Old 06-22-2021, 10:35 AM   #1
Junior Member
 
Join Date: Jan 2021
Posts: 23
Shore power not enough?

I recently bought a 2008 Allegro Bus 43 QRP and where I bought it said that it had 3 AC units but that on shore power I could only run 2 at a time but if using the generator I could run all 3. Is this right? It doesn't make sense to me but I am new to motor coaching. Here in AZ it is 🔥 HOT 🔥 and it doesn't keep up with the heat when I run 2. I am plugged in to a good 50 amp 220v receptacle and want to run all 3 units. Can this be done safely? Or was the guy at the stealership correct?
Rhobson is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-22-2021, 10:42 AM   #2
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
Quote:
Originally Posted by Rhobson View Post
I recently bought a 2008 Allegro Bus 43 QRP and where I bought it said that it had 3 AC units but that on shore power I could only run 2 at a time but if using the generator I could run all 3. Is this right? It doesn't make sense to me but I am new to motor coaching. Here in AZ it is �� HOT �� and it doesn't keep up with the heat when I run 2. I am plugged in to a good 50 amp 220v receptacle and want to run all 3 units. Can this be done safely? Or was the guy at the stealership correct?

If the three are wired correctly (two to one hot and the other to the other hot along with all other high-amp loads) I see absolutely no reason you can do it on 50 amp shore power.


Said another way, I can't see a way either L1 or L2 load could exceed 50 amps.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Old 06-22-2021, 10:50 AM   #3
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 9,750
What size gen do you have? If less than 12.5KW, it makes less power than a 50A shore connection!

I have 2 15k and 1 13.5k btu heat pumps and frequently run all three on a good shore connection.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is online now   Reply With Quote
Old 06-22-2021, 11:01 AM   #4
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,837
Quote:
Originally Posted by Rhobson View Post
I recently bought a 2008 Allegro Bus 43 QRP and where I bought it said that it had 3 AC units but that on shore power I could only run 2 at a time but if using the generator I could run all 3. Is this right? It doesn't make sense to me but I am new to motor coaching. Here in AZ it is 🔥 HOT 🔥 and it doesn't keep up with the heat when I run 2. I am plugged in to a good 50 amp 220v receptacle and want to run all 3 units. Can this be done safely? Or was the guy at the stealership correct?

So turn them ON......
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 06-22-2021, 12:46 PM   #5
Community Administrator
 
Lt Dan's Avatar


 
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 21,559
I run three all the time on both shore power and generator. Each one draws about 12 amps so 100amps (two legs of 50) is more than adequate. He may have been referring to 30amp service where you would only be able to run two but not much of anything else.
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previous '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
Lt Dan is offline   Reply With Quote
Old 06-22-2021, 01:16 PM   #6
Senior Member
 
garykk's Avatar
 
Tiffin Owners Club
Freightliner Owners Club
Join Date: Apr 2012
Location: Southern NM
Posts: 3,380
First thing is to be sure you have a 50 amp service and not a 30 amp. Some older units did require the genset to be running to operate the ACS. Make sure all the AC breakers are set, throw them and reset. Make sure you are getting 50 amps out of the pedestal, 50 amps on each leg. If that’s good, check the power at the breaker box for power on each leg. If not then it’s the transfer switch.
__________________
2018 Allegro Bus 37AP
2014 Phaeton 40 QBH (sold)
2022 Jeep JLURD
garykk is offline   Reply With Quote
Old 06-22-2021, 03:05 PM   #7
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,837
Quote:
Originally Posted by garykk View Post
First thing is to be sure you have a 50 amp service and not a 30 amp. Some older units did require the genset to be running to operate the ACS. Make sure all the AC breakers are set, throw them and reset. Make sure you are getting 50 amps out of the pedestal, 50 amps on each leg. If that’s good, check the power at the breaker box for power on each leg. If not then it’s the transfer switch.

OP was 'told' ...no actual issue
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 06-22-2021, 03:12 PM   #8
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
Quote:
Originally Posted by Old-Biscuit View Post
OP was 'told' ...no actual issue



Told by someone who does NOT know electricity or "read on the internet"-- kind of peas in a pod.


Agree, he needs to determine the FACTS by DOING IT.


And, if a problem, let us know under WHAT CONDITIONS.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Old 06-22-2021, 10:23 PM   #9
Junior Member
 
Join Date: Jan 2021
Posts: 23
Thank you for the responses. It didn't make sense to me since the generator is only 10kw. I will try it and see if I can cool off a bit.
Rhobson is offline   Reply With Quote
Old 06-22-2021, 10:48 PM   #10
Senior Member
 
SargeW's Avatar
 
Tiffin Owners Club
Join Date: Sep 2002
Posts: 1,524
My Bus has a 10KW gen, and it will run all 3 AC's at one time. My gen puts out 45 amps on each line, but a true 50 amp shore power should do 50 amp on each line. I was just a campground in So Cal on a 110 degree day. Although the pedestal was 50 amp, the voltage was a bit low mid day, in the 106 volt range. So for the 3rd middle AC I switched the fan to Low speed, which dropped the amp draw. All 3 AC's ran without a hitch.
__________________
Marty and Diane, Fulltiming!
2017 Tiffin Allegro Bus 40 SP
2018 Jeep Wrangler Sahara
mytripjournal.com/rvnchick2021
SargeW is offline   Reply With Quote
Reply

Tags
power, shore power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Enough is enough! MSHappyCampers RV'ing Humor & Crazy but True Stories 0 04-08-2021 05:01 PM
Plugging into shore power trips shore power breaker BFF Travel Supreme Owner's Forum 8 07-28-2017 10:53 PM
Shore power power not providing power to air conditioner jjhenley RV Systems & Appliances 6 06-21-2016 09:08 AM
Enough is Enough! It's gone! loranimal Monaco Owner's Forum 13 09-15-2007 08:36 PM