Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > THE OWNER'S CORNER FORUMS > Tiffin Owner's Forum
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 11-24-2020, 12:08 PM   #1
Member
 
Join Date: Sep 2020
Posts: 83
Pedestal GFI Pops

I am parked in a RV storage place that has a 20 amp pedestal with a GFI outlet. When I hook it up to my 2008 allegro bus, it lasts for about 20 or 30 seconds and the GFI pops. I reset it and the same thing. the house batteries are new as of last week. I have thot of just hooking up my battery charger and charge the batteries directly, bypassing the bus inner workings. it was previously hooked up to a 50 amp outlet and no problems. Any ideas?? thanks, John
john foose is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-24-2020, 12:44 PM   #2
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,843
Open your AC Panel and then open each CB one at a time until GFCI doesn't trip (helps having 2 people....one opening the CBs and one resetting the GFCI)

If after ALL CBs are open and GFCI still trips...Open the RV Main CBs

Typically it will end up being a heater element ,..... fridge, water heater
They can function A-OK but 'leak' a little current...GFCI senses the imbalance and trips
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 11-24-2020, 12:57 PM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
If you have built in surge protection, its testing may be another item thats causing the ground fault.

GFCIs are not overload devices, they save you from becoming a conductor of electricity if it gets out of the wires, and leaks to the chassis.
twinboat is offline   Reply With Quote
Old 11-24-2020, 01:11 PM   #4
Member
 
hipkts2010's Avatar
 
Tiffin Owners Club
Join Date: Apr 2010
Posts: 84
My suggestion is to go to your inverter control panel and turn down the available amps to 20 or 15. It is probably set to either 30 or 50. The inverter is trying to charge the batteries and drawing too much current. IMHO.
__________________
Mike & Linda Whitenton, Semi-Ret-2014, FT-2003
2010 43 QGP Allegro Bus/DEF (Sold), 2018 GMC Acadia Denali. Motorhomeless 12/25/2021.
hipkts2010 is offline   Reply With Quote
Old 11-24-2020, 01:22 PM   #5
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,843
Quote:
Originally Posted by hipkts2010 View Post
My suggestion is to go to your inverter control panel and turn down the available amps to 20 or 15. It is probably set to either 30 or 50. The inverter is trying to charge the batteries and drawing too much current. IMHO.
A GFCI monitors the amount of current flowing from hot to neutral. If there is any imbalance, it trips the circuit. The GFCI senses a mismatch as small as 4 or 5 milliamps, and it can react as quickly as one-thirtieth of a second.
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 11-24-2020, 02:24 PM   #6
Senior Member
 
garykk's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Apr 2012
Location: Southern NM
Posts: 3,380
Yours is one of many complaints about GFIs and Tiffins. They just done work together.
__________________
2018 Allegro Bus 37AP
2014 Phaeton 40 QBH (sold)
2022 Jeep JLURD
garykk is offline   Reply With Quote
Old 11-24-2020, 02:53 PM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
Quote:
Originally Posted by hipkts2010 View Post
My suggestion is to go to your inverter control panel and turn down the available amps to 20 or 15. It is probably set to either 30 or 50. The inverter is trying to charge the batteries and drawing too much current. IMHO.
If you draw to much power, the circuit breaker trips, not the GFCI receptcal. Fact.
twinboat is offline   Reply With Quote
Old 11-25-2020, 08:21 AM   #8
Senior Member
 
jkorn's Avatar
 
Tiffin Owners Club
Join Date: May 2018
Location: Third rock from the Sun
Posts: 564
Send a message via Yahoo to jkorn
I have the same problem..

It has NOTHING to do with the amount of draw from the RV like several have suggested. There seems to be some leakage back on the third wire ground from the Bus that the GFI outlet does not like, then trips. This is true no matter what amperage the outlet is.

That's what a GFI does, it looks for voltage on the 3 wire ground, which should have none most of the time.

I have had this issue with 50 and 20 amp GFI outlets. At home I have to find a outlet that is not a GFI. There just do NOT work together.

Friend had a 50 amp GFI at his site that I could not connect to either. He finally swapped it to a non GFI and all good.

Jeff
__________________
2021 Tiffin Allegro Bus 45OPP
2014 Tiffin Allegro Bus 40SP, 450HP
2015 Jeep GC, Air Force 1, Roadmaster Nighthawk
jkorn is offline   Reply With Quote
Old 11-25-2020, 05:05 PM   #9
Senior Member
 
Talloaks's Avatar
 
Country Coach Owners Club
Join Date: Feb 2019
Location: Tucson AZ
Posts: 457
Quote:
Originally Posted by jkorn View Post
I have the same problem..

I have had this issue with 50 and 20 amp GFI outlets. At home I have to find a outlet that is not a GFI. There just do NOT work together.

Friend had a 50 amp GFI at his site that I could not connect to either. He finally swapped it to a non GFI and all good.

Jeff
Jeff, have you and your friend verified that you do not actually have a ground fault condition on your rig?

The GFI receptacle tripping is designed to tell you that you have a ground fault. The subsequent steps that would confirm or dispel this symptom would be to systematically test for a ground fault. If you don't, the next indication would be when you experience the electrical shock. There is typically no other advance warning, because these ground faults, while large enough to injure or kill you or your loved one, they are not large enough to trip the actual circuit breaker, or cause any heating or odor. Your 15-20-30-50 amp circuit breakers are designed to protect the conductors that make up your electrical circuits and prevent them overheating and causing fires. They do not protect people from electrocution. Serious injury and death can result from very small currents, much smaller than what would be needed to trip your circuit breaker. That is what the GFI is for.

Changing to a non-GFI receptacle silenced the alarm that was telling you that you had a potentially lethal condition, but it did not make the condition go away.

Sometimes a GFI receptacle is faulty and needs to be replaced. That happens. But it's not a safe bet to assume the GFI is at fault.

And beware when people say "certain rigs don't play well with GFCI's." That (IMHO) is a copout for not taking the time or having the understanding to actually trace the fault. That also is not a safe bet for you and your loved ones.

Test your rigs electrical systems. It takes a little time but it's not that difficult.

Good luck.
__________________
John
2007 Country Coach Tribute; Cat C9 400; 2012 Ford Edge toad; Roadmaster Blackhawk 2 10,000 lb tow bar; Demco AF1 Braking System; 2007 BMW K1200LT Hannigan Trike Conversion; Member, IEEE, NFPA, PMI, NRC SRO (Ret).
Talloaks is offline   Reply With Quote
Old 11-26-2020, 05:39 AM   #10
Senior Member
 
vettenuts's Avatar
 
Join Date: Nov 2013
Posts: 5,778
I had this issue with my coach at home. This year I bought a US made Hubble GFCI plug, rather then the Chinese POS from Home Depot. Problem is now gone.

Is there another post you can plug into to find out if that particular outlet is the issue?
__________________
2015 Tiffin Phaeton 40QBH
2018 Chevrolet Colorado Toad
Roadmaster Tow Setup
vettenuts is offline   Reply With Quote
Old 03-31-2021, 01:45 PM   #11
Junior Member
 
Join Date: Mar 2021
Posts: 2
Same issue with a Tiffin Allegro RED QSA. The 50 AMP GFCI ran fine for about 20 min then tripped. Called Tiffin and explained the situation. House GFCI trips immediately cant run a thing. I went in the coach and turned all circuit breakers off with 50 AMP disconnected. (No power or manual cord reel Tiffin asked as these are problematic if not wound /mounted obviously). With circuit breakers and everything set to off I connected the 50 AMP to power box and it tripped the GFCI. Now I wondered did I have a bad Transfer Switch? Called Tiffin again they said remove the Power Cord connection to the (4 center wires) WITH THE 50 shore power cord disconnected 1ST ! from GFCI 50 AMP Pedestal) so you live to tell about the next step. Then after the 4 cables to the transfer switch were removed I taped the exposed wires so they couldn't touch each other or ground or energize anything (AKA Welding)! Then Tiffin said to plug the cord up and see if it tripped the GFCI with only the RV 50 amp cable plugged in. It did not trip the breakers so everything was good to the transfer switch. I unplugged the 50 AMP cord to the House pedestal and re connected the 50 AMP cable to the transfer switch. Others looked at their transfer switch and found burnt cables but mine all looked pristine so I figured it was time to suspect from the TRANSFER SWITCH to FUSEBOX connection as a slide might have pulled it loose/sloppy. this is the 2 Legs/POWER connections that come out on either side L OR R on the Transfer Switch. Where these cables entered the RV they removed the outside sheathing and just had the individual cables sheathing. I thought how unimpressive/poor design to remove the protective main sheathing and run the wires thru the side wall with only a strain relief to rub the cables cover down to the metal! There was a big was of the foam sealant over these connections where the wires went into the outside wall. I knew then I was probably looking at the issue. When I pulled these wires about 1/2 inch out from the outside wall (Leg 1 and Leg 2) I figured I'd run a zip tie around the cables so they couldnt creep back in to the wall and trip the 50 AMP GFCI at the pedestal. (the coach never tripped a single breaker anytime in the cloth set). I left the coach circuit breakers all off then plugged up the power and reset the GFCI. The GFCI is now holding AHA moment! I went and turned all the bedroom breakers on and then had power finally. The power cables barely fit thru the RV wall so the installer removed the sheathing! Then covered the problem with foam sealant to hide a lousy installation that just needed a few miles of rubbing on the stress to cause a bare wire grinding on the chassis. Corrected the L1 and L2 power leg entry points to the wall and life is good! No more grounding out !
1 more suggestion. NEVER plug into a pedestal and assume its wired correctly! I have seen folks burn their electrical system up. I camped at a place with a 30 amp plug. I came back and the campsite next to me was on fire by the pedestal headed for my unit. The guy who applied the electricity (notice I didn't call them an electrician) had it wired wrong and about sat everything on fire. (never use water on an electrical fire) !
2. Camped at another new place that had a New 50 AMP Installed (Warning signs went off naturally) got out my surge protector and plugged it up. Nothing and surge said it had no power as well. Pedestal surge was on so I reset it. Called the campground guy and he said Hmm just paid to put it in and I told them the box front wasn't on right either. The called the electrician and he wouldn't answer. We got another electrician to come out to see what the issue was. The other electrician had put up a breaker box on a 4x4 post and ran the wire underground about 6 inches below ground for about 3 foot out underground and had not wired it to ANYTHING! Buy an RV electrical surge protector and protect yourself and property from people who call themselves electricians! They are just "welders" who don't use any welding rods! HA imagine that...
Daboss is offline   Reply With Quote
Old 03-31-2021, 11:53 PM   #12
Senior Member
 
jkorn's Avatar
 
Tiffin Owners Club
Join Date: May 2018
Location: Third rock from the Sun
Posts: 564
Send a message via Yahoo to jkorn
DONT DO THIS

I finally cut off the third wire plug on my 30 amp to 20 adapter at the 20 amp side and gfi quit popping. I tested chassis to ground. No voltage. Jeff
__________________
2021 Tiffin Allegro Bus 45OPP
2014 Tiffin Allegro Bus 40SP, 450HP
2015 Jeep GC, Air Force 1, Roadmaster Nighthawk
jkorn is offline   Reply With Quote
Old 04-01-2021, 12:27 AM   #13
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
RVs and GFCI protected shore power often do not play well together - usually due to ground fault situations that can be inherent to RVs.

Best to swap out the GFCI or use different non GFCI protected circuit.

If you want to try to isolate a ground fault source. Drop all breakers in the main/sub breaker panel. Then bring them on individually until it trips.

A ground fault likely is occuring when the inverter relay transfers the neutral/ground bonding. It may be timing sensitive - so occurs intermittently.

Note. GFCI do not trip on excess power draw, rather a ground fault. Unless - its current sensor has saturated (ensure charger shore setting is reduced, no air conditioning on, etc). So excess current us a possibility. Ensure all high power draw items are turned off when connecting shore power.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 04-01-2021, 03:16 AM   #14
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
So we don't want to cut the ground pin off the adaptor, which will prevent the GFCI tripping, but its OK to remove the GFCI receptcal ?

I would leave the GFCI in place and cut the ground pin off. That way, if I found my body being the conducter of current, the GFCI would trip.
twinboat is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Convert GFI to non-GFI RV Vagabond iRV2.com General Discussion 28 12-14-2016 06:55 AM
Norcold problem--not recall--pops GFI ccraig RV Systems & Appliances 10 06-03-2013 06:28 PM
Heart Freedom 20 pops house GFI craigt Winnebago Industries Owner's Forum 9 12-13-2007 05:33 AM
Carlisle May-Pops have reared their head Todd T Travel Trailer Discussion 1 09-11-2006 06:29 PM
Heart Freedom 15 Inverter pops input circuit breaker. JB Texas MH-General Discussions & Problems 11 05-04-2005 08:53 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:46 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.