Old 09-24-2016, 02:07 PM   #15
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by vacationer04 View Post
I have been out this morning and here is what I have found:
When on shore power or GEN the BR, Converter and WH are dead.
If 120V is supplied to the converter outlet with a separate wire in place of a plug all 3 work as normal, (meaning I am putting 120V in instead of out).
But if I get in the breaker panel and switch off the front roof A/C breaker all of them go dead at once.

I checked all of the breakers when on shore and the WH and converter are not showing any voltage unless the roof A/C breaker is also on. I also have two outlets in my slide that are powered with the others.
I do not have a basement GFCI that I can find. I only have two outlets and one is the converter and the other is on the other side where the outdoor entertainment would be if equipped.
If I plug in the 50A shore while I have the other power source engaged in the outlet that seems dead it immediately affects the circuit it is plugged into in my garage. If the WH and converter are on separate breakers and circuits, how does the secondary power I have supplied fix both?
My front roof A/C has not been working for awhile but when the extra power source is engaged there is some cool air coming from the vents, even though the fan is not blowing, only like the compressor is powered up. I have even disconnected the AC Romex from the A/C. I do not see how that A/C breaker can affect the WH and converter. When the A/C breaker is off all of that half of the breaker panel dies with it. All of the breakers test do positive for continuity.
I am afraid to take it for service for fear of needing to mortgage my house to pay for "diagnostic time". As long as I can keep the batteries charged I'll keep my options going awhile longer.
My EMS board also is flashing when the GEN runs like it has a code stored.
Lets go back to the statement above. Do you mean the converter is plugged into a 120vac duplex outlet and you are supplying 120vac INTO that outlet by running a separate 120 line into that outlet by backfeed (the other half of the duplex outlet)?

AND, the converter, bedroom, and water heater work when you supply the backfeed?

AND, if you turn off the roof A/C breaker (in the distribution box), the converter, bedroom, and water heater go dead?

If any of this is not the case, please rephrase.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-24-2016, 03:06 PM   #16
Registered User
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Aug 2006
Location: arnold, mo
Posts: 166
If mine ever had an inverter it must have been removed in the past along with the additional batteries needed for it to function. There is no evidence I can see where more batteries were ever installed. The sales literature listed it as optional. Maybe because mine came with the W/D it wasn't included.
vacationer04 is offline   Reply With Quote
Old 09-24-2016, 03:24 PM   #17
Senior Member
 
bluepill's Avatar
 
Join Date: Jan 2011
Location: Pensacola, FL
Posts: 2,457
1. If it had an inverter, it would never be used to power a converter, a W Heater, or an A/C.

2. Question: What size is the breaker for the problem circuit?

I ask because a converter and an A/C would usually have 20 amp dedicated breakers, and the WH a 15. It is VERY unlikely that those 3 would ever be on the same circuit. It seems to me that some circuit failure has ended up chaining those circuits together by cross-feed or back-feed, and possibly failed from the overload.

Be very careful when testing and investigating. You may have reversed hot-neutral, bootleg ground, Hot Skin, or other problems that can zap you.

Good link on wiring problems here:

http://ecmweb.com/contractor/failure...esting-exposed
__________________
2008 Itasca 37H
2011 & 2012 Len & Pat's "One lap of America"
27K miles & 41 states in 13 months
Yellowstone Lake 6-1-2012
bluepill is offline   Reply With Quote
Old 09-24-2016, 03:55 PM   #18
Registered User
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Aug 2006
Location: arnold, mo
Posts: 166
That is what is frustrating me. How can 3 breakers be affected by one of them? The main breaker straddles the two panels that the breakers are hung onto. But the side that controls the WH, converter and front roof A/C is virtually dead until I back feed the converter receptacle. It shows at most 3 volts when probed with a meter.
vacationer04 is offline   Reply With Quote
Old 09-24-2016, 04:05 PM   #19
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
Just a guess, but did you check the buss bar that the whites are in. Make sure every screw is tight.
twinboat is offline   Reply With Quote
Old 09-24-2016, 04:08 PM   #20
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
I think post #5 is most likely ... one leg of 50 amp is not making it to the main panel.

BTW, if you are checking for tightness in the panel, back off each screw 1/2 turn before retightening. This will ensure the screw is not seized and just feels tight.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 09-24-2016, 04:19 PM   #21
Registered User
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Aug 2006
Location: arnold, mo
Posts: 166
I will check that tomorrow. I hope I don't have to investigate inside the ATS, as it is plastic and riveted together in such a way as to not be able to access the contacts, to check or refinish them.
vacationer04 is offline   Reply With Quote
Old 09-24-2016, 04:27 PM   #22
Registered User
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Aug 2006
Location: arnold, mo
Posts: 166
In response to Bruceisla, post #15. Yes that is exactly the scenario I am working with. The one leg theory makes sense so I will look into that next since neither shore or GEN make a difference.
vacationer04 is offline   Reply With Quote
Old 09-25-2016, 06:41 AM   #23
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by bruceisla View Post
I think post #5 is most likely ... one leg of 50 amp is not making it to the main panel.
Vacationer04
I agree that one missing leg of the 50A power is most likely the cause of your problem.
The fault could be in the campground pedestal, in your electric cord, in your transfer switch, or in the 120VAC electrical panel in your coach.
mel s is offline   Reply With Quote
Old 09-25-2016, 07:07 AM   #24
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by mel s View Post
Vacationer04
I agree that one missing leg of the 50A power is most likely the cause of your problem.
The fault could be in the campground pedestal, in your electric cord, in your transfer switch, or in the 120VAC electrical panel in your coach.

Pretty sure the OP said it fails on Genset or Shore. That should eliminate pedestal and cord. I'd start at the distribution panel.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 09-25-2016, 08:09 AM   #25
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by vacationer04 View Post
It makes no difference if I use shore or GEN.
Quote:
Originally Posted by bruceisla View Post
Pretty sure the OP said it fails on Genset or Shore. That should eliminate pedestal and cord. I'd start at the distribution panel.
bruceisla
Right you are.
Sorry.
Mel
mel s is offline   Reply With Quote
Old 09-25-2016, 12:25 PM   #26
Registered User
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Aug 2006
Location: arnold, mo
Posts: 166
I checked the ATS and don't have voltage on all legs coming out of the ATS on the house side. I am currently at home with it adapted down to a 20A plug for power as I have since March. Will that let me do a voltage check? I do not have access to 50A here. In order to get a 50A source I would have to get new service to my house and that is not cost efficient to me at this point. Never needed more than 20A to keep my old 30A coach up and charged. It did not make any difference when I was plugged in to 50A at a campground.
I did discover today that if I touch the metal around the power compartment when shore is plugged in that I get a mild tingle. It did that once before. But not since the outlets failed so I thought it was no longer a relevant issue. The backfeed cord was not connected when that happened today. If it may be a grounding problem where should I start to look? I am not aware of where the 120V house power is grounded.
vacationer04 is offline   Reply With Quote
Old 09-25-2016, 12:44 PM   #27
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by vacationer04 View Post
I checked the ATS and don't have voltage on all legs coming out of the ATS on the house side. I am currently at home with it adapted down to a 20A plug for power as I have since March. Will that let me do a voltage check? I do not have access to 50A here. In order to get a 50A source I would have to get new service to my house and that is not cost efficient to me at this point. Never needed more than 20A to keep my old 30A coach up and charged. It did not make any difference when I was plugged in to 50A at a campground.
I did discover today that if I touch the metal around the power compartment when shore is plugged in that I get a mild tingle. It did that once before. But not since the outlets failed so I thought it was no longer a relevant issue. The backfeed cord was not connected when that happened today. If it may be a grounding problem where should I start to look? I am not aware of where the 120V house power is grounded.
vacationer04
It will.
However you have what's called a "hot skin condition" that could be deadly, and must be corrected...(Google "rv hot skin condition" for more information about that serious problem).

BTW the hot skin condition and your other A/C electrical problem may, or may not, be related.

Good luck.

Mel
'96 Safari
mel s is offline   Reply With Quote
Old 09-25-2016, 05:09 PM   #28
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by mel s View Post
vacationer04
It will.
However you have what's called a "hot skin condition" that could be deadly, and must be corrected...(Google "rv hot skin condition" for more information about that serious problem).

BTW the hot skin condition and your other A/C electrical problem may, or may not, be related.

Good luck.

Mel
'96 Safari
Mel is right on !! ... in both statements.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2001 diplomat 120v receptacles Gorlininc Monaco Owner's Forum 2 05-26-2014 10:04 PM
electric receptacles not working shortboxer Winnebago Industries Owner's Forum 7 04-12-2014 10:41 AM
120v receptacles on d/s out? mytime Country Coach Owners Forum 3 08-04-2013 01:58 PM
Receptacles not working sqzdog Winnebago Industries Owner's Forum 4 05-13-2011 09:30 AM
Receptacles on one side of 5th wheel not working?? doodlebug52 5th Wheel Discussion 17 12-02-2010 11:33 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.