realize that I had to pull the neutral too.

Thanks so much again.
__________________
2005 Alpine Coach 36 FDDS
with Cummins ISL 8.9L 400hp
3x5 is offline   Reply With Quote
Old 09-16-2022, 10:50 PM   #10
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,352
Quote:
Originally Posted by 3x5 View Post
Twinboat:

You did it! Wow! You are the Master! You are a Wizard!!! Thank you, thank you, thank you!

BOTTOM LINE: I pulled the white neutral wire for the electric half of the water heater off the neutral bar and now the gfci receptacle for shore power does not trip. Just a screw driver and couple of minutes to test, and all solved. It was easier than running an extension cord to another outlet.

How did you know my electric water heater didn't work? I just had the breaker off. I didn't realize that I had to pull the neutral too.

Thanks so much again.
So, you are going to remove that white wire everytime you plug in at home?
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Old 09-17-2022, 03:08 AM   #11
3x5
Senior Member
 
Join Date: Aug 2017
Posts: 240
No. I will leave it taped up, and disconnected from the neutral bar. I don't need it to run the water heater on propane. I will replace the electric heating element in a few weeks, and that should take care of the ground fault. Then I will try to put it back on the neutral bar.
__________________
2005 Alpine Coach 36 FDDS
with Cummins ISL 8.9L 400hp
3x5 is offline   Reply With Quote
Old 09-17-2022, 09:26 AM   #12
Member
 
matcoman's Avatar
 
Join Date: Nov 2013
Location: Livingston, Texas
Posts: 63
After 15+ years in a storage stall without a GFCI outlet and zero problems, we recently moved in a new storage facility that requires the GFCI, we've found that the residential refrigerator will trip the outlet. We've since turned the fridge breaker off to solve our issue.


See this thread for our experience: https://www.irv2.com/forums/f53/stor...ra-592217.html
__________________
Richard (& Nancy, too!)
Livingston, Texas
2009 43' Allegro Bus QRP
matcoman is offline   Reply With Quote
Old 09-19-2022, 02:01 PM   #13
Member
 
Join Date: Aug 2022
Posts: 43
I apologise for the hijack but I just brought home a 2005 36 MDDS and it does the same thing, only different. It plugs in fine, inverter charger running some overhead 110 lights, tv. Plug a vacuum in and switch it on and the gfci trips. Not the box breaker just the gfci.

Any ideas? Water heater too?
dynoguy is online now   Reply With Quote
Old 09-19-2022, 02:16 PM   #14
Senior Member
 
Join Date: Jul 2014
Posts: 31,765
Quote:
Originally Posted by dynoguy View Post
I apologise for the hijack but I just brought home a 2005 36 MDDS and it does the same thing, only different. It plugs in fine, inverter charger running some overhead 110 lights, tv. Plug a vacuum in and switch it on and the gfci trips. Not the box breaker just the gfci.

Any ideas? Water heater too?
No, its not the water heater, its the vacuum !

GFCIs sense electrical leakage to your body, which can kill you but won't trip a circuit breaker.
twinboat is online now   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
House GFI trips when plugging in shore power TravelersMA RV Systems & Appliances 13 12-01-2021 10:24 PM
GFI receptacle kbenfield Alpine Coach Owner's Forum 20 08-12-2020 07:05 PM
GFI receptacle reset mystery 6Cats iRV2.com General Discussion 5 06-22-2020 08:26 AM
Plugging into shore power trips shore power breaker BFF Travel Supreme Owner's Forum 8 07-28-2017 11:53 PM
GFI Receptacle - Ice Maker liralen Monaco Owner's Forum 7 08-12-2010 04:50 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:39 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2022, vBulletin Solutions, Inc.