This really depends on what you want to be able to do while it is stored at home, I installed a 50 amp outlet in the shed where I store my coach which allows full life as normal operation.


A general outline of outlet sizes, and what you can generally run are:


15 amp 120V residential outlet (1,800 watts maximum, 1,500 watts nominal), lets you run battery converter /charger (can draw up to about 600 watts (maybe 850 on a larger converter) with depleted batteries being charged), plus RV refrigerator (which draws around 350 watts on its own), as well as a few lights and incidental loads.


20 amp 120V outlet (2,400 watts maximum, 1950 watts nominal), these are the ones that look like a 15 amp outlet, except one side has a T shaped slot and will accept either 15 or 20 amp cords, this is the minimum size you should consider if you want to run 1 RV roof top air conditioner (1,250 watts, with much more draw in starting surge), along with basic loads like battery charger maintaining batteries and refrigerator (350 watts)


30 amp 120V outlet (3600 watt maximum, 2880 watt nominal load), this is the common 30 amp RV outlet. This is as large as you need if you have a 30 amp RV, generally speaking this will supply life as normal load in a small RV with 1 air conditioner, basic loads, and possibly 1 other major load running (microwave, hair dryer, etc.)


50 amp 120/240V 4 prong outlet (12,000 watts maximum, 9,600 watts nominal), this is a 50 amp RV outlet, and lets you operate life as normal in an RV, run multiple roof top air conditioners, as well as major rv appliances, electric water heater element, ...


p.s. whatever outlet you plug into make sure it is in good condition, an old worn outlet is prone to overheating and potentially causing a fire if ran at continuous heavy loads, even it they are within its rated outlet due to corrosion and loose springs on the prongs. It is a good idea to check for heat buildup at the plug on all outlets, and if using an adapter for 15 or 20 amp outlets use the dobgone not the hockey puck style as they tend to dissipate heat a little better.
__________________
2002 Safari Trek 2830 on P32 Chassis with 8.1L w/ 400 watts solar 420Ah LiFePo4
2017 Jeep Cherokee Overland & 2007 Toyota Yaris TOADs with Even Brake,
Demco Commander tow bar and Blue Ox / Roadmaster base plates
Isaac-1 is online now   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-12-2019, 05:20 AM   #16
Senior Member
 
Rolling Ragu's Avatar
 
Join Date: Sep 2018
Location: Upstate South Carolina
Posts: 285
I'm looking to install a pedestal next year this time. In my case, I'm running about 150' to the RV. This makes the difference in cost from 30 to 50amp to be in the neighborhood of $500 for heavier gauge wire.

Since I'm in covered storage, I can't fathom when I couldn't get by quite well with 30 amp. $500 seems like a stiff premium for the handful of times I might want to run both A/C's.

Short run? No brainer to go 50amp. Long run? Not so sure. My point, every situation is unique.

For now, I run an extension from a 20amp in my garage. It allows for everything I need, requiring I manage only one large appliance at a time.
__________________
2011 Tiffin 34TGA Tony & Cindy
Explore with us on our YouTube channel
https://www.youtube.com/channel/UCCa...view_as=public
Rolling Ragu is offline   Reply With Quote
Old 01-12-2019, 06:10 AM   #17
Senior Member
 
Sweetbriar's Avatar
 
Thor Owners Club
Ford Super Duty Owner
Join Date: Jul 2011
Posts: 3,796
When I installed the outlet I'm currently using I probably violated some electrical code by installing 120VAC split phase 30 amp service to a NEMA 14-50 aka RV 50 amp outlet. My coach is 50 amp configured due to the second roof A/C and has worked fine on 30 amp service in the past but I had to watch loading with the second A/C and other additions. I wanted the option of being able to run everything with no worries of overloading a circuit. I had a 30 amp outlet for several years so running an additional single 10 gauge wire from the outlet back to the house panel, replacing the NEMA TT-30 outlet along with adding double pole 30 amp breaker in the house panel was easy Saturday morning upgrade.

The possible code problem? The outlet, NEMA 14-50, is rated for 240VAC split phase 50 amp service. My suspicion is per code the circuit supporting it should also has the same power capacity. I'm configured for 240 volt split phase 30 amps. A competent home inspector should find the miss match if I ever plan to sell.
__________________
2006 Hurricane 31D built on a 2006 Ford F53
Sweetbriar is offline   Reply With Quote
Old 01-12-2019, 07:44 AM   #18
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Quote:
Originally Posted by Sweetbriar View Post
The possible code problem? The outlet, NEMA 14-50, is rated for 240VAC split phase 50 amp service. My suspicion is per code the circuit supporting it should also has the same power capacity. I'm configured for 240 volt split phase 30 amps. A competent home inspector should find the miss match if I ever plan to sell.
NEC 210.21(b)(1) does not prohibit that, though most inspectors would probably raise an eyebrow at minimum, and it’s sometimes debated online amongst pros in the business. 210.21 Outlet Devices says:

“Outlet devices shall have an ampere rating not less than the load to be served and shall comply with (a) and (b) below.”, where (a) refers to lamp holders and (b) to receptacles. The 50A device (a receptacle or switch is a ‘device’) clearly has an adequate rating, even if the 30A circuit is light for the max load you could put on it by not managing the loads in the coach.

210.21(b)(1) Outlet Devices, Receptacles:
“A single receptacle installed on an individual branch circuit shall have an ampere rating of not less than that of the branch circuit.”

Tables 210.21(b)(2) and (3) do not apply, as they’re invoked by Art. 210.21(b)(2) and (3) only and refer to two or more receptacles or outlets on a branch circuit.

It may not be considered good design, but the NEC isn’t a design specification or instruction manual and says so (in those words) right in the beginning.

I was going to suggest 30A to a 14-50 receptacle in another thread to save money for someone who needed just a tad over the 30A 120V supplied by the TT-30R (3600W), but it would create more issues (and discussion) than it would solve. Like discussions of ‘undersized’ conductors on welder supply circuits, or not adhering to the 15/20/30A rule for 14/12/10 gauge copper on motor and HVAC circuits (also allowed).

Of course, the power cord is more like a feeder than a branch circuit, so there’s that.
KanzKran is offline   Reply With Quote
Old 01-12-2019, 08:12 AM   #19
Senior Member
 
les.warden's Avatar
 
Tiffin Owners Club
Join Date: Nov 2011
Location: Foley, AL
Posts: 1,093
Plugging into home electrical service

I’m in Central Illinois. Mine’s winterized and kept in a non-insulated building with 30A service. I dial the controller to say I’m using a 30A service so it doesn’t try to pull 50A for some unknown reason. Going on 3 years and works fine.
__________________
Les & Pam Warden
(Tiffin) 2017 Phaeton 40QBH; 2023 Wayfarer 25RW (coming soon)
2016 Jeep JKUS with Ready Brute Elite towbar
les.warden is offline   Reply With Quote
Old 01-12-2019, 08:29 AM   #20
Senior Member
 
LarryJB's Avatar




 
Tiffin Owners Club
RV Trip Wizard
Join Date: Oct 2016
Location: Mountainburg, AR
Posts: 1,647
Quote:
Originally Posted by winniman View Post
Yep. My previous rv was a 30 amp. I used to just plug it in to the outside plug on the house. It was enough to charge the batteries. My fridge, furnace, and water heater all could run on propane, so the 15 amp house plug was enough for these things plus lights. I had a 30 amp 110volt plug added to the outside of my house for the rv. My current rv is 50 amp, but the 30 amp is enough to run everything in the rv except both air conditioners at once, or the microwave at the same time as the air conditioners.
+1 to this. This is exactly what we did. When I got my current coach with the 50amp plug, I did not upgrade to 50 amp and see no real reason to do so. If I ever have the need to run all AC units (which has yet to happen), I can always start the genny.
__________________
There are 10 types of people... Those that understand binary and those that don't.
_________________________
2018 Tiffin Phaeton 40AH/2018 Hyundai Elantra Sport Toad
LarryJB is offline   Reply With Quote
Old 01-12-2019, 09:43 AM   #21
Member
 
Bagelboy's Avatar
 
Join Date: Jul 2017
Posts: 98
I plug mine into a standard 20 amp outlet at my house. I've been doing it this way for years, but I only leave the refrigerator on and charge the batteries, nothing else. In the summer I just leave a few windows open. I've never had problems.
Bagelboy is offline   Reply With Quote
Old 01-14-2019, 04:34 AM   #22
Senior Member
 
stew1's Avatar
 
Join Date: Sep 2013
Location: dickinson, tx
Posts: 327
Had a 50 amp breaker put in my outside breaker box and ran wires underground to motorhome with 50 amp plug for it leave plugged in all the time
stew1 is offline   Reply With Quote
Old 01-26-2019, 07:50 PM   #23
Junior Member
 
Join Date: Sep 2018
Posts: 18
I plug into 50 A at home because sometimes I run my air conditioners
rvingchub is offline   Reply With Quote
Old 01-26-2019, 08:08 PM   #24
Senior Member
 
rarebear.nm's Avatar
 
Excel Owners Club
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Aug 2014
Location: Santa Fe, NM
Posts: 6,816
I keep both our 5th (50Amp service) and the MH (30 Amp service; this is not a typo) plugged into two individual standard RV 30 Amp outlets. I can run anything I want on both rigs while in storage. Neither one has dual ACs to worry about. I did both circuits with 8 gauge wire to reduce the voltage drop and because I already had it around.

Whereas 15/20 Amp might work as Twinboat points out GFCI on those circuits may cause you unwanted troubles.

What ever you do, just do it right and stay safe.
__________________
Fred & Denise (RVM157) New Mexico
2007 Excel Classic 30RSO & Coach House 272XL E450
2007 RAM 3500, Diesel, 6Spd Auto, SWD, 4x4, CC & LB
[SIGPIC][/SIGPIC]
rarebear.nm is online now   Reply With Quote
Reply

Tags
electric, electrical, service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question when plugging TT into electric at home Dmrad iRV2.com General Discussion 10 10-24-2018 02:11 PM
Plugging into 110 at home? Baystar question... ghoticov Newmar Owner's Forum 30 01-04-2017 08:50 PM
Newbie question - plugging into home elec WVWilley iRV2.com General Discussion 16 06-17-2016 02:01 PM
Plugging into 15a at home HavingABlast Newmar Owner's Forum 40 01-02-2016 02:28 PM