10,000 Onan Gen. will not keep running. Have changed fuel filter and checked all fluid levels, nothing changed. Has anyone else had this problem and found a solution?
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
Check the settings in your gen controller to make sure it is not set to auto-shutoff when the batteries reach a certain state of charge. (on my Coach the settings are made through the Xantrex (Inverter/Charger) panel.
So, for example, if the programmed setup is to start generator automatically when battery voltage drops to 12.0 and then shutoff automatically when batteries reach 12.6V, it may be that batteries are already over 12.6 so once generator is manually started it reads battery voltage and then auto shuts off.
Check your manual and find the procedure to recover the blink codes. I can recover my blink codes by pressing the STOP switch 3 times within 5 seconds. It will then go through a sequence of blink codes. Once you get the codes you can check what they mean. Without these there could be a number of causes.
How many hours on the generator???
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
My 10k Onan genset has recently started pulsating and quivering, then it would shut down. It will easily restart, but then do the same thing. You need to get the code.