220V Stove?

I was just over in the class A motorhome discussion about all electric RVs. This is what one of the responders said:

QUOTE: TIFFIN all electric option comes with a glass INDUCTION electric cooktop (faster )& free set of compatible cookware but can only be used with 50a shore or 10-12kw generator power as it requires 220volts to operate-not useable on inverter power !!UNQUOTE

Can that 220V stove really be true? Does anybody here have one of those? Seems sort of impractical...but I could be wrong.
__________________
Gary & Eloise
1992 Ford 350, 21' Fleetwood Jamboree Searcher Special
'15 Jeep Cherokee; 30 yrs full time, now in a very comfortable house!
elgarc is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-14-2011, 11:42 AM   #2
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
If true, this could be problematic. Some RV parks, in order to upgrade their 30 amp facilities to 50 amp, simply tap onto the existing 30 amp live leg and connect it as the other live leg in the receptacle. This works as long as there is no 240 volt loads because each phase is 120 volts to ground but when measured from phase to phase the voltage is 0(zero).
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 10-14-2011, 12:02 PM   #3
Senior Member
 
Francesca's Avatar
 
Vintage RV Owners Club
Join Date: May 2011
Location: Port Hadlock, Washington
Posts: 2,855
220v stove???

Good grief.

The difference between a "motor home" and a "mobile home" gets harder to figure out all the time!

Francesca
Francesca is offline   Reply With Quote
Old 10-14-2011, 12:20 PM   #4
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
It was a matter of time. With people replacing their refrigerators with house models, the gas stove was the only other obstruction to going all electric. There are some Hydro-Hot units that already have 240 volt heating elements.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Old 10-14-2011, 01:59 PM   #5
Senior Member
 
Francesca's Avatar
 
Vintage RV Owners Club
Join Date: May 2011
Location: Port Hadlock, Washington
Posts: 2,855


Why don't they just take the wheels off and get it over with?

Francesca
Francesca is offline   Reply With Quote
Old 10-15-2011, 04:49 PM   #6
Junior Member
 
kannonvaggon's Avatar
 
Tiffin Owners Club
Join Date: Nov 2010
Posts: 27
The current run of all-electric coaches from Tiffin comes with an INDUCTION smooth surface cook top. It is NOT running on 220V but on one phase of it which is 120V .... just like a microwave / convection oven...

You can never run this kind of device off inverter without " issues " .... the current draw on microwaves is very high indeed and when ya need to cook ya need to be on SP or fire up the genset. Just like ya can't run your A/C or heat pumps off the inverter but they will work peachy on shore power or genset. This is why God invented them big quiet diesel generators with auto-start.

Not a big problem for many folks.... BUT it's not sumthin I want myself. If I had a BUS with Hydro Hot heating on diesel then it would be pretty easy to push myself into removing the LP tanks system completely and going all-electric... I prefer the two gas furnaces and a gas cook top myself. We seldom use the furnaces and a tank of LP lasted us a year and a half. The cook tops now are pretty slick, but ya need special pots and pans and such and ya have to watch ya don't scratch the top sliding things around on the surface. I like a plain old gas burner just fine.

YMMV
JMHO
__________________
Jay and Joyce.. and IZZY the Havanese guard dog
2009 Tiffin 42 QBH on Spartan, HydraLift, DualSport mosickle, Jeep Cherokee TrailHawk toad, AF1 brake system
kannonvaggon is offline   Reply With Quote
Old 10-16-2011, 08:04 PM   #7
Senior Member
 
Oldrtrcr's Avatar
 
Tiffin Owners Club
Join Date: Jan 2008
Location: Warren, PA
Posts: 303
Have owned a 2012 Allegro Bus for about a month now. The induction cooktop requires 50 amp service or the generator to operate. It does require 220V. Through the use of the energy management system it will know if the park has created a "funny" 50 amp setup.
__________________
Bill Mahan
2012 Allegro Bus 43 QGP
Oldrtrcr is offline   Reply With Quote
Old 10-17-2011, 04:51 PM   #8
Junior Member
 
kannonvaggon's Avatar
 
Tiffin Owners Club
Join Date: Nov 2010
Posts: 27
I realize that ya need a 50A supposedly to run yer cooktop.... BUT...
are ya SURE it is using current from both the 120V lines at once, or is it using about 30A on one phase? Even yer 10-12K gensets don't put out a true 220V but rather two 120V lines .

Interesting.
I know that the cooktop I had looked at on a Bus last year was actually a 120V unit. If the latest iteration is truly a 220V unit, then I for sure stand corrected yet again.
__________________
Jay and Joyce.. and IZZY the Havanese guard dog
2009 Tiffin 42 QBH on Spartan, HydraLift, DualSport mosickle, Jeep Cherokee TrailHawk toad, AF1 brake system
kannonvaggon is offline   Reply With Quote
Old 10-19-2011, 08:46 AM   #9
Senior Member
 
Iron Man's Avatar
 
Newmar Owners Club
Join Date: Jul 2006
Posts: 1,118
Quote:
Originally Posted by kannonvaggon View Post
I realize that ya need a 50A supposedly to run yer cooktop.... BUT...
are ya SURE it is using current from both the 120V lines at once, or is it using about 30A on one phase? Even yer 10-12K gensets don't put out a true 220V but rather two 120V lines .

Interesting.
I know that the cooktop I had looked at on a Bus last year was actually a 120V unit. If the latest iteration is truly a 220V unit, then I for sure stand corrected yet again.
Our 12.5 gen puts out true 240v (we have a all electric coach with a 240v residential dryer).
__________________
John, Pam, and Aria
NKK 16073L
2015 London Aire
2015 GMC Seirra
Iron Man is offline   Reply With Quote
Old 10-19-2011, 08:48 AM   #10
Junior Member
 
kannonvaggon's Avatar
 
Tiffin Owners Club
Join Date: Nov 2010
Posts: 27
I most assuredly DO have to stand corrected.

The current model Summitt induction cooktop being installed by TMH is a true 220V unit which is wired through a double pole breaker....
so it won't operate on one line phase or the other but needs both. It ain't gonna work on a 30A feed at all.

On the other hand, it doesn't use as many AMPS cuz of the higher voltage.

There ya go. Learn sumtin every day....
I STILL don't want one them though ....
__________________
Jay and Joyce.. and IZZY the Havanese guard dog
2009 Tiffin 42 QBH on Spartan, HydraLift, DualSport mosickle, Jeep Cherokee TrailHawk toad, AF1 brake system
kannonvaggon is offline   Reply With Quote
Old 10-19-2011, 08:53 AM   #11
Senior Member
 
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
Quote:
Originally Posted by RJay View Post
If true, this could be problematic. Some RV parks, in order to upgrade their 30 amp facilities to 50 amp, simply tap onto the existing 30 amp live leg and connect it as the other live leg in the receptacle. This works as long as there is no 240 volt loads because each phase is 120 volts to ground but when measured from phase to phase the voltage is 0(zero).
If L1 and L2 are in phase as you describe, another silent but potentially deadly problem exists. Since current in the common Neutral is additive, if both hot legs (i.e., L1 and L2) are drawing 50 amps in a properly wired 50 amp RV service, the legs are 180° out of phase, so the Neutral current is 50 amps + (-50 amps) = 0 amps. However, if the 50 amp RV service is miswired such that the hot legs are in phase, Neutral current in our example is 50 amps + 50 amps = 100 amps, and the common Neutral will be overloaded since it is only sized for 50 amps. This can result in a meltdown of the Neutral circuit and fire.

Rusty
RustyJC is offline   Reply With Quote
Old 10-19-2011, 01:43 PM   #12
Senior Member
 
elgarc's Avatar
 
Join Date: Jan 2004
Location: Southwest, usually
Posts: 151
Quote:
Originally Posted by RustyJC View Post
If L1 and L2 are in phase as you describe, another silent but potentially deadly problem exists. Since current in the common Neutral is additive, if both hot legs (i.e., L1 and L2) are drawing 50 amps in a properly wired 50 amp RV service, the legs are 180° out of phase, so the Neutral current is 50 amps + (-50 amps) = 0 amps. However, if the 50 amp RV service is miswired such that the hot legs are in phase, Neutral current in our example is 50 amps + 50 amps = 100 amps, and the common Neutral will be overloaded since it is only sized for 50 amps. This can result in a meltdown of the Neutral circuit and fire.

Rusty

Whew! Is there a simple way to check for that type of shore power before plugging in?
__________________
Gary & Eloise
1992 Ford 350, 21' Fleetwood Jamboree Searcher Special
'15 Jeep Cherokee; 30 yrs full time, now in a very comfortable house!
elgarc is offline   Reply With Quote
Old 10-19-2011, 01:53 PM   #13
Senior Member
 
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
I suspect you have a power monitor in your coach that takes care of that for you. By that I mean that, if it doesn't see 240VAC across L1 to L2, it defaults to 30 amp service.

Rusty
RustyJC is offline   Reply With Quote
Old 10-19-2011, 02:44 PM   #14
Senior Member
 
RJay's Avatar
 
Newmar Owners Club
Join Date: Jan 2010
Posts: 4,589
Quote:
Originally Posted by RustyJC View Post
If L1 and L2 are in phase as you describe, another silent but potentially deadly problem exists. Since current in the common Neutral is additive, if both hot legs (i.e., L1 and L2) are drawing 50 amps in a properly wired 50 amp RV service, the legs are 180° out of phase, so the Neutral current is 50 amps + (-50 amps) = 0 amps. However, if the 50 amp RV service is miswired such that the hot legs are in phase, Neutral current in our example is 50 amps + 50 amps = 100 amps, and the common Neutral will be overloaded since it is only sized for 50 amps. This can result in a meltdown of the Neutral circuit and fire.

Rusty
You are absolutely correct. These parks who trying to make a 30 amp service look like 50 amps are doomed to failure at best and destruction at worst. RVer's should be aware when testing voltage at the pedestal that a L1-L2 reading of 0 will significantly load their neutral. In addition the additional load on the neutral will create more voltage drop problems in the park.

In my last discussion with Progressive Industries, I was told they were going to try to incorporate the L1-L2 test. I got the impression they were trying to accomplish this on their existing control board and not do a redesign. At the time they weren't sure if they could do it or when it would be available. My guess is they already have the L1-L2 voltage relationship the problem is how to indicate it for the different readings. Since some parks are using a three phase 120/208 volt service to upgrade their electrical service the L1-L2 test is even more important.

RVer's should know phase to phase voltage relationships especially when those RV's have true 240 appliances and anything less will reduce their performance.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
RJay is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kitchen Project: Adding a Stainless Steel Stove Backsplash RedneckExpress Vintage RV's 9 01-11-2011 10:42 AM
12 volt stove exhaust fan replacement needed kartvines Vintage RV's 15 12-02-2010 12:55 PM
Microwave Stove Vent J Stemler Winnebago Industries Owner's Forum 7 06-16-2010 10:22 AM
Atwood Stove gator67 Alpine Coach Owner's Forum 5 05-10-2008 09:07 PM
Stove Top Grate GoneFishin Monaco Owner's Forum 3 04-28-2008 06:46 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:25 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.