I'm currently having the same issue, however, I am able to get it to work with some effort. This took a lot of experimentation.
To get it to work.
1. Turn zone 1 & 2 heaters off and then turn off heater.
2. Turn off anything else that uses propane.
3. Shut off all power to coach (Salesman Switch)
4. Disconnect Propane from the source.
5. Wait at least 5 min
6. Connect Propane to the source
7. Turn on the power (Salesman Switch)
8. Turn Heater to On
9. Select Zone 2 and only turn that zone on and set to higher than the current temperature.
10. If that works turn on anything else that currently needs propane.
The propane needs to work it's way back to zone 2 area. if the heater tries a few times and doesn't work. then switch the heater off for a couple of minutes and then switch it back on.
If 3 tries doesn't work then...
1. Turn off zone 2
2. Turn on Zone 1 and set to a higher than the current temperature.
3. Let zone one run for at least 15min
4. Turn on Zone 2 and set to a higher than the current temperature.
5. If that works turn on anything else that currently needs propane.
I'm thinking that my regulator is bad since my heater works, but seems to not be getting enough propane at times., and will be getting a new one asap.
Once the above actions get zone 2 going again, it runs well for as long as I have propane. Once I run out or need to refill I am having to go through this procedure again.
I hope this helps