I have been having issues with one zone of the t-stat. Zone 1 furnace would turn on and run and run and run. No matter where I set the temp, it would not shut off.

I have the Duo-Therm Comfort Control t-stat. I checked out the manual in case I was missing something stupid. I checked the forward temperature sensor as suggested in another post. See picture of the sensor here

To solve the problem, I used a "reset routine" that I found out about. I am posting it for educational purposes, and will claim ignorance if you blame me for messing up your t-stat
<UL TYPE=SQUARE>
<LI> Turn t-stat off
<LI> Hold Mode and Zone buttons in (top and bottom buttons)
<LI> Turn t-stat on
<LI> When you see "FF" release buttons
<LI> Turn t-stat off
<LI> Wait 2 minutes
<LI> Turn t-stat on[/list]
That seemed to take care of the t-stat issue. It now cycles on and off like a normal furnace


--kev
__________________
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

2006 Monaco Knight 40PLQ | 2011 Jeep Wrangler Rubicon Unlimited
digNbubbs is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-04-2007, 02:04 PM   #2
Senior Member
 
digNbubbs's Avatar
 
Monaco Owners Club
Join Date: Nov 2006
Posts: 530
I have been having issues with one zone of the t-stat. Zone 1 furnace would turn on and run and run and run. No matter where I set the temp, it would not shut off.

I have the Duo-Therm Comfort Control t-stat. I checked out the manual in case I was missing something stupid. I checked the forward temperature sensor as suggested in another post. See picture of the sensor here

To solve the problem, I used a "reset routine" that I found out about. I am posting it for educational purposes, and will claim ignorance if you blame me for messing up your t-stat
<UL TYPE=SQUARE>
<LI> Turn t-stat off
<LI> Hold Mode and Zone buttons in (top and bottom buttons)
<LI> Turn t-stat on
<LI> When you see "FF" release buttons
<LI> Turn t-stat off
<LI> Wait 2 minutes
<LI> Turn t-stat on[/list]
That seemed to take care of the t-stat issue. It now cycles on and off like a normal furnace


--kev
__________________
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

2006 Monaco Knight 40PLQ | 2011 Jeep Wrangler Rubicon Unlimited
digNbubbs is offline   Reply With Quote
Old 01-04-2007, 05:39 PM   #3
Community Moderator
 
"007"'s Avatar


 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 30,478
Thanks for the info "kev" alot of us have the Duo-Therm t-stat.
I'm sending this down to RV Systems & Appliances also.
They usually have a white cage over that sensor looks like someone removed it, the two screw holes are still there.
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 01-04-2007, 06:11 PM   #4
Senior Member
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Mar 2006
Location: Columbus, IN
Posts: 188
My thermostat problem is that the cycle times are too short. Three to five minutes on, then as little as 50 seconds off. (Fan times; burner ops are even shorter.) Before I try to find the anticipator circuit inside the stat, I'll try this reset procedure. Thanks for the info.
__________________
2016 Newmar Ventana 4002
2013 Honda CRV
bandcworkhorse is offline   Reply With Quote
Old 01-04-2007, 06:58 PM   #5
Senior Member
 
Monaco Owners Club
Excel Owners Club
Join Date: Nov 2006
Location: Hangin' with Sacs and the Pins
Posts: 9,412
Kev-
I think I am gonna print this post out so ...
1. I have instructions on what to do AND
2. I know who to blame if it doesn't work!



__________________
MM
*MonacoMama with the 2 Pins & SacsTC Nearby*
*2007 Monaco Diplomat 40' SFT<>2006 Chevy VortecMax Toad<>2006 Buick Lucerne Leading the Way*
MonacoMama is offline   Reply With Quote
Old 01-04-2007, 09:17 PM   #6
Senior Member
 
digNbubbs's Avatar
 
Monaco Owners Club
Join Date: Nov 2006
Posts: 530
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by "007":
Thanks for the info "kev" alot of us have the Duo-Therm t-stat.
I'm sending this down to RV Systems & Appliances also.
They usually have a white cage over that sensor looks like someone removed it, the two screw holes are still there. </div></BLOCKQUOTE>
Glad you found it useful There was a cage over the sensor - I had removed it to make sure the sensor was poking out of the wall sufficiently.

M*Mamma - I will deny all knowledge....


--kev
__________________
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

2006 Monaco Knight 40PLQ | 2011 Jeep Wrangler Rubicon Unlimited
digNbubbs is offline   Reply With Quote
Old 01-05-2007, 04:08 AM   #7
paz
Senior Member
 
paz's Avatar
 
Join Date: May 2005
Location: Full-timers - Home is where we park it.
Posts: 4,717
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by bandcworkhorse:
My thermostat problem is that the cycle times are too short. Three to five minutes on, then as little as 50 seconds off. (Fan times; burner ops are even shorter.) Before I try to find the anticipator circuit inside the stat, I'll try this reset procedure. Thanks for the info. </div></BLOCKQUOTE>

Please let us know how the reset works out for your problem of short cycles. I have a similar problem with short cycles, although not quite as short as yours.
paz is offline   Reply With Quote
Old 01-05-2007, 05:55 AM   #8
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 23,306
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">My thermostat problem is that the cycle times are too short. Three to five minutes on, then as little as 50 seconds off. (Fan times; burner ops are even shorter.) Before I try to find the anticipator circuit inside the stat, I'll try this reset procedure. Thanks for the info. </div></BLOCKQUOTE>

Short cycling in heating mode is usually not a t-stat problem. There are two common causes:

(1) A heat duct is too close to the t-stats sensor, causing it to warm up quickly while the rest of the room remains cool. The t-stat thinks it is warm and shuts off, but cools off as soon as the heat stops blowing on it. Close the offending vent or put some kind of deflector on it and see if that changes the cycling.

(2) Inadequate or blocked heating ducts, resulting in insufficient flow through the heat exchanger. This results in high internal heat in the furnace and a safety device called the High Limit Switch shuts down the burner while the fan continues to run to expel heat. Within 30-60 seconds the heat exchanger cools off and the High Limit condition goes away, allowing the burner to re-start. This is called cycling on the high limit and is fairly common in RVs. To fix it, inspect for crimped ducting, excess length of ducts (especially the flex coil stuff), dust or dirt on the air intake screen, and outlets that are closed (the little plastic knob may turn but the outlet may not actually open). Once plenty of air is flowing through the duct system, the short cycling should go away.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is in the Ocala Nat'l Forest near Ocala, FL
Summers in Black Mountain, NC
Gary RVRoamer is offline   Reply With Quote
Old 02-23-2007, 10:48 AM   #9
Senior Member
 
digNbubbs's Avatar
 
Monaco Owners Club
Join Date: Nov 2006
Posts: 530
I needed to bring this post back from Oblivion because it now has a real resolution.

To recap, I was having issues with the Zone 1 (front) furnace not shutting off. I called tech support and they walked me through the reset procedure above.

When I was on the phone with them, I had the t-stat real low (55 deg) so that I could see if it would turn off. I didn't think about setting it at a normal temp and testing it. Over time, I found the furnace would turn off only when the t-stat was set real low. I put a digital thermometer at the forward temperature sensor to watch for a pattern. It was usually off by about 15 degrees or so, but nothing real consistent. Example: t-stat would be set at 55 degrees, would cycle furnace off at 70-75+ degrees.

Over using it for a while, in different climates, I found that the heat pump and the A/C was short cycling. The compressor would kick on, and then off real quickly.

I had this problem looked at when I dropped into the Monaco Service Center in Wildwood, Florida. I went through all of the above anecdotal evidence. There were several guesses thrown out. The tech checked the positioning of the temp sensor, then removed the cover to the front A/C unit. This is what she found:



The coiled wire bundle is the remote temperature sensor! After pulling the ceiling light, she was able to find the broken end of the sensor that was installed. She was able to re-run that lead and connect it to the A/C unit.

It appears that something happened to the original sensor - possibly a broken connection or something during manufacturing - and the factory shoved another up inside the A/C unit. Maybe it was one of those "I will get that right after lunch" things

Regardless of how it happened, it now works great. The furnace, heat pump, and A/C all cycle on and off as they are suppose to.

Thought I would follow up on this odd problem.


--kev
__________________
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

2006 Monaco Knight 40PLQ | 2011 Jeep Wrangler Rubicon Unlimited
digNbubbs is offline   Reply With Quote
Old 02-23-2007, 02:07 PM   #10
paz
Senior Member
 
paz's Avatar
 
Join Date: May 2005
Location: Full-timers - Home is where we park it.
Posts: 4,717
Thanks for the follow-up. There were a lot of guesses and suggestions, but that's not something you would expect!
paz is offline   Reply With Quote
Old 02-23-2007, 03:49 PM   #11
Senior Member
 
ronboc's Avatar
 
Monaco Owners Club
Join Date: Jul 2005
Posts: 1,256
Hey Kev -

Who was your tech at Wildwood?
__________________
- - - - - - - - - - -

'06 HR Endeavor 40PAQ (Mission Hills decor). All options, but still finding more to add.
ronboc is offline   Reply With Quote
Old 02-23-2007, 06:11 PM   #12
Senior Member
 
digNbubbs's Avatar
 
Monaco Owners Club
Join Date: Nov 2006
Posts: 530
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by ronboc:
Hey Kev -

Who was your tech at Wildwood? </div></BLOCKQUOTE>

I had a team Brady was the service writer, the main tech was Halley, Jim helped out with the slide, and Todd helped with the monitor replacement. They all did a great job, and we had them over for Coronas after they finished up on the first day. Ang made them all cookies for after lunch snack



--kev
__________________
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

2006 Monaco Knight 40PLQ | 2011 Jeep Wrangler Rubicon Unlimited
digNbubbs is offline   Reply With Quote
Old 02-23-2007, 10:33 PM   #13
Senior Member
 
Monaco Owners Club
Excel Owners Club
Join Date: Nov 2006
Location: Hangin' with Sacs and the Pins
Posts: 9,412
...Ahhhh.. NOW HOW THE HECK DO YOU EXPECT US TO FOLLOW UP AFTER CORONAS 'N COOKIES!!! ... LOL ..glad you got a solution to your problems ...but .. did you have to make it hard on all of us who have to follow you after service?



__________________
MM
*MonacoMama with the 2 Pins & SacsTC Nearby*
*2007 Monaco Diplomat 40' SFT<>2006 Chevy VortecMax Toad<>2006 Buick Lucerne Leading the Way*
MonacoMama is offline   Reply With Quote
Old 02-24-2007, 04:18 AM   #14
Senior Member
 
ronboc's Avatar
 
Monaco Owners Club
Join Date: Jul 2005
Posts: 1,256
Now before MonacoMama and digNbubbs go and jump me for tugging this off-topic a bit , I'm going to plead that this follows Kev's repair job and service-experience at Monaco....

I too have had the same superb assistance from that team (Brady, Jim, Todd and HayLee). They are the best in my book (not that I'm slighting any of the others there whom I'd assume are just as qualified, but I really and truly don't want to have enough things go wrong that I experience EVERYBODY there).

When were you there, Kev? Todd had mentioned a few of them got together recently and wished he knew I was still there that afternoon. Bet we were there at the same time (early January?).

If anyone gets a chance, ask Todd how he came to be known as "Mr Hankee" (of SouthPark fame). Did he wash his hands before working on your coach, Kev?


See there? It's still on the same topic (sorta).
__________________
- - - - - - - - - - -

'06 HR Endeavor 40PAQ (Mission Hills decor). All options, but still finding more to add.
ronboc is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
12 Volt House Problem/Solution digNbubbs Monaco Owner's Forum 35 03-17-2011 08:44 PM
Heat Pump and stat problem moisheh Monaco Owner's Forum 9 06-08-2008 06:18 AM
Skid Wheel Problem and My Solution Mike Casella MH-General Discussions & Problems 5 11-22-2007 04:43 AM
Odd wiring problem solution JanBCarter Winnebago Industries Owner's Forum 2 08-10-2005 02:47 PM


All times are GMT -6. The time now is 05:06 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.