Heavy AC Power Load-Shore Power Drops Offline?

2016 Phaeton with Magnum Sine Inverter/converter (Model MS2012, I think) with remote panel over Driver's seat. Plugged into RV park 30 amp shore power & all seems OK - Panel shows batteries Float (& sometimes Absorb) charging, 12 to 13 volts, with green lights on PWR, CHG, INV. When "heavy" load, like AC unit, space heater, microwave, etc comes on, CHG drops off & it appears house batteries take the load (again CHG LED goes dark & Panel drops to under 12 volts & LED lights in coach flicker). Load, as shown on the "Power Control Central Monitor Panel" (also over Driver's Seat) shows Line 1 & 2 combined loads well under 30 amps (15 to 25 amps). After a few moments (with the AC device still working), CHG LED goes green again, coach lights stops flickering & all seems well.. I've had the coach over 5 years & this is a new experience. (Note, the majority of the time I have 50 amp service. However, I don't recall having this problem the few times I've been on on 30). Shore Power or Inverter or other issue? Thoughts / suggested remedies? Thx!
JT-RV is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-28-2022, 07:23 PM   #2
Junior Member
 
Join Date: Jan 2022
Posts: 16
How much current are the batteries drawing? Do you have the same issue if the batteries are disconnected from inverter/converter?
Mdb from BC is offline   Reply With Quote
Old 09-28-2022, 09:07 PM   #3
Senior Member
 
Newmar Owners Club
Entegra Owners Club
Join Date: Dec 2015
Posts: 1,165
It sounds to me like you may have a MSH model Magnum Inverter/Charger which features something called “load support”. Load support is used when you are connected to external power, either shore power or generator, and it senses that the current demand on its “pass-thru” output is exceeding the maximum that the external power can provide. The Magnum senses this and instantly shuts down it’s batt charging activity and turns on the Inverter (synchronized to the external power) and the inverter will supply additional current to the load from the 12VDC battery bank.
It’s a pretty cool feature but if you think yours isn’t acting properly it may be mis-programmed. Check the owners manual.
__________________
2021 Entegra Aspire 44W
Previous: 2006 Newmar Essex 4508
2013 Tiffin Allegro Open Road
Archer2 is offline   Reply With Quote
Old 09-29-2022, 10:56 AM   #4
Senior Member
 
garykk's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Apr 2012
Location: Southern NM
Posts: 2,882
It appears your system is operating as it should. You have way to many appliances on for a 30 amp service.
__________________
2018 Allegro Bus 37AP
2014 Phaeton 40 QBH (sold)
2022 Jeep JLURD
garykk is offline   Reply With Quote
Old 09-30-2022, 01:37 AM   #5
Member
 
Tiffin Owners Club
Join Date: Nov 2016
Location: On the Move . . .
Posts: 57
Heavy AC Load-Shore Power Drops Off-Line

Thx all. “Load Support” makes sense. Except, to clarify, I do not have all those appliances turned on at the same time. None are on. Just turning on just one of them causes the CHG Indicator to turn off and house battery voltage on the panel to drop as batteries take/share the load. After 10 to 30 seconds (with appliance still on) CHG indicator light goes on again & battery voltage jumps back up to 12 to 13 volts & “float charging” message returns & all seems well. As mentioned, during all of this, the Central Monitor Panel shows total line load well under 30 amps (typically under 20).
JT-RV is offline   Reply With Quote
Old 09-30-2022, 10:15 AM   #6
Senior Member
 
jkorn's Avatar
 
Tiffin Owners Club
Join Date: May 2018
Location: Third rock from the Sun
Posts: 506
Send a message via Yahoo to jkorn
30 amp

Understand that 50 amp provides two separate 110 volt legs. Out of phase. That’s how you get 220 for some appliance’s. Like the induction cooktop if you have one.

30 amp only provides power on one of the legs. Single phase. So typically some outlets will not have power. Those wired to the second phase. While 30 sounds like more than half of 50, basically it is not. So huge difference. AC’s may not work at all, or maybe one will depending on year of coach.

Hope this helps. Jeff
jkorn is offline   Reply With Quote
Old 09-30-2022, 10:33 AM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 31,677
Quote:
Originally Posted by jkorn View Post
Understand that 50 amp provides two separate 110 volt legs. Out of phase. That’s how you get 220 for some appliance’s. Like the induction cooktop if you have one.



30 amp only provides power on one of the legs. Single phase. So typically some outlets will not have power. Those wired to the second phase. While 30 sounds like more than half of 50, basically it is not. So huge difference. AC’s may not work at all, or maybe one will depending on year of coach.



Hope this helps. Jeff
That doesn't help because with a 30 amp to 50 amp adaptor, both legs are supplied power. The adaptor has a jumper in it for that purpose.

Now you share that single 30 amp leg to both 50 amp legs and everything works, but limited to 30 amps, not 100.
twinboat is offline   Reply With Quote
Old 09-30-2022, 10:49 AM   #8
Senior Member
 
garykk's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Apr 2012
Location: Southern NM
Posts: 2,882
You also have to take into consideration the actual power coming from the campground pedestal. We were once at a campground in Canada that was supposed to be 30 amp. The campground was crowded and it was hot. The power from the pedestal was not even enough to get thru my EMS.
__________________
2018 Allegro Bus 37AP
2014 Phaeton 40 QBH (sold)
2022 Jeep JLURD
garykk is offline   Reply With Quote
Old 09-30-2022, 03:03 PM   #9
Senior Member
 
SamKVA's Avatar
 
Join Date: Sep 2015
Posts: 224
Quote:
Originally Posted by twinboat View Post
That doesn't help because with a 30 amp to 50 amp adaptor, both legs are supplied power. The adaptor has a jumper in it for that purpose.

Agree.

Now you share that single 30 amp leg to both 50 amp legs and everything works, but limited to 30 amps, not 100.
However, a 50 amp source is just that; it's not 50 amps per leg for a total of 100 amps.
__________________
2021 Tiffin Phaeton 40IH
2016 Jeep Wrangler JK Sport TOAD - Air Force One
SamKVA is offline   Reply With Quote
Old 09-30-2022, 03:09 PM   #10
Senior Member
 
SteveJ.'s Avatar
 
Join Date: Dec 2019
Location: America's Seaplane City.
Posts: 845
Quote:
Originally Posted by SamKVA View Post
However, a 50 amp source is just that; it's not 50 amps per leg for a total of 100 amps.
Actually, it is 50 per leg for a total of 100 unless someone has done some creative alterations.
__________________
1998 Safari Trek 2480, 7.4 Vortec
'15 Kawasaki Versys650LT, well farkled
Mid Flowriduh
SteveJ. is online now   Reply With Quote
Old 09-30-2022, 08:17 PM   #11
Senior Member
 
SamKVA's Avatar
 
Join Date: Sep 2015
Posts: 224
Quote:
Originally Posted by SteveJ. View Post
Actually, it is 50 per leg for a total of 100 unless someone has done some creative alterations.
Mathematically, you are correct as a 50 amp circuit breaker is rated for each pole to trip at 50 amps. However, when one pole trips, the bridged/total breaker trips. Therefore, it's pretty unlikely you would ever get to 100 amps current draw even if the campground was capable of delivering it which in my experience, is also unlikely.

Sam
__________________
2021 Tiffin Phaeton 40IH
2016 Jeep Wrangler JK Sport TOAD - Air Force One
SamKVA is offline   Reply With Quote
Old 10-01-2022, 07:09 AM   #12
Senior Member
 
vettenuts's Avatar
 
Join Date: Nov 2013
Posts: 5,512
The Power Control Panel is doing that and what you observing is normal. Their website has a good explanation of its operation. I saw the same thing a few months back when I had an issue with my air conditioner and found the information on the website.
__________________
2015 Tiffin Phaeton 40QBH
2018 Chevrolet Colorado Toad
Roadmaster Tow Setup
vettenuts is offline   Reply With Quote
Old 10-01-2022, 01:01 PM   #13
Senior Member
 
jkorn's Avatar
 
Tiffin Owners Club
Join Date: May 2018
Location: Third rock from the Sun
Posts: 506
Send a message via Yahoo to jkorn
I stand corrected ………

We are in the coach today. So I disconnected the 50 amp and connected to 30. Our coach is highly automated so watching the led panel I could see how it shed then reconnected items. Finally the aquahot electric heater came back on and I ran the middle heat pump successfully. And yes I could see amperage on both legs. Didn’t test floor heat but computer seems to prioritize what gets power when.
This probably doesn’t help older rigs but I did test our 2021. Jeff
jkorn is offline   Reply With Quote
Old 10-01-2022, 01:26 PM   #14
Member
 
Tiffin Owners Club
Join Date: Nov 2016
Location: On the Move . . .
Posts: 57
Looks like GaryKK got the answer on this one. Yes, it was an excessive power drain issue, but on the SHORE POWER side. At my next campground, I plugged into 30amp service & no issues. So, I think the campground where I first had the problem (Gary-coincidentally in Canada-haha) wasn't delivering 30 amps - Possibly because Hurricane Fiona had passed by the day before, causing havoc with the power grid. Bottom line - Nothing wrong with my RV Inverter / power control systems! Thanks All!
JT-RV is offline   Reply With Quote
Reply

Tags
power, shore power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage drops when Under load - Alternator? rpasetto Monaco Owner's Forum 9 11-02-2021 08:45 PM
Onan Quiet Diesel drops offline while driving maddog468 Monaco Owner's Forum 15 07-11-2017 02:01 PM
How heavy is too heavy? Radio Flyer Trailer Towing and Tow Vehicles Discussion 7 06-16-2014 10:27 PM
Generator Drops Offline Thudman Winnebago Industries Owner's Forum 13 07-31-2005 07:43 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:32 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2022, vBulletin Solutions, Inc.