ScotchJones,
Did this just happen one day, or were the A/C units worked on or replaced?
If they were replaced then the Dip Switches inside the unit control board need to be set for Furnace. See below.
If they have not been worked on or replaced, you have a bad connection on the RJ11 telephone communications cable. You will need to open up the bottom A/C covers inside the coach and clean the comm cable ends and connectors.
I like to use DeOxit to clean the ends and connectors.
https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1
After cleaning all the connectors do another thermostat reset. Slide the black on/off switch on the bottom off (forward). Depress and hold both the top and bottom buttons while sliding the on/off switch on. Watch for FF in the display.
If you need to set the Dip switches the Dometic guide is below.
Dip switches are in the “OFF” position
when shipped from the factory. They are
visible through the opening in the electronic control box. See (FIG. 22), (FIG. 23)
& (FIG. 24).
FIG. 23 Dip Switches
Ext. Stage
Zone 2
Zone 3
Stage
Heat Strip
Heat Pump
Furnace
Dehumidify
Gen Start
Zone 4
a. Ext. Stage - Ext. Stage is not used on this
unit. Leave in the “OFF” position.
b. Zone selection - Each CCC 2 thermostat can
have up to 4 zones. When only one unit is installed it becomes Zone 1 and no dip switch
setting is required. Each additional unit must
be assigned a zone (2 through 4). Each unit
must have a different zone setting.
c. Stage selection - Stage is not used on this
unit. Leave in the “OFF” position.
d. Heat Strip - Heat strip is not used in these
units. Leave in the “OFF” position.
e. Heat Pump - Heat pump is not used in these
units. Leave in the “OFF” position.
f.
Furnace - If a Furnace/
Aqua heat system has
been connected to this unit, the furnace dip
switch must be placed in the “ON” position.