Furnace problem

Used our furnace thu nite the 27th worked great two nites later it came on just fine except no heat then it shut down. Tried again same thing no heat and it shut down, blower is working gas turns on but no flame. Any ideas to where to start looking first ? 2003 southwind 32V
__________________
2004 Fleetwood Southwind
smithd7 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-02-2021, 10:25 AM   #2
Senior Member
 
J Birder's Avatar
 
Join Date: Feb 2012
Location: Lake County, IL
Posts: 1,507
It would probably help if we knew the mane and model of the furnace.

Are you certain that you're not out of propane?

How have you determined that the gas comes on? Are you getting a spark?

Is your 12V supply high enough to run the blower at full speed? If not, the sail switch may not be closing, although, that probably not allow the gas to turn on.

Is it possible that insects (usually wasps or spiders) have not clogged up the outside vent?

Joel
__________________
Retired electronics engineer. Avid paddler & birder.
2011 Silverado 2500HD, diesel, 4x4,crew cab, 8' bed
Palomino Puma 253FBS (27' 5er) & '94 19' Class B
J Birder is offline   Reply With Quote
Old 06-02-2021, 01:32 PM   #3
Junior Member
 
Join Date: May 2018
Location: Coburg, Oregon
Posts: 26
It’s a Atwood 8535-iv-DCLP
Do you mean vent or exhaust. I can’t find the sail switch. There are two switches one is the on off switch the other has a blue wire that goes to the circuit board and a red wire going to the on off switch. This switch is fully enclosed with no moving outside parts.
__________________
2004 Fleetwood Southwind
smithd7 is offline   Reply With Quote
Old 06-02-2021, 02:13 PM   #4
Senior Member
 
Join Date: Nov 2015
Posts: 16,964
1)Thermostat on Heat...closes
2)DC goes back to furnace ---starts fan (via TDR)
***RED wire from On/Off Goes to TDR then to motor/BLUE wire from thermostat goes to TDR then to Ground Yellow Wire
3)Fan comes up to 75% speed....moves the paddle for sail switch closing it
4)That allows DC to go to circuit board for Gas valve and Spark electrode
5)Spark electrode fires CLICK, CLICK, CLICK igniting the gas flame
***Flame generates a electric current that circuit board senses ---prove flame lit (spark electrode is return for that milliamp signal)

SO..
Obstructed intake/exhaust vents
Low DC voltage..fan not up to speed
TDR (Timed Delay Relay) failed.....DC from thermostat allows DC to Fan Motor
Sail Switch stuck closed....dirty or paddle is binding against metal
Spark Electrode dirty...soot/carbon
Spark Electrode high voltage wire loose
Circuit Board faulty

See pg 10 for 85-IV wiring (local sense with Timed Delay Relay)
See pg 30 for all of the possible issues....blow runs/no flame
See pg 41 for exploded view of 8500-IV series
http://techsupport.pdxrvwholesale.co...anual-2004.pdf
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 06-02-2021, 03:25 PM   #5
Senior Member
 
J Birder's Avatar
 
Join Date: Feb 2012
Location: Lake County, IL
Posts: 1,507
I don't know that furnace. The sail switch will be a fairly large paddle connected to a switch. It is intended to prevent the furnace from operating if there isn't air flowing into the ducts. It will be located very near where the air duct connects to the furnace.


Joel
__________________
Retired electronics engineer. Avid paddler & birder.
2011 Silverado 2500HD, diesel, 4x4,crew cab, 8' bed
Palomino Puma 253FBS (27' 5er) & '94 19' Class B
J Birder is offline   Reply With Quote
Old 06-02-2021, 04:30 PM   #6
Senior Member


 
Winnebago Owners Club
Join Date: Sep 2015
Posts: 803
Quote:
Originally Posted by J Birder View Post
I don't know that furnace. The sail switch will be a fairly large paddle connected to a switch. It is intended to prevent the furnace from operating if there isn't air flowing into the ducts. It will be located very near where the air duct connects to the furnace.


Joel
The wires for the sail switch on an Atwood come out the top or side, but the switch itself is under the outside blower cover.

I want to know how he knows the gas is coming on? Can you smell it? Hear it?

If the gas valve is coming on, letting gas through, and you can hear the ignition click, you should get a couple second poof of flame. The gas valve will not stay on more than a second or two if it does not sense flame from the igniter electrode.

I had one once that would go through the entire cycle, open the gas valve, and didn't ignite until the 3rd spark, Shot about a 3 foot flame out of the exhaust, then went out.

I had another one that would not run on battery power, but if connected to shore power and full 13+ volts would run fine. Finally tore into it and 2 fins on the fan (plastic) were broke off. Needed to run full power to trip the sail switch. Replaced with steel fan. No more problems.

But from the sounds of it, since it was working, then suddenly quit, I would put my money on the time delay relay.

Also, pull the burner out and check condition. They tend to burn through and then the flame is not consistent and even.

And while the burner is out, pull the igniter, shut the LP off at the tank and try to fire it. See if you get a spark. The igniter is very sensitive to the gap. 1/8 inch, no more, no less. If you get a spark, clean both probes with steel wool and make sure the gap is right.
__________________
2006 Winnebago Journey
39K
Cat C7
amosnandy is offline   Reply With Quote
Old 06-02-2021, 04:37 PM   #7
Senior Member


 
Winnebago Owners Club
Join Date: Sep 2015
Posts: 803
Quote:
Originally Posted by smithd7 View Post
Itís a Atwood 8535-iv-DCLP
Do you mean vent or exhaust. I canít find the sail switch. There are two switches one is the on off switch the other has a blue wire that goes to the circuit board and a red wire going to the on off switch. This switch is fully enclosed with no moving outside parts.
The sail switch is inside the blower compartment. It will have two wires going to it. Some come out the top and you have to take the front fan cover off to get at it, some have two screws and just pull out the front cover.
__________________
2006 Winnebago Journey
39K
Cat C7
amosnandy is offline   Reply With Quote
Old 06-02-2021, 04:48 PM   #8
Senior Member


 
Winnebago Owners Club
Join Date: Sep 2015
Posts: 803
One more item that no one has mentioned is the High Limit Switch. It is designed to shut the furnace off if it get too hot. On an Atwood I believe it it is on the back. I've never had one fail but it is easy to check. Access the back of the furnace is the hard part. Usually you have to take a drawer or a panel off to get at the back. It is just a half dollar size disc with 2 wires. It is normally closed, meaning no resistance to it. A VOM should read zero or close to it. You can also just put a jumper between the 2 wires which completes the circuit. It should only be open if the furnace is overheated. Since this one is cold, of it is open it has failed. But again, I've checked them but never had a failed one on a furnace I worked on.
__________________
2006 Winnebago Journey
39K
Cat C7
amosnandy is offline   Reply With Quote
Old 06-03-2021, 10:20 AM   #9
Junior Member
 
Join Date: May 2018
Location: Coburg, Oregon
Posts: 26
I had the circuit board checked and it is bad, will see if that solves the problem.
__________________
2004 Fleetwood Southwind
smithd7 is offline   Reply With Quote
Old 06-05-2021, 11:42 AM   #10
Junior Member
 
Join Date: May 2018
Location: Coburg, Oregon
Posts: 26
put new board in and it still will not lite. I'll try to check the electrode
__________________
2004 Fleetwood Southwind
smithd7 is offline   Reply With Quote
Old 06-09-2021, 08:47 AM   #11
Junior Member
 
Join Date: Jun 2020
Posts: 5
Many of the Atwood furnaces have a red indicator light on the circuit board that will flash when there is a trouble code detected. Check the trouble code via the number of flashes being displayed after shut down. This will narrow down your problem and solution.
Sirjohnesq4 is offline   Reply With Quote
Old 06-16-2021, 05:43 PM   #12
Junior Member
 
Join Date: May 2018
Location: Coburg, Oregon
Posts: 26
update on furnace problem, thanks to all that replied to my post. The board was bad as was the electrode, replaced electrode and bingo!!! it works, thanks again for all the help.
__________________
2004 Fleetwood Southwind
smithd7 is offline   Reply With Quote
Reply

Tags
ace, furnace, problem



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace fan 2002 Alpine (Suburban gas furnace) dlmoo1 Alpine Coach Owner's Forum 5 01-21-2020 10:31 PM
Suburban NT-45S Furnace or Furnace motor Ronbstewart Monaco Owner's Forum 7 05-25-2018 08:15 PM
Furnace problem may not be in the furnace! turkeychuckt MH-General Discussions & Problems 3 02-03-2010 03:26 PM
Furnace problem? rlrich Excel Owner's Forum 8 01-15-2009 10:48 AM
furnace or thermostat problem georgetown350 MH-General Discussions & Problems 12 05-02-2007 03:57 PM


All times are GMT -6. The time now is 02:41 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.