Hi all.
I have an Executive with 3 15000 BTU Duo Therm heat pumps.
When the rear one tries to start the compressor, it blows the circuit.
Even the Generator cannot start it. Also a strange smell coming out of it.
I'm assuming I'm going to need to replace the unit.
Is there any chance of just replacing the compressor?
Any help would be appreciated.
base341 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-05-2020, 10:18 PM   #2
Senior Member
 
Join Date: Oct 2016
Posts: 1,804
Good evening Base341; Just recently there has been a lot of A/C discussions here in the forum. First, I doubt that just trying to replace the compressor is an option, just my thought. A new unit would be a better way to go. Not speaking from experience, but there have been discussions here about the roof A/C's having the start capacitor's fail in the A/C unit. From what I have read some say it does not cost that much to replace the capacitors and is not a complicated job. You need to read how to deenergize them so not to set your hair on fire. I am sure someone with more experience with the situation you described will respond. Try using the search box at the top right of this page for the problem you have described and you should find other posts about problems with A/C units not starting the compressor. Sorry, that's all I can of this evening. Hope this info helps!
8.3Oilbuner is offline   Reply With Quote
Old 07-06-2020, 06:06 AM   #3
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,607
What kind of amperage are you seeing when you just try to run this AC unit. You can start the generator and see it on the load center. What is it when the fan first starts and then when the compressor kicks in?
I was having trouble with my front AC unit, it started to pull higher amps with the fan and sometimes would kick the breaker when the compressor kicked in. I finally crawled on the roof and removed the shroud to check things out. I found that the fan motor was almost froze up, could barely turn it over with my hand. Found a replacement and changed the motor which solved he problem. Cost was ~$120 for the motor. If you pay a repair shop to do this it probably won't be economic but is a DIY type job,
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is online now   Reply With Quote
Old 07-06-2020, 06:14 AM   #4
Senior Member
 
onechaddude's Avatar
 
Join Date: Jul 2011
Location: Lexington NC
Posts: 1,952
Quote:
Originally Posted by base341 View Post
Hi all.
I have an Executive with 3 15000 BTU Duo Therm heat pumps.
When the rear one tries to start the compressor, it blows the circuit.
Even the Generator cannot start it. Also a strange smell coming out of it.
I'm assuming I'm going to need to replace the unit.
Is there any chance of just replacing the compressor?
Any help would be appreciated.
I believe Oil burner hit the nail on the head. My rear AC did that several years ago. We were camping and awoke to the burning smell I'm sure the same as you smelled. Long story short, the compressor capacitor took a dump. Had a new one overnighted to the campground and we were back in business. Like Oil burner said, make sure you denergize it before you handle it. Good luck.

Chad
onechaddude is offline   Reply With Quote
Old 07-06-2020, 06:36 AM   #5
Community Moderator
 
Spdracr39's Avatar


 
Monaco Owners Club
Join Date: Jul 2016
Location: Central, Arkansas
Posts: 11,294
I third the capacitor diagnosis.
__________________
2004 Beaver Monterey Laguna IV
Cummins ISC 350HP Allison 3000 6 speed
2020 Chevy Equinox Premier 2.0t 9 speed AWD
Spdracr39 is offline   Reply With Quote
Old 07-06-2020, 06:46 AM   #6
Senior Member
 
Monaco Owners Club
Join Date: Sep 2013
Posts: 2,508
Quote:
Originally Posted by base341 View Post
Hi all.
I have an Executive with 3 15000 BTU Duo Therm heat pumps.
When the rear one tries to start the compressor, it blows the circuit.
Even the Generator cannot start it. Also a strange smell coming out of it.
I'm assuming I'm going to need to replace the unit.
Is there any chance of just replacing the compressor?
Any help would be appreciated.
Burnt electrical smell? PTCR frequently does that and is mounted on a capacitor which are the first suspects. Measure the capacitance with a meter or just replace them with non-Chinese parts. While there clean the coils.
__________________
2014 Newell 2020P 45'8" ISX 600 HP
hypoxia is offline   Reply With Quote
Old 07-06-2020, 06:47 AM   #7
Senior Member
 
CountryB's Avatar
 
Monaco Owners Club
Join Date: Aug 2017
Location: Orlando, Florida
Posts: 5,819
Try starting the rear AC unit by itself (with middle and front units Off) while on shore power. If the AC unit hums but doesn't start then it is most likely the "start capacitor" but if it still trips the circuit breaker, then you may have a wiring issue (shorted wire, etc.). The circuit breaker should not trip on a bad capacitor.
__________________
Mike --- 2005 Beaver Patriot Thunder CAT C13 525HP --Links below to my OneDrive docs---
*SMC, Beaver, Monaco History, Problems https://1drv.ms/f/s!AtvAXw_lfqbToxXYREK9YdBP08Jn
*Monaco Wiring Diagrams https://1drv.ms/f/s!AtvAXw_lfqbTm0WTuuNqpn9a8hCh
CountryB is offline   Reply With Quote
Old 07-06-2020, 07:24 AM   #8
Member
 
Join Date: Dec 2019
Posts: 32
Thanks for the suggestions.
I think the start capacitor is at least worth a try since they are pretty cheap and look to be pretty easy to change.
The fan itself runs fine, I just assumed the compressor was frozen up or something, the capacitor fail makes sense.
I love this place
base341 is offline   Reply With Quote
Old 07-06-2020, 10:41 PM   #9
Senior Member
 
DFord's Avatar
 
Ford Super Duty Owner
Join Date: May 2006
Location: Near St Louis, MO
Posts: 594
Start capacitors are only good for so many starts per hour (less than one a minute). They should only be in the circuit for less than a second during compressor start-up. They overheat easily and that could be what you're smelling. Get up on the roof and take the cover off to examine what things look like. Another common failure is the ends crimped on the wires for the spade connectors. Check all of them. Pop the cover off the compressor terminals and make sure none of the connectors look burnt. Same for the capacitors. The start capacitor will probably be a round Bakelite plastic and the run capacitor will be in a metal can. Both should have their electrical ratings written on the sides. The replacements may not look identical but the electrical ratings should be the same.
DFord is offline   Reply With Quote
Old 07-07-2020, 11:49 AM   #10
Senior Member
 
DFord's Avatar
 
Ford Super Duty Owner
Join Date: May 2006
Location: Near St Louis, MO
Posts: 594
VERY IMPORTANT; I forgot to mention the "start relay". (It may not be a real relay in these days of solidstate devices.) It should be replaced whenever the start capacitor is replaced. If it malfunctions and leaves the start capacitor in the circuit too long it will ruin the start capacitor in a few seconds. Don't risk it, they aren't that expensive.
DFord is offline   Reply With Quote
Old 07-16-2020, 08:17 PM   #11
Member
 
Join Date: Dec 2019
Posts: 32
Well I've been trying for 2 days to find the right capacitor.
I need a dometic or similar 370v 50/15 and there's literally none for sale in the country right now that I can find. Some places show they have stock but don't.
I did find a 370v 50/10 and ordered a couple of them to try. Hopefully it won't make much of a difference. I also ordered a replacement hard star capacitor.
Wish me luck
base341 is offline   Reply With Quote
Old 07-16-2020, 09:32 PM   #12
Senior Member
 
DFord's Avatar
 
Ford Super Duty Owner
Join Date: May 2006
Location: Near St Louis, MO
Posts: 594
You're ordering the "run" capacitor. You may not need it unless the old one shows signs of bulging. It can be tested with a meter but you'd probably need to order one of those too - everybody doesn't stock them. The 50mfd side takes care of the compressor and 15mfd side takes care of the fan motor. You should be able to get by with the 50/10 but I'd keep looking in earnest for the correct replacement. I think the start kit is really what you need. Wasn't there one on it to begin with? The tightwads may be saving a few bucks these days by trying to get by without them but they are a must for RV air conditioners.
DFord is offline   Reply With Quote
Old 07-17-2020, 04:11 PM   #13
Senior Member
 
Monaco Owners Club
Join Date: Jan 2017
Location: Utopia, TX
Posts: 500
I recently had a capacitor failure. Here's the dual capacitor I bought:
https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1

Did you confirm that it's the capacitor? Somebody mentioned a humming. When my capacitor failed, there was a lot of humming before the breaker popped.

Couple-years ago I had a control board fail in one unit with similar symptoms. A relay apparently fried and it would just trip the breaker.

Cheers,
Walter
__________________
2003 Monaco Dynasty 42 Regal.
wamcneil is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
duo-therm touch pad need help to find part classic_wax MH-General Discussions & Problems 13 01-21-2015 10:23 PM
HELP- Duo Therm AC manual needed mamacarol RV Systems & Appliances 11 03-17-2014 01:46 PM
Need help troubleshooting duo-therm ac unit Joedonna2 Monaco Owner's Forum 3 07-19-2009 09:45 PM
Duo Therm Ac Help BobC.Bunker RV Systems & Appliances 4 06-23-2007 12:31 AM
Duo-Therm Micro-Therm Air Filter System BeenThere DoneThat RV Systems & Appliances 1 04-25-2005 02:49 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:48 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.