What is the battery voltage? Is it low?
Check the voltage at the batteries and also at the inverter?
If it's erroring and saying batt voltage is low when it's not really low, sounds like an internal problem to me. Might be worth doing a reset. Why not try it?
Might need to call tech support and describe the issue. I had some questions for them during my installation and initial setup and found them to be pretty responsive.
Here's the remote manual. Is this the remote you have? Low Batt fault is described on p27
https://www.magnum-dimensions.com/si...ev-D-ME-RC.pdf
From the manual:
4.4.2 Performing a Power Reset
To perform a power reset (also known as a “hard reset”):
1. Open the inverter’s positive DC disconnect (or disconnect the positive battery cable to the
inverter).
Note: If parallel stacked with multiple inverters, open all the inverter’s’ DC disconnects at the
same time.
CAUTION: If removing all battery power (positive and negative) to the inverter, do
not remove the DC negative connections to the inverter or any accessory until after
all positive battery connections have been disconnected. This will prevent damage to
the inverter or to any network connected accessory.
2. Ensure the inverter(s) and the remote are disconnected from all AC and DC power (the
remote display will be blank).
3. After the inverter(s) has been disconnected from all power for 30 seconds, reconnect the
inverter DC disconnects (or reconnect the positive battery cable) and resume operation.
Info: If DC disconnects are not used, there may be a momentary spark when the
positive battery cable is connected to the inverter’s terminal. This is normal and
indicates that the inverter’s internal capacitors are being charged.