01-04-2019, 05:55 AM
|
#1
|
Member
Join Date: Dec 2018
Location: Cookeville, TN
Posts: 53
|
Dolphin Basement Air
I have a 2004 Dolphin with basement air. When I go to electric heat the unit does not kick on. There is a lot of "clicking" from the thermostat (especially when I touch in the area of the on/off switch) but 9 times out of 10 it won't start. When it does start it works great.
Has anyone had this issue?
Thermostat?
Mike
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
01-04-2019, 06:44 AM
|
#2
|
Senior Member
National RV Owners Club
Join Date: Jul 2013
Location: JACKSONVILLE,FL ex Newport Beach,Ca
Posts: 321
|
Coleman-Mach unit manual states If you set temp 2-3 degrees higher than temp shown, it should start.That is in the owners manual somewhere.
Tom 07 Pacifica
|
|
|
01-04-2019, 06:46 AM
|
#3
|
Senior Member
Winnebago Owners Club Freightliner Owners Club
Join Date: Mar 2007
Location: Home on the hill in Georgia
Posts: 2,742
|
I would thing loose or dirty connections on the thermostat itself. Most are easily removed from the base, clean the connections and plug back in. May help to plug and unplug several times.
__________________
Jerry Potter, Taz
1999 Coachman Catalina Sport
[SIGPIC][/SIGPIC]
|
|
|
01-04-2019, 06:49 AM
|
#4
|
Senior Member
National RV Owners Club Workhorse Chassis Owner
Join Date: Feb 2011
Location: Covington, GA
Posts: 785
|
Coleman HVAC info
The basic heat pump / gas heat operation is:
If the mode at the thermostat is elect heat, and the difference between the ambient temp and the desired temp is 5 deg or less the heat pump is activated & warmish air comes out of the ceiling vents.
If the difference is > 5 deg OR the mode is GAS, the gas furnace under the refrigerator comes on and warms the coach using the floor level vents.
I've had the Heat pump work down to 40deg F setting on the thermostat, provided I didn't set the room temp >5 deg.
__________________
J.J. Hayden (KN4SH)
Covington, GA
2005 National Dolphin 5342
|
|
|
01-04-2019, 07:05 AM
|
#5
|
Registered User
Join Date: Sep 2018
Posts: 310
|
I had the same problem.
Does the thermostat display go blank?
Check for 12 volts at the 3 pin connector when it powers up.
Mine went down to 3 volts
I had a bad wire connection somewhere and it was too difficult to find the starting point.
If it is coming from the furnace, it will be hooked to the positive of the two
blue "thermostat" wires on the furnace.
I was told by Airxcel that it didn't matter where the stat got it's power from and just find a good 12 volt power source.
It worked.
If that's not the problem then this was their diagnostics to test some of the wiring.
To test the lifeline:
1. Disconnect the lifeline (9-pin harness) from the thermostat, and the PC
board at the AC
2. At the PC board end of the lifeline, test for continuity from any wire to
the blue wire with the inline spade connector. If any wire in that lifeline is
shorted to that blue with the spade connector, the Lifeline would need
to be replaced.
If no shorts found, test the relays
To test the Relays:
1. Remove the wires from the coil side of each relay (compressor one will be a
yellow wire and a blue wire, compressor two relay will be an orange wire and a
blue wire)
2. Perform an Ohms test between the two terminals on the relay. If you show
resistance, the coil is likely good. If you show infinite Ohms, the coil is
shorted, and the relay would need to be replaced. If you show zero
resistance, the relay does need to be replaced, but it is not the source of your
short.
If you don't find a problem with the lifeline or the relays, the only other
possibility would be the PC board itself.
Part numbers you may need:
PC board replacement kit = 6535C3209
Compressor Relay = 1460-1131
Lifeline = If this is not a Winnebago the part number would be 6795C4351. If
this is a Winnebago, you would need to contact them for a part number, as they
made their own lifeline for this.
|
|
|
01-05-2019, 09:02 PM
|
#6
|
Senior Member
National RV Owners Club
Join Date: Mar 2012
Location: Lac Du Bonnet, Manitoba
Posts: 685
|
JJH3rd is correct. The thermostat is designed to only "maintain" the warmth in the RV if in electric heat(heat pump) mode. If the RV's temperature needs to be raised a lot, that is 5 degrees or more, the thermostat is designed to do it the fastest way by turning on the gas furnace. To save on LP gas, I often "fool" the thermostat's routine by turning up the temperature 4 degrees at a time, then the heat pump(electric heat) with kick in instead of gas heat. As the room approaches the increased 4 degree temperature, I raise the setting again another 4 degrees and so on.
__________________
Ellen & Greg
08 National Dolphin DL-35Ci, RoadMaster Rear Sway Bar, Rear Trac Bar, Koni Shocks Front,
Workhorse W22, Kelderman Air Ride, Towing 2016 Smart Car
|
|
|
01-06-2019, 10:08 AM
|
#7
|
Member
Join Date: Dec 2018
Location: Cookeville, TN
Posts: 53
|
Quote:
Originally Posted by TOM356C
Coleman-Mach unit manual states If you set temp 2-3 degrees higher than temp shown, it should start.That is in the owners manual somewhere.
Tom 07 Pacifica
|
Thanks it works great when I do this. I looked for trouble shooting...probably should have looked at operating instructions.
|
|
|
01-06-2019, 11:10 AM
|
#8
|
Registered User
Join Date: Sep 2018
Posts: 310
|
I guess mine was a different issue.
The stat would just start clicking randomly with nothing on.
And i have a spare stat if anyone wants to try it, lol.