Old 01-17-2021, 08:40 AM   #1
Senior Member
 
Genevatexan's Avatar
 
Newmar Owners Club
Texas Boomers Club
Oklahoma Boomers Club
American Coach Owners Club
Spartan Chassis
Join Date: May 2019
Location: Dallas, Texas
Posts: 102
Question Surge Guard Failed- need guidance

Our inbound power transfer switch shut down sometime this week and we found it Saturday. The coach batteries were discharged (coach and batteries new to us in Aug). I have inbound power at switch verified, but no power into the coach. We charged the house batteries with an external charger, and were lucky they came back up. This is a 2007 American Tradition with a model 40250 Surge Guard and an Intellitec EMS. We also tried to start the generator and the switch flashes but now won't start. Questions: 1) I read here that the 40350 switch (40250 discontinued) will fit the coach but may have to settings we must set to configure correctly. Anyone know what they are? 2) is there any other trouble shooting or repair or is the switch junk if no power is outbound? 3) will the 40350 work with Intellitec EMS? 4) should the generator run with the switch out but the coach batteries recharged? 5) any reason I can't replace on my own? 6) will the slide-outs run with the switch down? I gave one a bump and it was reluctant to go.
Genevatexan is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-17-2021, 08:54 AM   #2
Senior Member
 
Ljwt330's Avatar
 
Join Date: Jan 2018
Location: Capistrano Beach, California
Posts: 4,465
Quote:
Originally Posted by Genevatexan View Post
Our inbound power transfer switch shut down sometime this week and we found it Saturday. The coach batteries were discharged (coach and batteries new to us in Aug). I have inbound power at switch verified, but no power into the coach. We charged the house batteries with an external charger, and were lucky they came back up. This is a 2007 American Tradition with a model 40250 Surge Guard and an Intellitec EMS. We also tried to start the generator and the switch flashes but now won't start. Questions: 1) I read here that the 40350 switch (40250 discontinued) will fit the coach but may have to settings we must set to configure correctly. Anyone know what they are? 2) is there any other trouble shooting or repair or is the switch junk if no power is outbound? 3) will the 40350 work with Intellitec EMS? 4) should the generator run with the switch out but the coach batteries recharged? 5) any reason I can't replace on my own? 6) will the slide-outs run with the switch down? I gave one a bump and it was reluctant to go.
General response only.

First, have you inspected the inside of the transfer switch by removing the cover? You may find loose or disconnected terminal lugs are the problem, especially the ones that lead from the switch to the main panel in the coach.

The generator may not be starting because I believe it needs to detect a load of some kind, if only the load to the power panel. I am not certain of that, but I had a coach with a manual plug for the generator to the panel, and the generator would not start unless that plug was in the socket.

You should be able to change out the switch yourself if you have access and basic skills. It is fairly straight forward. Your slides operate off of the batteries, so they should be able to operate without any ac power at the coach.
__________________
Larry, Eileen, and Finley
2004 Alpine 36FDDS
Third motor home, first Alpine, no need for another.
Ljwt330 is offline   Reply With Quote
Old 01-17-2021, 09:19 AM   #3
Senior Member
 
Tha_Rooster's Avatar
 
Join Date: Aug 2008
Location: Georgia
Posts: 8,638
Quote:
Originally Posted by Genevatexan View Post
Our inbound power transfer switch shut down sometime this week and we found it Saturday. The coach batteries were discharged (coach and batteries new to us in Aug). I have inbound power at switch verified, but no power into the coach. We charged the house batteries with an external charger, and were lucky they came back up. This is a 2007 American Tradition with a model 40250 Surge Guard and an Intellitec EMS. We also tried to start the generator and the switch flashes but now won't start. Questions: 1) I read here that the 40350 switch (40250 discontinued) will fit the coach but may have to settings we must set to configure correctly. Anyone know what they are? 2) is there any other trouble shooting or repair or is the switch junk if no power is outbound? 3) will the 40350 work with Intellitec EMS? 4) should the generator run with the switch out but the coach batteries recharged? 5) any reason I can't replace on my own? 6) will the slide-outs run with the switch down? I gave one a bump and it was reluctant to go.


I would verify that both house probably (4) batteries are fully charge 12.6 volts or higher on your panel and chassis batteries are fully charged. Start engine which is suppose to be running operating slides per fleetwood. Make sure salesman switch is on and chassis switch is on also. To start genny hold down start button it should prime then start keep holding down till it starts.
__________________
2007 Fleetwood Revolution LE 40V
Tha_Rooster is offline   Reply With Quote
Old 01-17-2021, 02:06 PM   #4
Senior Member
 
Genevatexan's Avatar
 
Newmar Owners Club
Texas Boomers Club
Oklahoma Boomers Club
American Coach Owners Club
Spartan Chassis
Join Date: May 2019
Location: Dallas, Texas
Posts: 102
trouble shooting so far

Pulled the cover on the Surge Guard and did not find any obvious failures. No blackened parts, or ruptured items on the circuit board- relay looks ok, main two power blocks don't show any failure. My analog voltage meter on the house batteries reads about 13.4 volts. We run 4 6 volt house batteries wire positive to negative to acheive two 12 volts units. Shore power plugged in was hot on inbound, cold on outbound and no "whump" when unplugged and plugged back in. Does the engine charge the house batteries when running or must they charge from shorepower or generator? Generator start sounds a fast speed clicking but no turnover.
Genevatexan is offline   Reply With Quote
Old 01-17-2021, 02:35 PM   #5
Registered User
 
Join Date: Sep 2018
Posts: 1,205
Shore power plugged in was hot on inbound, cold on outbound
Is this inside the Surge Guard?
Does the engine charge the house batteries when running or must they charge from shorepower or generator?
Most do from the engine. Run it and measure the batt. voltage before and after. (with external charger off)
Generator start sounds a fast speed clicking but no turnover.
That sounds like the generator fuel pump 'clicking'. Measure the battery volts while trying to start generator, volts should stay above 12V.
EDIT: But the clicking could be the generator starter (if the battery volts drop too low)
OldWEB is offline   Reply With Quote
Old 01-17-2021, 02:47 PM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,420
Diesel generators will click while warming the glow plugs and then start cranking and start.
twinboat is offline   Reply With Quote
Old 01-17-2021, 04:47 PM   #7
Senior Member
 
Ljwt330's Avatar
 
Join Date: Jan 2018
Location: Capistrano Beach, California
Posts: 4,465
Quote:
Originally Posted by Genevatexan View Post
Pulled the cover on the Surge Guard and did not find any obvious failures. No blackened parts, or ruptured items on the circuit board- relay looks ok, main two power blocks don't show any failure. My analog voltage meter on the house batteries reads about 13.4 volts. We run 4 6 volt house batteries wire positive to negative to acheive two 12 volts units. Shore power plugged in was hot on inbound, cold on outbound and no "whump" when unplugged and plugged back in. Does the engine charge the house batteries when running or must they charge from shorepower or generator? Generator start sounds a fast speed clicking but no turnover.
The lack of "whump" indicates the contacts are not closing, IMO, and that would account for the lack of power through to the panel.

The engine will charge the chassis batteries first, then should switch to the house batteries so both sets eventually get charged. The opposite sequence happens when on shore power or generator.
__________________
Larry, Eileen, and Finley
2004 Alpine 36FDDS
Third motor home, first Alpine, no need for another.
Ljwt330 is offline   Reply With Quote
Old 01-18-2021, 07:36 AM   #8
Member
 
Join Date: Nov 2019
Posts: 41
Quote:
Originally Posted by Ljwt330 View Post
General response only.

First, have you inspected the inside of the transfer switch by removing the cover? You may find loose or disconnected terminal lugs are the problem, especially the ones that lead from the switch to the main panel in the coach.

The generator may not be starting because I believe it needs to detect a load of some kind, if only the load to the power panel. I am not certain of that, but I had a coach with a manual plug for the generator to the panel, and the generator would not start unless that plug was in the socket.

You should be able to change out the switch yourself if you have access and basic skills. It is fairly straight forward. Your slides operate off of the batteries, so they should be able to operate without any ac power at the coach.
Agreed! Open it up and check things. While it's unplugged from shore power and gen off of course. Mine kept "opening" when on shore power. Opened it up and a terminal was lose. Got torque from manufacturer. Tightened and problem gone.
__________________
2018 Fleetwood Bounder 35K (IT LOVES UNLEADED!)
Ford F53 22k GVWR with Front CHF & Roadmaster RSSA Steering Stabilizer
2010 Chevy Equinox w Master Tow tow dolly
meebarb is offline   Reply With Quote
Old 01-18-2021, 07:59 AM   #9
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by Genevatexan View Post
Our inbound power transfer switch shut down sometime this week and we found it Saturday. The coach batteries were discharged (coach and batteries new to us in Aug). I have inbound power at switch verified, but no power into the coach. We charged the house batteries with an external charger, and were lucky they came back up. This is a 2007 American Tradition with a model 40250 Surge Guard and an Intellitec EMS. We also tried to start the generator and the switch flashes but now won't start. Questions: 1) I read here that the 40350 switch (40250 discontinued) will fit the coach but may have to settings we must set to configure correctly. Anyone know what they are? 2) is there any other trouble shooting or repair or is the switch junk if no power is outbound? 3) will the 40350 work with Intellitec EMS? 4) should the generator run with the switch out but the coach batteries recharged? 5) any reason I can't replace on my own? 6) will the slide-outs run with the switch down? I gave one a bump and it was reluctant to go.
What switch?

Intellitec is a Load shedding device. Not a true EMS Protective device. It turns off 6 selected circuits.

It sounds like your battery disconnect got turned off. Light will show that voltage is present at the switch. Not whether it is on or off.

Battery disconnect will keep some drain on the battery for safety. CO. LP Stereo for clock and presets.

get your batteries load checked. Battery disconnect must be on for interior lights and control circuits if not plugged into shore power with the converter on.

slides will not work with the disconnect off.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Reply

Tags
led, surge guard



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
SURGE GUARD PROTECTION - on Tiffin Progressive vs Surge Guard? JimLuk Tiffin Owner's Forum 17 12-24-2020 09:36 PM
Surge Guard failed Xanrax 458 Blew Up! MikeandRuth National RV Owner's Forum 2 10-20-2017 12:10 AM
Autoformer with Surge Protection AND/OR Surge Guard specmga1 Newmar Owner's Forum 22 11-23-2016 01:30 PM
Surge Guard portable surge protector Bymorris Class A Motorhome Discussions 15 11-30-2013 07:39 AM
Surge Guard or Progressive Industries Surge Protector ? VACMAN Newmar Owner's Forum 41 08-20-2009 10:22 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:39 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.