Old 12-09-2019, 05:34 AM   #15
Senior Member
 
Join Date: Jun 2011
Location: USA
Posts: 472
Quote:
Originally Posted by Pttwig View Post
I have wrapped on the check valves, I can feel the pumps are working. Seems like the problem is at the return manifold possibly. I have all 3 zones running and when I remove one of the return lines from the manifold connections you would think fluid would come back out of the manifold, but nothing. Is it possible there is a blockage? What about the radiator cap ? Could that stop the system from flowing?
Although you report the burner as operating it almost sounds as if you don't have enough antifreeze in the system, i.e., no fluid in the return line?? If you look in the install manual it will tell you how to purge the lines by shorting the pumps. If it truly is not the check valves jammed up, it's all that occurs to me. How long did this unit sit before you tried using it? I have a 600D and there is no manifold, the return lines just come back into the tank integral with the unit.
__________________
Bill B
2007 Navigator, 45' Series 60
Full-Timing since 2004
Bill767 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-09-2019, 06:38 AM   #16
Registered User
 
Join Date: Oct 2011
Posts: 2,183
Caution
Everytime you UNHOOK YOUR LINE'S.
You introduce AIR INTO THE SYSTEM.
And you should repurg and presurize the system.
If your unit sat for a long time ???
Its likely your boiler valves are gunked up.

Add some boiler fluid slowely over time and see if you can purge the air out of the tubing.

I think your trouble shooting efforts have caused you more work.
HJLowell is offline   Reply With Quote
Old 01-02-2020, 10:17 PM   #17
Junior Member
 
Join Date: May 2019
Posts: 19
Got it figured out. The manifold that the return lines all connected to in the unit was completely clogged with sediment (looked like dirt). I removed the hoses and took the manifold out . The clog was so solid I had to drill thru it all to clean it up. Then got a wire brushes to clean it up. The rubber hoses connected to it were all clear, only the aluminum manifold was filled solid. So far the unit has worked great since.

Thank you for your help.
Pttwig is offline   Reply With Quote
Old 01-03-2020, 05:04 PM   #18
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,822
Fascinating and strange. Where would the sediment have come from? It is a closed system and the boiler fluid should not have sediment settling out of it.

Was it more a matter of corrosion?
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 01-05-2020, 12:08 PM   #19
Junior Member
 
Join Date: May 2019
Posts: 19
It could have been corrosion. Never seen anything like it. The manifold is aluminum and was the only part that was affected.
Pttwig is offline   Reply With Quote
Old 01-05-2020, 03:33 PM   #20
Senior Member
 
RamiDav's Avatar
 
Join Date: Jan 2016
Posts: 1,529
Quote:
Originally Posted by Pttwig View Post
Got it figured out. The manifold that the return lines all connected to in the unit was completely clogged with sediment (looked like dirt). I removed the hoses and took the manifold out . The clog was so solid I had to drill thru it all to clean it up. Then got a wire brushes to clean it up. The rubber hoses connected to it were all clear, only the aluminum manifold was filled solid. So far the unit has worked great since.

Thank you for your help.
Might be a good idea to change the fluid
RamiDav is online now   Reply With Quote
Old 01-05-2020, 03:49 PM   #21
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,822
Quote:
Originally Posted by Pttwig View Post
It could have been corrosion. Never seen anything like it. The manifold is aluminum and was the only part that was affected.
Aluminium is reactive, it could have reacted to something in the fluid. Strongly doubt sediment. If it was brass it would be less likely to be corrosion.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 01-08-2020, 03:46 PM   #22
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,006
AH is an expensive item I have not read yet about anyone testing and changing its fluid in few years, I have been lurking here. Seems like it would difficult to completely empty the circuits.We have a solvent distilling unit at work and have to monitor glycol for lowering ph levels in chiller side. Heating side is synthetic oil.The oil is as high 370f When it starts cooling the oil at end of process.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 01-09-2020, 09:13 PM   #23
Junior Member
 
Join Date: May 2019
Posts: 19
I just ordered a tester to check the fluid make up. I will test the glycol and let you know what it reads
Pttwig is offline   Reply With Quote
Old 01-09-2020, 09:59 PM   #24
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,006
I see the Centry brand comes in 2 to 1 concentrate . So I guess you could fully wash out system and still get proper concentration.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 01-09-2020, 10:18 PM   #25
Senior Member
 
Captjake1's Avatar
 
Monaco Owners Club
Join Date: May 2015
Location: Where I happen to land
Posts: 2,528
It's not hard to drain, flush (bypass pumps to flush) and fill with premix.
I paid to have it done, but it was easy after watching.
I've since drained mine numerous times to fix leaks, etc.
Quote:
Originally Posted by 153stars View Post
AH is an expensive item I have not read yet about anyone testing and changing its fluid in few years, I have been lurking here. Seems like it would difficult to completely empty the circuits.We have a solvent distilling unit at work and have to monitor glycol for lowering ph levels in chiller side. Heating side is synthetic oil.The oil is as high 370f When it starts cooling the oil at end of process.
__________________
John and Debi
2008 Beaver Contessa, 2005 Jeep Grand Cherokee,
28 years retired Fire Captain Tales of the Muttley Crew
Captjake1 is offline   Reply With Quote
Old 02-12-2020, 12:53 AM   #26
Junior Member
 
Join Date: Jan 2020
Posts: 7
Quote:
Originally Posted by Pttwig View Post
I have wrapped on the check valves, I can feel the pumps are working. Seems like the problem is at the return manifold possibly. I have all 3 zones running and when I remove one of the return lines from the manifold connections you would think fluid would come back out of the manifold, but nothing. Is it possible there is a blockage? What about the radiator cap ? Could that stop the system from flowing?
We had an issue where the furnace to the front half of the coach only blew cold air. I talked by phone to John Carrillo, a hydronic heating specialist located in CO. He said that about 95% of the time, the problem we had could be fixed by tapping with a wrench or screwdriver handle on the part of the pipe that holds the stuck valve. However, you have to tap the pipe while the Aqua-Hot and furnace are running. We turned on the furnace so it was calling for heat in that zone. We had already removed the metal shroud from the A-H. The front zone is pump #3. Based upon the diagram in the owner's manual, I traced the supply and return ports for that pump. I tapped on the "fat" part of the correct port. It's located just BELOW the stainless steel top of the A-H case. It looks like a pipe that "swallowed a ping-pong ball". The "fat" part is where the valve is located. It worked. The A-H motor immediately sounded different. My husband was inside monitoring the air coming out of the furnace vents. He let me know that it immediately started blowing warm air. Thank you, John C.!
TravelFools is offline   Reply With Quote
Old 02-12-2020, 08:41 AM   #27
Senior Member
 
RamiDav's Avatar
 
Join Date: Jan 2016
Posts: 1,529
Quote:
Originally Posted by Pttwig View Post
I just ordered a tester to check the fluid make up. I will test the glycol and let you know what it reads
We never heard back from the OP about how the tester work .

Aluminum is very reactive to PH levels that are to high .
I have seen aluminum completely dissolve when placed in the wrong
chemical .
The OP should change the fluid regardless .

Ray
RamiDav is online now   Reply With Quote
Reply

Tags
ace, aqua hot, heat, monaco, monaco dynasty



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aqua Hot 600 Heat Exchangers Dynasty33 RV Systems & Appliances 3 01-29-2019 01:42 PM
Aqua Hot AHE-100-02S fluid MTK46 RV Systems & Appliances 12 04-19-2018 11:09 PM
Aqua Hot AHE 100 02S 1997 Monaco Dynasty Rustrodsrule Class A Motorhome Discussions 4 04-24-2016 10:16 AM
Aqua Hot furnace vs. Heat Pumps for heat S-n-L RV Systems & Appliances 14 12-17-2015 07:36 PM
Help my ahe-100-02s over flow tank never goes empty jeepstermog RV Systems & Appliances 4 12-07-2011 12:41 AM


All times are GMT -6. The time now is 08:19 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.