Old 05-31-2017, 06:04 AM   #29
Senior Member
 
Join Date: Oct 2014
Posts: 7,881
Quote:
Originally Posted by theoldwizard View Post
They do sell certain types of 4 wire cable with a smaller neutral, but that can only be used after some careful load analysis. The basic assumption is that there are few 120V loads and 240V load usually (always ?) pull equally.
No, the reason one can "get by" with a smaller-gauge neutral is that the neutral on a 50 amp circuit only carries the DIFFERENCE in load between L1 and L2.

And, would like for someone to post a link to a current electrical code that calls for a ground except at the main CG breaker box.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-31-2017, 06:10 AM   #30
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
In the typical American system there is no need for a neutral connection for 240 VAC. The power is drawn from each end of the power pole transformer with no neutral needed but the safety ground is in place. There may be a lug for neutral or their may be a timer or similar small load on one leg.

I've seen installers go nuts over that when confronted with European origin spa heaters. They use ~240 as their basic distribution so there is no neutral connection point. That leaves a spare wire that causes some interesting conversations. ;-)
nothermark is offline   Reply With Quote
Old 05-31-2017, 06:25 AM   #31
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Quote:
Originally Posted by wolfe10 View Post
...And, would like for someone to post a link to a current electrical code that calls for a ground except at the main CG breaker box.
You are kidding...right?
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 05-31-2017, 07:44 AM   #32
Senior Member
 
Join Date: May 2017
Posts: 1,299
Quote:
Originally Posted by wolfe10 View Post
No, the reason one can "get by" with a smaller-gauge neutral is that the neutral on a 50 amp circuit only carries the DIFFERENCE in load between L1 and L2.
That was what I was trying to say ! Thanks for clearing it up !!
theoldwizard is offline   Reply With Quote
Old 05-31-2017, 07:51 AM   #33
Senior Member
 
Join Date: May 2017
Posts: 1,299
Quote:
Originally Posted by nothermark View Post
In the typical American system there is no need for a neutral connection for 240 VAC.
There may be "no need" for true 240V loads, but the NEC has been changed to say that pretty much ALL 120V AND 240V residential outlet must have both neutral and a ground wire in the switch box and in the outlet/fixture.

You can not buy a a 3 prong oven/dryer plug/outlet any more.
theoldwizard is offline   Reply With Quote
Old 05-31-2017, 08:04 AM   #34
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
Quote:
Originally Posted by theoldwizard View Post
There may be "no need" for true 240V loads, but the NEC has been changed to say that pretty much ALL 120V AND 240V residential outlet must have both neutral and a ground wire in the switch box and in the outlet/fixture.

You can not buy a a 3 prong oven/dryer plug/outlet any more.
I'm not quibbling over code. I am talking about what is needed.

Don't need to buy a 3 prong as I have a box full. Does leave me wondering what other folks with old equipment do. ;-)
nothermark is offline   Reply With Quote
Old 05-31-2017, 08:08 AM   #35
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
There still is an exception in the code that allows the use of existing 3 prong outlets. You buy a 3 prong pigtail and continue to feed even 4 wire appliances with the 3 wire cord. You can still get 3 wire pigtails and there is a jumper in most dryers for this method.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 05-31-2017, 07:11 PM   #36
Senior Member
 
ralph0808's Avatar
 
Join Date: Mar 2010
Posts: 279
Ok guys I still the problem and I think it is inside the RV somewhere!! I have the grounding rod installed and it made no difference. I then returned to the water heater which was part of the problem. The dealership Service Manager told me 1/06/15 when I purchased it that he personally changed the electric element, and it was a 2000 watt on a 15 amp circuit. I put a 1500 watt element in today because of high current loading on leg L1. But the voltage swing continues with one going high 127-129 volts while the other maybe 111-115 or even down to 109. So I have crawled around inside the beast and checked every screw for every wire in the hard wired TRC 40250-RVC surge guard. I have checked the connections for the inverter, the main panel, sub panel, checked the power cord and cleaned the pins on the plug. The surge guard was replaced in 4/15 at a different dealership under extended warranties. So I don't know what to check next. I have the PT50 plugged in at pedestal saying E-0 and giving the same voltages that I have with digital meters and also two DVM that are usually within a volt or two difference. So what's next??
__________________
2018 Ram & Beacon 41LKB
ralph0808 is offline   Reply With Quote
Old 05-31-2017, 08:03 PM   #37
Senior Member
 
Join Date: Aug 2010
Posts: 2,772
Are you saying you have tested the plug with a volt meter and it passes this test


14-50R

The voltage between Y and X should be 240-Volt, X and W 120-Volt, Y and W 120-Volt, X and G 120-volt, Y and G 120-volt, W and G 0-Volt
__________________
Terry & Alice
2006 Bounder 38L DP
2012 GMC Terrain
firedoc is offline   Reply With Quote
Old 05-31-2017, 08:04 PM   #38
Senior Member
 
Join Date: Aug 2010
Posts: 2,772
Oops picture didn't load
__________________
Terry & Alice
2006 Bounder 38L DP
2012 GMC Terrain
firedoc is offline   Reply With Quote
Old 05-31-2017, 08:06 PM   #39
Senior Member
 
Join Date: Aug 2010
Posts: 2,772
Here is a better diagram
Click image for larger version

Name:	IMG_2465.JPG
Views:	69
Size:	84.5 KB
ID:	163684
__________________
Terry & Alice
2006 Bounder 38L DP
2012 GMC Terrain
firedoc is offline   Reply With Quote
Old 05-31-2017, 08:40 PM   #40
Senior Member
 
ralph0808's Avatar
 
Join Date: Mar 2010
Posts: 279
Well actually I am measuring voltage and current at connection points of L1 & L2 at the main panel with some digital meters capable of reading voltage on top display and current with a coil around the wire. I have also verified the values and compared them with a clamp on current meter and a digital DVM. So for instance just had L1 with 124 volts & .2 amps with L2 with 121 volts & 7.7 amps. The wife put a hair dryer on high to L1 116 volts & 13.5 amps L2 125 volts 7.2 amps. This is only a slight change in comparison to bigger loading or AC turning on while cooking.
__________________
2018 Ram & Beacon 41LKB
ralph0808 is offline   Reply With Quote
Old 05-31-2017, 08:41 PM   #41
Senior Member
 
ralph0808's Avatar
 
Join Date: Mar 2010
Posts: 279
But yes at the pedestal that is now pretty close to what I had measured there yesterday.
__________________
2018 Ram & Beacon 41LKB
ralph0808 is offline   Reply With Quote
Old 05-31-2017, 08:44 PM   #42
Senior Member
 
ralph0808's Avatar
 
Join Date: Mar 2010
Posts: 279
243 across the hots with 121 or 122 to neutral and ground. O volts between W and G,
__________________
2018 Ram & Beacon 41LKB
ralph0808 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Load range F vs. Load range G Txcirclem Class A Motorhome Discussions 18 06-17-2013 04:03 AM
NEW Adobe Acrobat Reader Version XI (11) won't load older PDFs DriVer Technology: Internet, TV, Satellite, Cell Phones, etc. 6 12-23-2012 01:50 PM
Load Range D vs Load Range E royjeri 5th Wheel Discussion 29 07-29-2011 04:30 AM
Changes in Longitude... Changes in Attitude RickO Full-Timers 11 09-16-2010 05:13 PM
J-71 Auto Park, version II NALSO Winnebago Industries Owner's Forum 1 07-29-2010 09:46 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:54 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.