Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > THE OWNER'S CORNER FORUMS > Monaco Owner's Forum
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 11-26-2020, 08:50 AM   #1
Senior Member
 
Join Date: Oct 2020
Posts: 588
Inverter/power issue?

Morning and Happy Thanksgiving, everyone!

On our first big trip today and have run into issues. Stupidly we left at 10pm without any propane when it was 20F. We thought we could fill up at the truck stop but all of them we tried had a 8 or 9pm cut off. So we drove all night but we were freezing.

We were using a heat cube in the cockpit running off the inverter. This worked great until the inverter shut off (lasted about 6 hours.) I haven't done the math yet but 1200w heater should have lasted longer than that on 4x big 6v batteries while being recharged by the alternator (via BIRD controller)..... Right?

Anyway, inverter shut off and I believe due to low voltage because I would turn it back on and it would run for 5-10m and then shut back off. I left it off.

This morning I'm not getting any 110v at the outlets. Inverter is on and green light is lit but it detects no load . I have reset it's breakers as well as all the breakers in my panel. Even with the gen running I have no outlet power. There is a tripped gfci on the bathroom sink outlet which trips as soon as I reset it. Nothing plugged in to any outlet at all.

2000/01 Diplomat w/ a trace 1500w inverter and 7.5kw onan. Would be very thankful for any help!
Fffrank is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-26-2020, 09:31 AM   #2
Senior Member
 
avfordguy's Avatar
 
Monaco Owners Club
Ford Super Duty Owner
Join Date: Dec 2008
Location: Kingsville TX
Posts: 1,754
At the load tou described, you maxed out the engine alternator, question is why didn't you run the generator? 99 monaco that we had i ran 3 1500 watt heaters for travel off 3 circuits, at .5/ gal/hr why not?
avfordguy is offline   Reply With Quote
Old 11-26-2020, 09:33 AM   #3
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,600
You may want to put your coach make/model/year in your signature.

If your alternator does not charge your house batteries you would have been better off running your generator.

Check your inverter, there is probably a breaker on it that has tripped, when voltage goes down, amps goes up so you deplete your batteries faster.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 11-26-2020, 09:36 AM   #4
Senior Member
 
avfordguy's Avatar
 
Monaco Owners Club
Ford Super Duty Owner
Join Date: Dec 2008
Location: Kingsville TX
Posts: 1,754
One thing to remember is that if you have a "wet bay heater" it draws about 35 amps 12v, so that adds into your problem.
avfordguy is offline   Reply With Quote
Old 11-26-2020, 09:41 AM   #5
Senior Member
 
Join Date: Nov 2018
Location: Beaver Dam, Wisconsin
Posts: 5,152
A 1300 watt electric heater would about max out a 1500 watt inverter. At 120 volts the heater would draw 11 amps. The inverter would draw 130 amps at 12 volts to run the heater. Plus the inverter would draw a little more to power the conversion.

High current draw from a lead acid battery will cause low terminal voltage. Voltage drop due to 130 amp draw would cause the terminal voltage to drop dramatically. Inverter would trip soon due to low input voltage.

Lead acid deep draw batteries are inefficient for high current draw. Battery bank would run down in short order.

Recharging from the engine might be between 20 and 80 amps. It is not nearly enough to replace what is consumed by the heater.

I have been there and done that! My TT uses "20 #" bottles. I exchanged at a gas station at 2 am. Even Walmart closes in a Covid year.
__________________
Paul Bristol
Kodiak Cub 176RD
Nissan Pathfinder 2015
Persistent is offline   Reply With Quote
Old 11-26-2020, 09:47 AM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Ad far as the battery life, the heater was drawing 10 amps, so 10 AH at 120 volts.

That's 100 AMPs at 12 volts !

6 hours = 600 AH plus inverter losses of about 30 AH = 900 AH.
4, 6 volt batteries avarage about 400 AH. You did good getting that much out of them.

Running at night uses more of your alternator power for chassis lights and heaters, leaving less for charging thru the BIRD ( Isolation Solenoid ). It will disconnect, If the chassis battery drops below 12.6 volts and delay reconnecting, protecting the chassis functions.

Run the generator.

GFCIs will not reset if there is no power. If it has power, unplug everything until it stops tripping.
twinboat is offline   Reply With Quote
Old 11-26-2020, 10:09 AM   #7
Senior Member
 
Join Date: Oct 2020
Posts: 588
It's all a learning experience. Honestly I thought it was a 600w heater and that it was using "free" power from the alternator. Lesson learned!

I found another gfci under the dining table and now that outlet works (but only that outlet. ) Bathroom circuit still trips as soon as it resets and can't find any other breakers and still nothing plugged that I can find. Inverter has two breakers and neither of them are tripped.
Fffrank is offline   Reply With Quote
Old 11-26-2020, 02:18 PM   #8
Senior Member
 
Outbound's Avatar
 
Join Date: Jun 2012
Location: NorCal
Posts: 3,000
Not a good way to start your trip, hopefully you will find propane and things will start to improve, you may have a GFI circuit in your outdoor storage bins.
__________________
Outbound
2002 Monaco Executive 500 ISM
2004 GMC 2500HD 4X4
Outbound is offline   Reply With Quote
Old 11-26-2020, 02:43 PM   #9
Senior Member
 
Join Date: Oct 2020
Posts: 588
Quote:
Originally Posted by Outbound View Post
Not a good way to start your trip, hopefully you will find propane and things will start to improve, you may have a GFI circuit in your outdoor storage bins.
Good call!

We did find propane and are now quite warm. Loves in Hudson, CO informed me that company policy is that all Loves that offer bulk propane (should be most of them) are required to sell 24/7. The woman working was quite bothered to hear I had stopped at 3 that refused late-night service. Who knows.

Great day to eat up some miles. No traffic. Just pushed through the eisenhower tunnel and left footing it to Moab.

Will check the bin outlets once we get parked this eve.
Fffrank is offline   Reply With Quote
Old 11-26-2020, 02:58 PM   #10
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Quote:
Originally Posted by Fffrank View Post
Good call!

We did find propane and are now quite warm. Loves in Hudson, CO informed me that company policy is that all Loves that offer bulk propane (should be most of them) are required to sell 24/7. The woman working was quite bothered to hear I had stopped at 3 that refused late-night service. Who knows.

Great day to eat up some miles. No traffic. Just pushed through the eisenhower tunnel and left footing it to Moab.

Will check the bin outlets once we get parked this eve.
I'v been turned down for propane fill in a few Flying J after 5 PM. The excuse was no one trained to do it on site.
twinboat is offline   Reply With Quote
Old 11-26-2020, 07:42 PM   #11
Senior Member
 
Join Date: Oct 2020
Posts: 588
I know a gfci provides quicker protection than the circuit breaker but I bypassed it tonight and all is well. I'll pick up a new one and hopefully problem solved while still being safe.
Fffrank is offline   Reply With Quote
Old 11-26-2020, 08:12 PM   #12
Registered User
 
Monaco Owners Club
Join Date: Nov 2017
Posts: 1,493
You got lots of great advice in here. I have the same unit as you so I'll add in my two cents as I recall the same issues as a new owner. Here's how it worked for me;

First, if you don't have 50 amp service you have to be careful what you plug in and run at the same time. You will blow breakers and such until you learn. Here's the checklist when that happens;

1) Check two breakers on inverter
2) Check two breakers on Generator
3) Check all the GFCI's. The bathroom seems to be the main culprit. There is also one under the kitchen table and one on the counter. Reset them all as necessary.

That will normally address the symptoms until you learn, from experience, why it happens. Also, just an FYI, on your inverter, when it's been completely powered off, you have to press the on button TWICE to turn it back on.
BobJones is offline   Reply With Quote
Old 11-26-2020, 08:59 PM   #13
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Quote:
Originally Posted by Fffrank View Post
I know a gfci provides quicker protection than the circuit breaker but I bypassed it tonight and all is well. I'll pick up a new one and hopefully problem solved while still being safe.
GFCIs don't offer quicker protection, they offer different protection.

Circuit breakers protect you from overloading the wiring and causing an electrical fire.

GFCIs protect against you from getting a deadly shock.
twinboat is offline   Reply With Quote
Reply

Tags
inverter, power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Class A Power inverter issue. need help! RatandRed Class A Motorhome Discussions 7 04-24-2020 05:48 PM
Power loss switching from generator to power inverter woodtouch6 Newmar Owner's Forum 6 04-07-2016 03:56 PM
Shore power/ Inverter issue Rod J RV Systems & Appliances 3 12-07-2014 04:23 AM
2001 Adventurer 35U Inverter no DC power issue paulyzx Winnebago Industries Owner's Forum 6 06-20-2012 08:22 PM
Southwind 36D Issue after issue after issue.... fixn2gocamp Fleetwood Owner's Forum 4 10-21-2009 07:05 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:50 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.