A lot of you guys are making a simple issue far more complicated than it needs to be. I don't have a Xantrex, but all inverter/chargers have to follow certain rules.
1. When AC is available, they pass it through. Inverter function isn't needed.
2. When AC is available, the integrated charger becomes active.
3. When AC is not available, the only source of power is the battery bank. Without that 12V input, nothing can work.
When the OP found +12 on the battery cables at the inverter, with shorepower connected, that tells us the charger is trying to charge something. It does not prove whether the inverter/charger is connected to any batteries.
When the OP found 0V at the inverter with shorepower disconnected, that it an obvious indication of a battery or cable problem. Yes, the fuse would be the next thing to check. Now that the fuse has been replaced, the inverter has a source of DC power and can be powered up. Great!
From this point on, we are looking at the behavior of certain AC appliances. If a GFCI outlet trips on inverter power but not on shorepower, that tells us that the inverter AC waveform is somehow inferior to the shorepower waveform, or that the switchover isn't happening smoothly.
For curiosity, I'd like to see the inverter AC output on a scope. But, for practicality and expediency, I think simply replacing the GFCI receptacle is the quick and dirty way to go. That is, as long as every other AC appliance is behaving nicely on inverter power. As a temporary troubleshooting measure, you could try a standard (non-GFCI) receptacle in that location.
If that new Xantrex isn't performing perfectly, you will want to know that before it goes out of warranty. At the very least, make sure you report the GFCI problem to Xantrex, just to get it on the record.